Looking for suggestions on how to verify bonding of gutters, panels and appliances. What tool do you use. Thanks
Reply With Quote
  #2  
Old 8/8/08, 9:20 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Verify bonding

My eyes. And I didn't know a gutter needed to be bonded.

If I don't see a bond at a panel box, I say this: "An electrical bond of cabinet and ground was not apparent. A bond should be confirmed by a licensed electrician."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 8/8/08, 9:35 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 525
Default Re: Verify bonding

Good ol Texas Standards. They say verify bonding at gutters. A new guy asked me what to do and I said "Huh"? Gutters (I believe they are more appropriately called wireways) are found in large homes, multi family or commercial. Hardly ever see wireways on the average home. The Texas rule implies one must remove the gutter cover. I don't know many that do that. Its dangerous on energized equipment. Anyway, I am still looking for any comment to make me smarter or dumber.

Duh in Texas
Reply With Quote
  #4  
Old 8/8/08, 9:45 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Verify bonding

John, I may be wrong but I think this is going to require all Texas HI's to invest in a Ideal Industries SureTest Circuit Analyzer with a:


Quote:

#61-175 Ground Continuity Adapter

This adapter allows the operator to verify that a cabinet or equipment chassis has been properly bonded to the system ground. Plugging the SureTest into the ground continuity adapter isolates the SureTest from the electrical ground. If the equipment is properly grounded, then connecting the alligator clip from the ground continuity adapter to the cabinet or equipment chassis should provide a pathway to ground, and consequently a normal wiring condition on the SureTest.
After the ground continuity adapter has been connected, the SureTest can be used to measure the ground impedance of the cabinet or equipment chassis back to the panel. See the section on Line Impedance Measurements for test instructions for ground impedance.




Reply With Quote
  #5  
Old 8/8/08, 10:13 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 525
Default Re: Verify bonding

Now that's funny Mike. I have been using that for 24 years now. I took a beat up 3 prong tester and plugged it into a 2 prong adapter. Soldered lead onto 2 prong ground tab. I plug it into a grounded receptacle and touch everything with the alligator clip. If the tester lights up its bonded. Real ugly but works. There are more professional tools but the old ones are fun. I also used a zip lock bag full of water to seal off shower drains. Cheap but works great. See attachment.
Attached Thumbnails
verify-bonding-snag-0003.jpg  
Reply With Quote
  #6  
Old 8/8/08, 10:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Verify bonding

Quote:
Originally Posted by mboyett
John, I may be wrong but I think this is going to require all Texas HI's to invest in a Ideal Industries SureTest Circuit Analyzer with a:

#61-175 Ground Continuity Adapter
You mean to tell me, you don't already have one?
Attached Thumbnails
verify-bonding-p8080001.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 8/8/08, 11:11 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 525
Default Re: Verify bonding

Oh man Jeff, your either very tidy or ya aint never used it. They work great however.
Reply With Quote
  #8  
Old 8/9/08, 12:11 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Verify bonding

I use the alligator clamps regularly, but I've never had the need to use the other one. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 8/10/08, 8:35 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Verify bonding

Quote:
Originally Posted by jpope
You mean to tell me, you don't already have one?
Nope, never had the need for one. Maybe now though. Jeff, can you tell me if a SureTest Circuit Analyzer will measure ground impedance of a chassis using only the adapter and alligator clip to the chassis? In other words, the SureTest would not be plugged into an outlet anywhere nor any other electrical connection made from or to the SureTest...only the alligator clip to the chassis. Will the SureTest be able to perform a ground impedance test under those conditions? How does the SureTest read out in that mode? An Ohms measurement I assume, right?
Reply With Quote
  #10  
Old 8/10/08, 11:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Verify bonding

I'm not sure I understand what you're asking Mike. The SureTest will give no measurement without an energized connection.

With an energized connection, it will give the ground impedance when using those adapters, which is measured in ohms.

I use the alligator clips often when I can't visually verify the bond at the service equipment, but all three must be connected to get the reading. An unbonded cabinet will simply give an "open-ground" indication.

Measuring and interpreting the impedance might be where the TX requirement gets hung up. Just "verifying" the bond does not mean that the bond is proper or adequate.

If a bond is present, but has 4 ohms of impedance/resistance, is it really a "bond?"

How about considering the SureTest itself. You may get a reading of 0.03 ohms. However, the current used by the SureTest is not measured or displayed, so there's no real way to verify that the bond is sufficient enough to clear a "high-current" fault.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 8/10/08 at 11:56 AM..
Reply With Quote
  #11  
Old 8/10/08, 12:07 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Verify bonding

Quote:
Originally Posted by jpope
The SureTest will give no measurement without an energized connection.
OK, that is what my 'electronics testing' background was telling me but that is not how the SureTest instruction manual reads. What I am looking for is to be able to hold a test device in my left hand and touch the appliance chassis with a probe and the test device would ensure bonding to ground. I know that's asking a lot but it is not technically impossible but maybe cost prohibitive.

There will be controversy and a learning curve as we (Texas HI's) determine exactly what the new proposed SOP will require and how we will accomplish that. This is just one of several instances.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Neutral bus bar failed inspection Greg Moritz Electrical 18 1/19/08 2:53 PM
Bonding Piping 101....Good To Know ! pabernathy Electrical 37 4/28/07 12:25 PM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 5:22 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts