Default use of extension cords

So I have had a few dishwashers and garbage disposals lately that have been installed using an orange extension cords that have been direct wired to the units. (not used as extension cords but as the actual wire)

Should I be writing that up, is that an appropriate material to be using?



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/8/11, 10:38 AM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: use of extension cords

The condition of an extension cord being used in place of cable should always be identified as a safety issue. The extension cord in question is likely not being utilized as designed and/or intended by either the manufactuer of the extension cord or the installed appliance. The NEC touches on this, but quoting codes by an HI is obviously a slippery slope.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #3  
Old 2/8/11, 10:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: use of extension cords

Extension cords are listed components - they are listed for temporary use. Electrical components must be used in accordance with their listing.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/8/11, 11:01 AM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: use of extension cords

Extension cords are UL listed and as long as the conductor size is proper it should be fine to use and many electricians do this on a regular basis. It's a good way to use a cord that was damaged some place else on the cord which made it unusable as an extension cord. So the argument I've heard is after it's been cut it's no longer an extension cord so if it's of the proper conductor size and no longer than 4 feet, as far as the NEC goes it's no different than an appliance cord you can buy The reason I would mention it in my report would be that once it was cut it no longer meets it's UL listing.
Reply With Quote
  #5  
Old 2/8/11, 11:02 AM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: use of extension cords

Quote:
Originally Posted by scoslett View Post
The condition of an extension cord being used in place of cable should always be identified as a safety issue. The extension cord in question is likely not being utilized as designed and/or intended by either the manufactuer of the extension cord or the installed appliance. The NEC touches on this, but quoting codes by an HI is obviously a slippery slope.
That was my initial thought, I never quote code but want to bring it to their attention, it they want to go further than that its their decision.
Thanks to all



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #6  
Old 2/8/11, 11:31 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: use of extension cords

Quote:
Originally Posted by jpope View Post
Extension cords are listed components - they are listed for temporary use. Electrical components must be used in accordance with their listing.

Exactly Cover your ***** .
We did a home this week that we did in 2002 .
Exactly the way it was 9 years ago except they had put on vinyl where it was aluminum before .
Same no ground on some plugs hot neutral reversed No GFI installed Tape on laundry drain same colours same cracked Toilet.
Some people are it works so thats OK .
Still a tired house that has many needs.
So you can expect they could leave the extension cord .
Still a lot better then the 300 ohm TV cord I have seen used.



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 2/8/11, 12:02 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: use of extension cords

Speaker wire, extension cords, lamp cords and many others find their way into the use of permanently connected appliances... and should be an easy catch and fix.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #8  
Old 2/8/11, 12:21 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: use of extension cords

Quote:
Extension cords are UL listed and as long as the conductor size is proper it should be fine to use and many electricians do this on a regular basis. It's a good way to use a cord that was damaged some place else on the cord which made it unusable as an extension cord. So the argument I've heard is after it's been cut it's no longer an extension cord so if it's of the proper conductor size and no longer than 4 feet, as far as the NEC goes it's no different than an appliance cord you can buy The reason I would mention it in my report would be that once it was cut it no longer meets it's UL listing.
I don't believe it is the case, but it appears as if you are implying the practices mentioned are valid if an electrician performed them....thus the need for HI's.

While modifying an extension cord will likely void its UL listing (what if an extension cord is not UL listed?....can it then be modified?), the NEC is the final authority in regard to the specification of wire or cable used in a permanent installation.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #9  
Old 2/8/11, 3:39 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: use of extension cords

My point is that we are to refer to a licensed electrician when something electrical is questionable since we are not experts or code inspectors. The people call the electrician and he says I do that all the time it's no big deal. Like I said, as long as the cord is of the right conductor size and in good shape the electrician will use it. The NEC 422 doesn't say the type of cord. It states "suitable for the purpose in the installation instructions
of the appliance manufacturer
". The NEC doesn't cover cords or appliances, UL does. That's why I mentioned the UL listing. It states "suitable fitting for line connection assembled to a length of general-purpose flexible cord". This sounds like an extension cord can be used to me. But UL always states you should not use an extension cord if it's been cut.

Nondetachable Types
Power-supply Cord — This is a power-supply cord consisting of a length of flexible cord assembled with an attachment plug or current tap as a line fitting but without a cord connector (appliance coupler) at the opposite end. It is intended for direct wiring connection to an appliance and may include a through-cord switch. Nondetachable power-supply cords may be one of the following:
  • Power-supply Cord for General Use — This is a power-supply cord consisting of a suitable fitting for line connection assembled to a length of general-purpose flexible cord, and may include a through-cord switch.
  • Power-supply Cord for Ranges and Dryers — This is a power-supply cord consisting of a general-use nondetachable power-supply cord constructed using Type SRD or SRDT flexible cable. The flexible cable may employ a neutral conductor which is two AWG sizes smaller than the other circuit conductors, but not smaller than 10 AWG.
Reply With Quote
  #10  
Old 2/8/11, 4:17 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: use of extension cords

For cord and plug appliance connections there are several NEC requirements, one being that the appliance must listed for cord and plug connection:

Quote:
400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for the following:
400.7(A)(Eight)Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection.
Quote:
422.16 Flexible Cords.
(A) General. Flexible cord shall be permitted (1) for the connection of appliances to facilitate their frequent interchange or to prevent the transmission of noise or vibration or (2) to facilitate the removal or disconnection of appliances that are fastened in place, where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection.
Another requirement is that the cord be identified as suitable for the purpose in the appliance installation instructions. I would doubt that the instructions would permit an orange extension cord to cut and be used in either of these applications. Also I agree with Scott that modifying an extension cord would likely violate it's listing.

Quote:
422.16(B) Specific Appliances.
(1) Electrically Operated Kitchen Waste Disposers. Electrically operated kitchen waste disposers shall be permitted to be cord-and-plug-connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer, where all of the following conditions are met:
(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed kitchen waste disposer distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall not be less than 450 mm (18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be accessible.
422.16(B)(2) Built-in Dishwashers and Trash Compactors. Built-in dishwashers and trash compactors shall be permitted to be cord-and-plug-connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer where all of the following conditions are met:
(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed dishwasher or trash compactor distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to 4 ft) measured from the face of the attachment plug to the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be located in the space occupied by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.
Reply With Quote
  #11  
Old 2/8/11, 4:24 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,260
Default Re: use of extension cords

Did you remove the wire nuts and have a look see or are you just assuming it was an extension cord?






INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #12  
Old 2/8/11, 6:00 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: use of extension cords

Quote:
Did you remove the wire nuts and have a look see or are you just assuming it was an extension cord?
I would assume an extension cord based on the lack of spec stamping usually found on NM cable insulation.....no need for disassembly.

Quote:
The NEC doesn't cover cords or appliances, UL does. That's why I mentioned the UL listing. It states "suitable fitting for line connection assembled to a length of general-purpose flexible cord". This sounds like an extension cord can be used to me. But UL always states you should not use an extension cord if it's been cut.
The NEC has numerous provisions covering cords and appliances as pointed out by Mr. Meier. Ultimately, I believe we were discussing the proper installation of a dishwasher and garbage disposal. As stated, the NEC directly addresses the proper installation of these appliances. I am not aware UL has issued such spec's.

In conclusion, the appliances did not appear installed correctly per the NEC, and the use of a modified extension cord does not meet the UL listing for the cord......



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #13  
Old 2/8/11, 7:30 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: use of extension cords

Flexible cord is permitted by the NEC as long as it of suitable for the purpose. UL is the governing body of appliances and cords. If you read the NEC is often says "listed" when referring to extension cords. NEC doesn't do the listing UL does. The NEC only refers to the use of such devices. UL does have installation requirements for both dishwashers (UL 749) and disposers (UL430). Both allow cords as long as they are proper. I would agree the cut extension cord is not "proper". In new installs I believe you need to get the cord directly from the appliance manufacture but it wasn't always the case as long as the cord meet the UL standards for the appliance type.
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/8/11, 8:39 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: use of extension cords

Quote:
UL does have installation requirements for both dishwashers (UL 749) and disposers (UL430)
I believe the stated sections are referring to product safety in general as it applies to the given appliances....Correct me if I am wrong, but UL installation policy states the appliance must be installed per the NEC.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #15  
Old 2/8/11, 9:40 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: use of extension cords

Very close to NEC. The NEC regulates the installation of electrical components but in this case we are talking about an appliance. The internal wiring and how an appliance connects to power is listed by UL.
UL Standard UL-749
UL 749
Household Dishwashers

7.3 Installation instructions

7.3.1A Where the installation instructions for a built-in dishwasher specifies
that the appliance is able to be connected by means of a power-supply cord
not already attached to the appliance by the manufacturer, the instructions
shall specify that a power-supply cord kit marked for use with dishwashers
shall be used. The cord kit shall comply with Clause 25.2A. The part or model
number of the power-supply cord kit shall be included in the appliance
installation instructions.
7.3.2 The installation instructions provided with a cord-connected undercounter appliance shall include the following instructions or equivalent information:
a) the power-supply receptacle for the appliance shall be installed in a cabinet or on a wall adjacent to the undercounter space in which the appliance is to be installed;
b) there shall be an opening through the partition between the compartments specified in (a) thatis large enough for the attachment plug to pass through. The longest dimension of the opening shall not be more than 38 mm;
c) the edges of the opening specified in (b) shall, if the partition is wood, be smooth and rounded, or, if the partition is metal, be covered with an edge protector provided for this purpose by the manufacturer; and
d) care shall be exercised, when the appliance is installed or removed, to reduce the likelihood ofdamage to the power-supply cord.

25.2 Cord-connected appliances
25.2.1 The power-supply cord of an appliance provided with a means for grounding shall include anequipment-bonding conductor and shall terminate in a grounding-type attachment plug.

25.2.4 For a cord-connected built-in appliance:
a) the flexible cord shall be Type S, SJT, SPT-3, or the equivalent; and
b) the length of the flexible cord shall be 0.9 – 1.2 m, measured from the face of the
attachment plug to the plane of the rear of the appliance.

25.2.5 The power-supply cord shall be attached permanently to the
appliance or shall be in the form of a separate cord supplied as part of a
power-supply cord kit with means for connection to the appliance. The
power-supply cord kit shall comply with Clause 25.2A.
25.2.6 The ampacity of the cord and the current rating of the fittings shall not be less than the current
rating of the appliance.
For an appliance rated more than 15 A, the current rating of the attachment plug shall not be less than 125% of the current rating of the appliance.
A 20 A plug shall be acceptable for an appliance rated not more than 4000 W at 240 V. The attachment plug shall be acceptable for use at a voltage equal to the rated voltage of the appliance.

25.2A Power-supply cord kits for use with undercounter or built-in
dishwashers
25.2A.1 A power-supply cord kit intended for the installation of an
undercounter or built-in dishwasher shall include the following:
a) power-supp ly cord, strain-relief means, and push-back relief that complies
with Clause 25.2;
b) a part or model number marked on the power-supply cord kit package, or
in the kit installation instructions;
c) installation instructions; and
d) grounding instructions in accordance with Clause 7.2.2.4(a).

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Extension Cords in Crawl Spaces Skip Erwin Electrical Inspections 10 6/25/06 3:39 PM
Joe F, update? jtedesco1 Electrical Inspections 54 4/10/06 10:35 AM


All times are GMT -4. The time now is 7:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts