Other than possibly not being "workmanlike," is there anything in the NEC that prohibits a panel from being installed upside down? Upside circuit breakers read "NO" instead of "ON" and "FFO" instead of "OFF," which I don't consider workmanlike, of course.
NACHI 2005 U.S. Member of the Year
|
|
#2
|
|||
|
|||
|
Please Note:
ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
I remember a post about a panel being installed sideways and the sparkies said it was OK. Were Dr. Quervo and Mrs. Margarita assisting you with this inspection???
|
|
#3
|
||||
|
||||
|
240.81 Indicating. Circuit breakers shall clearly indicate whether they are in the open “off” or closed “on” position. Where circuit breaker handles are operated vertically rather than rotationally or horizontally, the “up” position of the handle shall be the “on” position. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Ms Margarita and Dr Cuervo thank you, Jeff.
By the way, what's the status on the Woodland Hills inspection? Anything? NACHI 2005 U.S. Member of the Year
|
|
#5
|
||||
|
||||
|
I don't think they've fully committed to that property at this point, and may start shopping again.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is no such thing as an upside down panel, unless this is an older panel with an "up/down" main breaker.
Most modern panels have a side to side motion main breaker so it can be installed either way. Even some no-so-new panels have side/side mains but all the writing and labels are readable with the main up. Putting the main down in this case is still acceptable. Nothing unworkmanlike about it. |
|
#7
|
||||
|
||||
|
Quote:
Looks like I'll have to post the picture later; the message board ain't cooperating. NACHI 2005 U.S. Member of the Year
Last edited by rray; 9/15/06 at 4:59 PM.. |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
All the breakers, as well as the panel itself, were upside down.
NACHI 2005 U.S. Member of the Year
|
|
#10
|
||||
|
||||
|
Yeah, the message board is working again.
Here's the picture. NACHI 2005 U.S. Member of the Year
|
|
#11
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, that most definitely qualifies as an upside down panel.
|
|
#12
|
||||
|
||||
|
This panel was upside down as indicated by to sticker on the lower left. The breakers were installed with the correct orientation.
Foxe Smothers ( Owner / Inspector ) Pelican State Inspection Your Best Choice for Home Inspection in the Shreveport & Bossier City Area! www.PelicanState.Net www.ShreveportHomeInspector.net www.BossierCityHomeInspector.net foxe@pelicanstate.net LSBHI #10399 |
|
#13
|
||||
|
||||
|
Quote:
I really like to have Peter Parker on my side once in a while. NACHI 2005 U.S. Member of the Year
|
|
#14
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smothers,
What makes that panel upside down IS the sticker. If the mfg states a specific orientation then we must follow it, even though that panel cannot be considered upside down according to the breakers. The NEC only cares about the "up/down=on/off" issue. Only: 110.3(B) Installation and Use Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling. ...applies here. *So guess I have to recant my statement above about no upside down panels. |
|
#15
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |