  #16  
Old 9/15/06, 7:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Upside down panel

Guys......most panels today can be either direction...the fact is you are still going to put the breakers in at the CORRECT direction anyway....so it makes no real difference.

We install many upside down if you would like to call it that....does not matter.

Now as Speedy stated...if it is an old panel with clear UP labeling and it should be installed as the manufacturer intended...but not the case really on the newer models.

AS for sideways or Horizontal panels....it is fine IF it is a single throw disconnect and such where the ON/OFF is left to right like a typical breaker.......but as you see alot with Zinsco's....where it is sideways and the ON is actually not visible because of the orientation of the breaker...then that is a violation of Sec 240.81

The NEC actually states in Sec 240.33 that "Enclosures containing OCPD's devices SHALL BE mounted in a "Verticle" position unless this is impractable. Circuit Breaker enclosures CAN BE installed horizontally, IF the circuit breaker is installed in accordance with 240.81.

With that said...Sec 240.81 states " Circuit Breakers shall clearly indicate whether they are in the open " OFF" position or closed 'ON" position. When the handle of a circuit breaker is operated vertically, the "UP" position of the handle shall be the " ON" position.



Paul W. Abernathy
Reply With Quote
  #17  
Old 9/16/06, 12:33 AM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Upside down panel

If I recall NEC [240-33] had to do with the "horizontal" issue where the breaker switch in the down position gave a false indication to being "off" when it is actually still in the "on"



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #18  
Old 9/16/06, 7:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Upside down panel

Yes it does.....BUT I gave BOTH to clarrify the difference



Paul W. Abernathy
Reply With Quote
  #19  
Old 9/16/06, 7:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Upside down panel

Quote:
Originally Posted by pabernathy

The NEC actually states in Sec 240.33 that "Enclosures containing OCPD's devices SHALL BE mounted in a "Verticle" position unless this is impractable. Circuit Breaker enclosures CAN BE installed horizontally, IF the circuit breaker is installed in accordance with 240.81.

With that said...Sec 240.81 states " Circuit Breakers shall clearly indicate whether they are in the open " OFF" position or closed 'ON" position. When the handle of a circuit breaker is operated vertically, the "UP" position of the handle shall be the " ON" position.
See above



Paul W. Abernathy
Reply With Quote
  #20  
Old 9/18/06, 1:17 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Upside down panel

Gottcha, thanks Paul



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts