Default Use of tied breakers on 110v circuits

I have recently checked some houses in Elgin with a common builder and the under-sink receptacle for the dishwasher and disposal was a split duplex receptacle with a dedicated circuit for each appliance. This setup was protected by a 2 pole tied circuit breaker. When I questioned the electrical inspector he cited the 2008 NEC code for multiwire branch circuits, saying a common neutral wire required the 220v breaker.
It still seems to me that there would be a potential failure to trip if there was a problem on one appliance. Any comments?

Mark Kollath
Mark Kollath Home Inpection, Inc.
Chicago
Reply With Quote
Need a home inspection in Alaska? Check out InterNACHI's listing of Alaska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/8/11, 2:54 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of tied breakers on 110v circuits

It's required. Under the 2008 it's required for all MWBC's, circuits with shared neutrals. In this instance it was required for many years prior to the 2008 code change since there are two circuits on the same yoke.
Reply With Quote
  #3  
Old 7/8/11, 3:12 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Use of tied breakers on 110v circuits

It still seems to me that there would be a potential failure to trip if there was a problem on one appliance. Any comments?

No comments.
they work well and protects people who want to do electrical work by shutting of both circuits



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 7/8/11, 3:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of tied breakers on 110v circuits

Circuit breakers are designed to trip internally. Even if the handle is held in the closed position the breaker will still trip. As Roy mentioned this was added to the 2008 NEC for the safety of someone working on the circuit with a shared neutral. Shared neutrals can be dangerous if they're opened with only one of the circuits turned off.
Reply With Quote
  #5  
Old 7/8/11, 3:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Use of tied breakers on 110v circuits

Quote:
Originally Posted by mkollath View Post
It still seems to me that there would be a potential failure to trip if there was a problem on one appliance. Any comments?
That's exactly the reason that proper (listed) ties are necessary.

A wire, or some other "make-shift" tie may not pull the other breaker into the open position when there is a fault.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 7/8/11, 4:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of tied breakers on 110v circuits

Quote:
Originally Posted by jpope View Post
That's exactly the reason that proper (listed) ties are necessary.

A wire, or some other "make-shift" tie may not pull the other breaker into the open position when there is a fault.
If there was a fault situation in one of the circuits why would the other circuit need to open? Even a listed handle tie might not open the other breaker.
Reply With Quote
  #7  
Old 7/8/11, 4:03 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Use of tied breakers on 110v circuits

Quote:
Originally Posted by jpope View Post
That's exactly the reason that proper (listed) ties are necessary.

A wire, or some other "make-shift" tie may not pull the other breaker into the open position when there is a fault.
Correct me if I'm wrong, but the breakers trip without regard to the handles. The tie is only so one cannot be independantly operated without the others at the same time.

Edit... OK I just reread the thread, and think I got the answer to my own question.
Reply With Quote
  #8  
Old 7/8/11, 4:48 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of tied breakers on 110v circuits

Quote:
Originally Posted by mkollath View Post
I have recently checked some houses in Elgin with a common builder and the under-sink receptacle for the dishwasher and disposal was a split duplex receptacle with a dedicated circuit for each appliance. This setup was protected by a 2 pole tied circuit breaker. When I questioned the electrical inspector he cited the 2008 NEC code for multiwire branch circuits, saying a common neutral wire required the 220v breaker.
It still seems to me that there would be a potential failure to trip if there was a problem on one appliance. Any comments?

Mark Kollath
Mark Kollath Home Inpection, Inc.
Chicago
In Canada, kitchen counter split receptacles have been protected this way since the 1970's. Although there have been code changes since then requiring single circuit GFCI protected receptacles near sinks, the present code still allows split receptacles protected by double-pole "tied" breakers away from sinks.

There appears to have been no problems with this arrangement.

Last edited by Brian A. MacNeish; 7/9/11 at 6:36 PM..
Reply With Quote
  #9  
Old 7/9/11, 2:32 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Use of tied breakers on 110v circuits

Someone posted a photo of a breaker a while back where Harry Homeowner had tried to "fix" a breaker that kept tripping by jamming a stick up against the breaker handle inside the panel ...

It didn't work of course because of the internal trip mechanism of the breaker. But ya have to give him credit for really trying to kill himself. Wish I could find that photo/topic again. It was priceless!



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Using 100 breakers on 220 circuits? rsole Electrical Inspections 4 1/8/11 5:31 PM
220 breakers on 120 circuits? rsole Electrical Inspections 12 12/12/08 3:14 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 7:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts