Default Using approved methods for PVC runs

All joints between lengths of rigid nonmetallic conduit "PVC", and between conduit and couplings, fittings, and boxes, shall be made by an approved method.

Does this mean that it doesn't have to be glued when it is buried?

Can the AHJ allow duct tape?
Reply With Quote
  #2  
Old 3/18/08, 10:46 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 619
Default Re: Using approved methods for PVC runs

I just recently built a shop and when I ran my conduit the code inspector made it clear to me to it needed to be glued, there was no mention of tape.
I know you know this already but in my limited knowledge of electrical, water can penetrate the tape right? thats why he said to glue it. I cant imagine that tape would ever be approved IMHO



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #3  
Old 3/18/08, 11:03 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Using approved methods for PVC runs

PVC typically uses a solvent cement. When the pieces that have glue applied and are joined, the PVC pieces actually melt into each other. This allows for a water tight coupling.

There are some cements that allow ABS and PVC to be directly glued. My recommendation is to use a PVC somvent cement.
Reply With Quote
  #4  
Old 3/18/08, 11:03 AM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Using approved methods for PVC runs

It gets glued from what I have seen around here. Water as Troy said will get in otherwise, as you know.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #5  
Old 3/18/08, 11:06 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

Water will get in anyway. Either from a joint or from condensation.
An underground PVC run is a WET location.

I think to suggest anyone would allow "duct tape" or not gluing is absurd. I think the suggestion was a bit facetious.
Reply With Quote
  #6  
Old 3/18/08, 12:00 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Using approved methods for PVC runs

These are different adhesives from E-Z Weld Manufacture
It appears that homeowners could use the all around Multipurpose Cemnt and manage to do their thing.

My recommendation would be to use the cement designed for the particular purpuse.

208 Multi Purpose Cement

Plumbing Plenty to choose from eh.

Click on any above and see their properties and differences.


Marcel
Reply With Quote
  #7  
Old 3/18/08, 12:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

Joe is looking for 110.3(B). The manufacturer's instructions call for a solvent welded connection, as often as not the solvent they sell. OTOH you will probably be using an expansion fitting on long runs and that is a slip joint.
A Pete says, all outdoor and underground raceways are wet locations and usually accumulate water over time. A hole in the pipe is as likely to be letting water out as letting it in. Most installers will drill holes in boxes to let the water out
Reply With Quote
  #8  
Old 3/18/08, 12:27 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

"an Approved" should be changed to "a Listed," not being facetious at all!

Greg got it right, I am just asking the same question asked of me today here in Delaware.

Marcell: Thank you too, for the information.
Reply With Quote
  #9  
Old 3/18/08, 12:40 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

Quote:
Originally Posted by jtedesco1
Greg got it right, I am just asking the same question asked of me today here in Delaware.
So someone actually asked you if duct tape was ok to use???

To someone like that you just say: "Yes. Yes it is." and walk away.
Reply With Quote
  #10  
Old 3/18/08, 2:09 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

OK, I will also tell them to "Go and get me the adjustable needle nosed pliers and a can of steam!"
Reply With Quote
  #11  
Old 3/18/08, 2:29 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Using approved methods for PVC runs

Quote:
Originally Posted by jtedesco1
OK, I will also tell them to "Go and get me the adjustable needle nosed pliers and a can of steam!"
Hey, Joe, don't forget them to add two eggs and their radiator problem and duck tape on the radiator hose are gone.

So ofcourse it is alright to join two pipes with just wires in it.

Marcel

Reply With Quote
  #12  
Old 3/18/08, 2:31 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using approved methods for PVC runs

Quote:
Originally Posted by jtedesco1
OK, I will also tell them to "Go and get me the adjustable needle nosed pliers and a can of steam!"
That's the spirit!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Liability question jcahill Legislation, Licensing & Legal Issues for Inspectors 30 8/24/08 4:10 PM
New Policy for approved Education Providers and those seeking approval jfarsetta Inspection Education & Training 1 2/10/08 6:47 PM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Ceilings falling with wires in it. jsmith3 Interior Inspections 9 3/16/06 7:24 PM


All times are GMT -4. The time now is 7:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts