CABINETS AND CUTOUT BOXES (CYIV)






GENERAL






This category covers sheet-metal boxes and nonmetallic boxes. Cutout boxes are provided with a door secured by hinges and one or more fasteners and are intended for surface mounting. A cabinet consists of two parts: a cabinet box and a mating cabinet front that contains a door.
A cabinet may be flush mounted or surface mounted. These boxes are intended for installation in accordance with Article 312 of ANSI/NFPA 70, ‘‘National Electrical Code.’’

So a panel cover is not correct and although Deadfront is used the term here is the correct term, I must say.

PS: Anyone who wants me to review their electrical narratives can send them to me and let me BOLD the suggestions I have, so that when talking to a electrician the same language will be spoken.














Last edited by jtedesco1; 1/11/08 at 12:48 PM..
Reply With Quote
  #2  
Old 1/11/08, 5:02 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Using Correct Electrical Terms in Reports

It is important that inspectors know both the correct terms, and that they use terms the clients are familiar with. Clients know what a panel cover is, most would not know a deadfront if you slapped them with it.

Our job is not just knowledge, it is the effective communication of that knowledge.

I can't tell you how many of my clients rever to the service panel as "the fuse box"...



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 1/11/08, 5:17 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by bwiley
It is important that inspectors know both the correct terms, and that they use terms the clients are familiar with. Clients know what a panel cover is, most would not know a deadfront if you slapped them with it.

Our job is not just knowledge, it is the effective communication of that knowledge.

I can't tell you how many of my clients rever to the service panel as "the fuse box"...
That is correct Blaine, and that is how I describe things Electrically because I don't know the proper term myself. ha. ha.

I think that today's common knowledge, we can also start using the breaker box and they would understand. ha. ha.

Marcel
Reply With Quote
  #4  
Old 1/11/08, 5:44 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Using Correct Electrical Terms in Reports

I may get some reddies for saying it. But I use terms that my clients understand. With all respect to the electricians, if the terminology that I use in my reports seems amature to them, I couldn't care less. If I call something out, I want my "lay person" client to understand it as best they can. I just want the electrician to fix it.

PS. Please don't get me wrong. Joe I sincerely appreciate the lessons you are giving us here, as well as the proper terminology. But please don't get too upset if you don't see me using the proper terms all the time.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 1/11/08, 5:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by bwiley
Our job is not just knowledge, it is the effective communication of that knowledge.
Worth repeating. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/11/08, 6:13 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Using Correct Electrical Terms in Reports

Absolutely.

The ability to EFFECTIVELY communicate what we observe is KEY. The exactly correct terminology is secondary to the conveyance of the INFORMATION.

I am sure that a technocrat could correct me all day long with some of the technically "incorrect" electrical terminology I use. Dont get me wrong, it aint WAY out there. I'd rather use descriptive language, and common terms, that my clients can understand. The NEC terminology can be quite confusing. Since I am not writing the report for an electrical engineer, who really cares anyway.

But, ask one of my clients if they understand the condition I am reporting on. They will say "yes". TO that end, the electrician who uses the report to Confirm and repair the condition also understands what was written.

Report writing is an art, and not a science. We must never forget this.
Reply With Quote
  #7  
Old 1/11/08, 6:37 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: Using Correct Electrical Terms in Reports

We've had this discussion many times (message board, telephone and classroom).

Suffice it to say, if I were a vendor wanting to sell a class on electrical terminology, I would first have to create a market for it by convincing people it were necessary.

I think I can recall one particular vendor who taught an electrical course at one of our St. Louis chapter meetings make a point of what a master electrician "might think" if he read a report lacking in "electro-ese", if you will.

In my opinion, the ideal report will address the problem in language that a Soccer Mom can understand.

We don't write to impress....but to inform.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #8  
Old 1/11/08, 6:41 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using Correct Electrical Terms in Reports

Using street logo is OK, I only wanted to remind the industry that the people who think you are jokes are sometimes electricians, and inspectors who should be aware of your knowledge.

As many of you may remember, everyone thought that I said that a few years ago and was banned, but I didn't write that about the HI, his name is Ryan Jackson UT and he said that in his message on the other board now deleted.

If he says otherwise I will personally call him a Liar, I am really serious and will defend my position here.

I have stated in the past, and will again now that I believe the HI is a much better overall inspector than many I see today during my field trips, and at seminars. Its OK to say fuse or breaker, but I will include "overcurrent device", or its OK to say Panel Box but I will say "Panelboard in a cabinet."

My reason for this post, as were for others, was to set the stage for what you will see sometime soon on InterNACHI TV.

I was chained for over 7 hours, and could not get lunch or move away from the chair next to Nick while we discussed "Defect Recognition" and while we made electrical inspections through my eyes on the property and at a home.

I don't expect to make some of you "Old Dogs" learn any new tricks, but for those who who will come after us, we need to begin to elevate the image of the HI, I don't plan on stopping anytime soon, and since we are involved in the same areas, I will say that you will be better off knowing what the terms are so you can talk to a professional electrical person some of which are realy JOKES themselves!
Reply With Quote
  #9  
Old 1/11/08, 6:45 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by jtedesco1
Using street logo is OK, I only wanted to remind the industry that the people who think you are jokes are sometimes electricians, and inspectors who should be aware of your knowledge.
I remember when you were making us the butt of your jokes, Joe, on other professional message boards.

Your ideas of what home inspectors should be are very well documented.

I don't think you want to go there.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #10  
Old 1/11/08, 6:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by jtedesco1
Using street logo is OK, I only wanted to remind the industry that the people who think you are jokes are sometimes electricians, and inspectors who should be aware of your knowledge.

As many of you may remember, everyone thought that I said that a few years ago and was banned, but I didn't write that about the HI, his name is Ryan Jackson UT and he said that in his message on the other board now deleted.

If he says otherwise I will personally call him a Liar, I am really serious and will defend my position here.

I have stated in the past, and will again now that I believe the HI is a much better overall inspector than many I see today during my field trips, and at seminars. Its OK to say fuse or breaker, but I will include "overcurrent device", or its OK to say Panel Box but I will say "Panelboard in a cabinet."

My reason for this post, as were for others, was to set the stage for what you will see sometime soon on InterNACHI TV.

I was chained for over 7 hours, and could not get lunch or move away from the chair next to Nick while we discussed "Defect Recognition" and while we made electrical inspections through my eyes on the property and at a home.

I don't expect to make some of you "Old Dogs" learn any new tricks, but for those who who will come after us, we need to begin to elevate the image of the HI, I don't plan on stopping anytime soon, and since we are involved in the same areas, I will say that you will be better off knowing what the terms are so you can talk to a professional electrical person some of which are realy JOKES themselves!
Well said Joe. Thank you and worth repeating.

Marcel
Reply With Quote
  #11  
Old 1/11/08, 6:50 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by jbushart
I remember when you were making us the butt of your jokes, Joe, on other professional message boards.

Your ideas of what home inspectors should be are very well documented.

I don't think you want to go there.
Jim:

Stop and think about what I have contributed here and bury the hatchet!.
Reply With Quote
  #12  
Old 1/11/08, 6:52 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by jtedesco1
Using street logo is OK, I only wanted to remind the industry that the people who think you are jokes are sometimes electricians, and inspectors who should be aware of your knowledge.
Joe,

Perhaps you don't understand that many of US in the home inspection industry are the ones who think many of the tradesmen are "jokes". Not all of them, perhaps not many of them, but we've certainly come across them.

I have written up FPE panels for a thorough exam by a qualified electrician and been rebuked because there is no issue with FPE panels. I have written up neutral/ground terminations under the same terminal and been rebuked. I have written up many, many other incorrect items installed by electricians, plumbers, roofers, framers, HVAC contractors, etc., that I know were incorrect, and my clients or the sellers have been told "he don't know what he's talking about". So, many HI's are of the opinion that the tradesmen are all too often too lazy to do it correctly.

The standard line from the lazy tradesmen who follow us to do the repairs comes in one of two fashions. A; That inspector doesn't know what he's talking about, or B; your inspector should have caught this.

So pardon me if many of us bristle when told some in the industry will think we're jokes if we don't use the proper terminology, or don't call out certain things, or beg to differ with someone who is not a home inspector, but this tenured inspector doesn't buy it.

I do appreciate the knowledge of the electric industry you possess, and also appreciate your willingness to share it with home inspectors. I for one though wish you would keep your posts relevant to what a competent home inspector will deal with during a standard visual home inspection.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #13  
Old 1/11/08, 6:56 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by bwiley
I do appreciate the knowledge of the electric industry you possess, and also appreciate your willingness to share it with home inspectors. I for one though wish you would keep your posts relevant to what a competent home inspector will deal with during a standard visual home inspection.
This is good advice, Joe.

I'm keeping my hatchet handy, for I am not convinced that you are "wired" any differently than you were three years ago.

This thread sends up a red flag, for sure.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #14  
Old 1/11/08, 7:19 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using Correct Electrical Terms in Reports

Quote:
Originally Posted by bwiley
Joe,

Perhaps you don't understand that many of US in the home inspection industry are the ones who think many of the tradesmen are "jokes". Not all of them, perhaps not many of them, but we've certainly come across them.

I have written up FPE panels for a thorough exam by a qualified electrician and been rebuked because there is no issue with FPE panels. I have written up neutral/ground terminations under the same terminal and been rebuked. I have written up many, many other incorrect items installed by electricians, plumbers, roofers, framers, HVAC contractors, etc., that I know were incorrect, and my clients or the sellers have been told "he don't know what he's talking about". So, many HI's are of the opinion that the tradesmen are all too often too lazy to do it correctly.

The standard line from the lazy tradesmen who follow us to do the repairs comes in one of two fashions. A; That inspector doesn't know what he's talking about, or B; your inspector should have caught this.

So pardon me if many of us bristle when told some in the industry will think we're jokes if we don't use the proper terminology, or don't call out certain things, or beg to differ with someone who is not a home inspector, but this tenured inspector doesn't buy it.

I do appreciate the knowledge of the electric industry you possess, and also appreciate your willingness to share it with home inspectors. I for one though wish you would keep your posts relevant to what a competent home inspector will deal with during a standard visual home inspection.
Wait for the TV show and watch Nick and I discussing the defects and there may be about 6 if they are prepared.
Reply With Quote
  #15  
Old 1/11/08, 7:47 PM
Ryan C. Jackson Ryan C. Jackson is offline
New User
 
Join Date: Jan 2008
Posts: 9
Please Note: Ryan C. Jackson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Using Correct Electrical Terms in Reports

You're right Joe, a while back I did post a comment at another forum stating that home inspectors were a joke. This is/was based on many experiences with them. At the time that I had written that, I had not met a single HI that wasn't a joke. The one that worked for the buyer of my old home that I was selling wrote "violations" that even my wife knew were inaccurate. She called me at work, I went home and met him with several code books, and showed the guy how wrong he was.

I have also had several home owners call me at my office (I work as a municipal inspector) after an HI had visited their homes, and they told me how terrible my cities inspectors are. I visit their house, see their "violations" and give the owner and HI code references showing that they are not violations.

Now, having said all of that, I have since met some HIs that do very good work, and are well versed in not only quality/workmanship issues, but code issues as well.

...so...I did say that HIs are jokes. If I could recant that, I would say that many HIs are jokes...but many municipal inspectors are jokes as well. Search the internet for degenerate inspectors that are taking bribes, or doing hundreds of inspections a day. Those people give me a bad name just like many HIs give you guys a bad name.

Joe called me today, and we had a nice talk. He asked me if I would visit the site and emphasise the fact that it indeed was me that stated that HIs are jokes. Indeed, those were my words.

Edited for spelling.

Last edited by Ryan C. Jackson; 1/11/08 at 7:55 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 3:00 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
Electrical Fire Safety jtedesco1 Electrical Inspections 3 2/1/08 10:02 AM
Electrical Terms & Cable Glossary pabernathy Electrical Inspections 7 3/9/07 10:18 PM
Electrical Safety Principles pabernathy Electrical Inspections 8 1/1/07 2:13 PM


All times are GMT -4. The time now is 5:06 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts