  #1  
Old 3/22/09, 1:45 PM
Ron S. De Mott Ron S. De Mott is online now
InterNACHI Member
 
Join Date: Oct 2008
Location: northern N.J.
Posts: 62
Default using 120v on a 240v breaker ?

Hey guys thanks in advance on this one. If a 120 volt well pump is wired to only half of a 240 volt breaker and nothing is attached to the other lug, its just empty, is this a acceptable practice. The reason that was given was that in the future a 240 volt pump can be installed. I let this go on a job, as I have done this myself in the past. Is there any hazard ?, does it overload the circuit to the pump? Will the breaker still work if there is a short? Thanks Ron
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #2  
Old 3/22/09, 2:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: using 120v on a 240v breaker ?

No problem. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 3/26/09, 6:50 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: using 120v on a 240v breaker ?

Aren't breakers rated in AMPS?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 3/26/09, 9:15 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: using 120v on a 240v breaker ?

Well yes, the protection rating of any general purpose breaker is in amps. I am assuming the question did not concern the ampacity rating of the breaker vs the load, but rather whether it is ok it use only one pole of a two pole breaker (which it is). Wasteful, but ok.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 3/26/09, 9:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: using 120v on a 240v breaker ?

He should have said a "two-pole breaker" rather than a 240V breaker, but I think I understood the question. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/26/09, 9:42 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: using 120v on a 240v breaker ?

I think your answer was clear.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 3/26/09, 10:38 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: using 120v on a 240v breaker ?

Ahh, now I get it.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Breaker Question rsole Electrical Inspections 6 11/23/08 9:57 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 7:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts