Post Use of Type UF Cable for AC Unit

Is Type UF cable permitted to be used as the supply from an AC disco to the unit without any support when installed outdoors?

I can't seem to find any sop where this is OK, please let me know.
Reply With Quote
  #2  
Old 4/9/06, 9:56 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

Sparks,

Most of the time when we are installing these units we use " liquid tight " for the application and install conductors rated for wet locations. Now I will have to admit many electricians just sleeve 10-2 NM inside the pipe which I am sure could raise a entirly new debate.....

However, because of the risk of damage we install " liquidtite" and pull UF cable within it......Sure some will say you should pull individual conductors of like THWN and so on.....which is probably the best.....but in the real world I do not believe we have been turned down for a short 2-3' UF sleeved within Liquidtight.....I like it better than people sleeving NM Cable within it because NM is not rated for the wet location existant in conduit.

Ok...can you run UF to the AC unit from the disconnect.....hmmm.....Is it subject to physical damage?....Probably....another note is UF should be sized based on 60 degree ratings as listed in table 310.16

If you sleeve it...support it 12" from the enclosure.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 4/9/06, 10:23 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

lol...Sad thing is "Liquid Tight " is not protection from Physical Damage either really........but AHJ's have never really had a issue with it.

Either way....of the choices.....I would write up the UF as being exposed to damage......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 4/9/06 at 10:31 PM..
Reply With Quote
  #4  
Old 4/9/06, 10:32 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of Type UF Cable for AC Unit

I am guessing that means it was a bootleg job. Is this common around your area? May be right or could have more serious problems of an HVAC nature, like a bad charge.
Reply With Quote
  #5  
Old 4/9/06, 10:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

Not sure I follow you Greg.......Bootleg Job?



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 4/9/06, 10:46 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,515
Default Re: Use of Type UF Cable for AC Unit

Greg,
Bootlegged connections and runs abound here out the wahzoo. I routinely find a handyman has installed wiring to an AC unit. They have been known to run NM, UF outside (literally coming out of the soffit down to the unit, no NM clamps) I found one not long ago the fella had run the NM from inside the Air handler closet down through the line set chase out to the outdoor unit. It was bright yellow too for all the world to see. Another time I found someone had used green garden hose for a "sorta" liquidtight FMC to run cable (again NM) out to their shed. Its like anything goes here if you can get away with it.
Reply With Quote
  #7  
Old 4/9/06, 10:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

OHHH..SNAP....you mean the UF to the AC unit as being BOOTLEG...done by a handyman....DANG...I was SLOW on that......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 4/10/06, 2:06 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of Type UF Cable for AC Unit

The best case might be an HVAC guy moonlighting who just didn't have any sealtite on the truck
Worst case would be a stolen unit installed by a handyman working out of his trunk.
I would also be looking at shortcuts they took in the ductwork and other issues
Reply With Quote
  #9  
Old 4/10/06, 8:00 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Use of Type UF Cable for AC Unit

"How to install outdoor wiring"
http://www.dulley.com/diy/dw107.htm
Reply With Quote
  #10  
Old 4/10/06, 9:18 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default Re: Use of Type UF Cable for AC Unit

http://www.dulley.com/diy/dw107.htm

This article states that the NEC requires #12 for all residential wiring....

When did this change ?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #11  
Old 4/10/06, 10:18 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

Bruce,

Are you refering to that comment line in the article you posted which I have re-posted below:

"The National Electrical Code now requires No. 12 gauge wire for all residential electrical wiring."

News to me.........We are buying # 14 AWG everyday...and just for the record I am NOT one of those who believe every plug in the house should be 12 AWG...sure it has more capacity....but if you KNOW what you are doing and size it correctly...14 AWG is fine...

I am not aware of any stoppage of # 14 AWG....atleast not in the CODE book I use...thehehehe



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 4/10/06, 1:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Use of Type UF Cable for AC Unit

That's one problem I see in all of these "wiring made easy" books. They don't know what the code says
Reply With Quote
  #13  
Old 4/10/06, 2:21 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

Agreed......Anyone can write a book...the research is the important part.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 4/11/06, 7:24 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Use of Type UF Cable for AC Unit

Quote:
Originally Posted by bking
http://www.dulley.com/diy/dw107.htm

This article states that the NEC requires #12 for all residential wiring....

When did this change ?
That is strange...

But I can say that 90% of Electricians (in Massachusetts) installing wiring in new construction today, utilize 12 AWG.
Reply With Quote
  #15  
Old 4/11/06, 11:02 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Use of Type UF Cable for AC Unit

David,

could be quite possible, however in VA or atleast in the area's I deal with....14 AWG is used with no problems and has been in use since 1928 when NM Cable was introduced.

I do not have a problem wiring 14 AWG for bedrooms and general lighting...and guess what...I have done 1,000's of homes....no reports of random tripping yet.....tehehehhe

If the client requests 12 AWG we most certainly will run it, they have to also be aware of the additional charge for wire and labor associated with running more 12 AWG wire.

Ok..for those who say that is not a big difference in labor...they obviously have not done alot of houses in 12 AWG....Kitchens are bad enough...but the entire house....murder in mid-winter....

I dont have a problem with it either way...Both work fine to me as it ends up being on the shoulders of the electrician to wire the branch circuits correctly and break up the wiring to reduce any potential for Voltage Drop....remember 50' is still a long way...considering all the factors envolved like panel placement and so on....

14 AWG....12 AWG...its all good.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
Did you KNOW this about NM Cable? pabernathy Electrical 0 12/19/06 9:46 AM
Hey Joe Tedesco pbolliger Electrical 7 4/11/06 1:17 AM
Ceilings falling with wires in it. jsmith3 Interior 8 3/16/06 8:24 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 2:52 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts