Default Voltage Drop

My question pertains to using a SureTest or similar instrument for testing voltage drop.

According to the pamphlet I have it states the NEC recommends no more then a 5% voltage drop.

It also states that a higher voltage drop leads to heat buildup and performance issues.

What percentage would you recommend evaluation by a licensed electrician?

What are the causes for higher voltage drops.

How would you report high voltage drop.


Thanks
Reply With Quote
  #2  
Old 9/5/07, 11:09 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by dmacy
My question pertains to using a SureTest or similar instrument for testing voltage drop.

According to the pamphlet I have it states the NEC recommends no more then a 5% voltage drop.

It also states that a higher voltage drop leads to heat buildup and performance issues.

What percentage would you recommend evaluation by a licensed electrician?

What are the causes for higher voltage drops.

How would you report high voltage drop.


Thanks
Sorry I am an retired Electrician and I do not see where I as a home inspector should be doing voltage testing so I do not test for voltage drop.

.......... Cookie
Reply With Quote
  #3  
Old 9/5/07, 11:22 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: Voltage Drop

Quote:
Originally Posted by rcooke
Sorry I am an retired Electrician and I do not see where I as a home inspector should be doing voltage testing so I do not test for voltage drop.

.......... Cookie
Same here.


You might want to consider a consultation for doing voltage drops.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 9/5/07, 12:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Voltage Drop

I do

First thing to remember is, the NEC statement is a "Permissive Rule," and not a "Mandatory Rule." Simply put, this is not an "enforceable code."

Generally, excessive VD is an indication of high resistance within a circuit.

I don't have time this morning to get into this, but I'll check back later. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 9/5/07, 1:08 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: Voltage Drop

You have apply a bit of common sense to such findings.

A 10% drop at the end of AWG 14 outlet circuit in the far corner of a McMansion may not be evidence of a wiring "defect".

The same voltage drop 20' from the service equipment and half way down a string of kitchen counter outlets suggest there is a problem.
Reply With Quote
  #6  
Old 9/5/07, 3:49 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 476
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by mthomas2
You have apply a bit of common sense to such findings.

A 10% drop at the end of AWG 14 outlet circuit in the far corner of a McMansion may not be evidence of a wiring "defect".

The same voltage drop 20' from the service equipment and half way down a string of kitchen counter outlets suggest there is a problem.
Using #14 for long wire runs is a defect by itself.
Reply With Quote
  #7  
Old 9/5/07, 5:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,032
Default Re: Voltage Drop

I agree Ron.

Reporting on voltage drops can get you into trouble. I would suggest that anyone considering this, educate themselves first.

The first consideration is the line voltage. If the voltage at a given receptacle is 125V, a 10% drop with a 15 amp load is not necessarily a "big deal," as this will have little effect on appliances because you still have 112.5V at the receptacle. However, if your initial voltage reading is in the 110V range, a 10% drop may cause problems with some appliances.

A large variation in VD at receptacles on the same circuit is more of a concern (IMHO). All receptacles on the same circuit should generally have similar drops when a load is applied. A big difference could indicate a poor connection or worse.

There's much more to understand before attempting to accurately interpret voltage drop measurements and I'm not the one you should be learning from

Maybe some of our resident experts will chime in. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 9/5/07, 5:38 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by rdawes
Using #14 for long wire runs is a defect by itself.


That might not be a good rule to live by. I have installed lights such as those in the photograph as far as 700 feet away using #14 UF cable.




The door operator that is used on this gate could plug into a receptacle that is on that same circuit and not be hurt due to a voltage drop.




The amount of voltage drop is proportionate to the load it is serving.

Something else that needs to be considered is the voltage that the power company is supplying.

Here at my home, most of the time, I can read as high as 124 volts through out the house. I am the sole user of the transformer supplying my house.

My brother shares his transformer with a couple of others and I have saw his at 114 volts especially on a real hot or cold day.

Last edited by Mike Whitt; 9/5/07 at 5:43 PM..
Reply With Quote
  #9  
Old 9/5/07, 8:01 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by Mike Whitt

That might not be a good rule to live by.
Not only is it not a good rule to live by, it is totally false.

Someone who is not well versed on the subject may consider it an opinion that is it not good, but there would be NO factual information to support it. At least in the blanket way it was presented.

Quote:
Originally Posted by rdawes
Using #14 for long wire runs is a defect by itself.
Replace "is" with "could be" and you are making a more reasonable statement.
Reply With Quote
  #10  
Old 9/5/07, 8:31 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,361
Default Re: Voltage Drop

I would not run any motor on a 14 wire, especially a 700' 14 wire. It may appear to be okay, but it will have a premature death. I would not use and high wattage bulbs either. Some times those gate lights only use 15 watt bulbs. I hate to be one but if you're having to ask these type of questions, you might not want to report on VD, it is not part of a home inspection. JMO
Reply With Quote
  #11  
Old 9/5/07, 8:51 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by klott
I would not run any motor on a 14 wire, especially a 700' 14 wire.
That gate operator is a 12 volt DC system and has a trickle charger that plugs into a general purpose receptacle.

With two 40 watt bulbs and the little charger that is around 75 watts the total draw on the circuit would only be 115 watts and would not be a very large voltage drop at all.

A very big misconception about voltage drop can be hushed with the only mandatory calculation for a Voltage Drop found in the NEC

695.7 Voltage Drop.
The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage) under motor starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor.
Reply With Quote
  #12  
Old 9/5/07, 9:08 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Voltage Drop

Proper use of a volt meter is not something that requires a person with a lot of training

Voltage drop percentage is not hard to compute if you did not sleep through high school math 101

Measure the no load voltage

Measure the voltage under load

Do the math

-------

To check the drop to the home

Turn everything off - read the voltage at the panel

Turn everything on - read the voltage at the panel

-----

Yes, this is out side of a home inspection but not beyond the skill level of someone who can use a volt meter

-----

Remember that voltage drop % does not require one to load a circuit to its max rating -- just the current of what it is used for

That is why a long run of #14 to the gate lights is not a problem.

----

If one wants to go the next step - go and compute the % of voltage drop on #14 or #12 wire per 200 feet (or 1000 if you want) at rated current.

Having a feel for what readings should be is a good thing - at least if you see something that does not look good you can get on the NACHI BB and ask the experts

Remember that when the gage of wire is computed for a job all this math is done by someone that knows ohms law E=IR

A good electrician can teach this subject in one day

rlb
Reply With Quote
  #13  
Old 9/5/07, 9:36 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 476
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Quote:
Originally Posted by Speedy Petey
Not only is it not a good rule to live by, it is totally false.

Someone who is not well versed on the subject may consider it an opinion that is it not good, but there would be NO factual information to support it. At least in the blanket way it was presented.

Replace "is" with "could be" and you are making a more reasonable statement.
Peter,

In a home where the outlets are supposed to be able to deliver 15 amps, when is it OK for #14 to be used for long runs? All the calculators and tables I have seen show 5% drop (at 15 amps) in the wire alone for a 75ft run. Many larger (not mansion) homes may runs much longer than that by the time the wire is routed from the panel on one side to an upper bedroom on the opposite side. I don't consider 75ft to be a long run. Several cities in my area have banned use of #14 for new construction. Is it a problem when pulling 2 amps for a radio? Nope. But the outlets are rated for 15 amps.
Reply With Quote
  #14  
Old 9/5/07, 9:45 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

Are we home inspectors or are we trying to do an electricians job.
Where does it end.
Balancing Air handling units .
Size of the feed and return on AC.
Are the air ducts the correct size .
Do they have too many bends in the Dryer vent.
Is 1/2 pipe large enough for a gas demand water heater.
The choice is yours .
How long do you wish to spend on a visual Home Inspection.

..... Cookie
Reply With Quote
  #15  
Old 9/5/07, 9:58 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 476
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Voltage Drop

I for one, am not trying to do an electricians job but it doesn't take an electrician to go "wow, it's a long way from the panel to this bedroom" and then plug my SureTest into the outlet and see that it shows 22% voltage drop due to the long run of #14 wire and multiple backstabbed outlets in series. I then can suggest that qualified electrician be used to assure that it's really OK or to get it fixed. That gets the monkey off my back and lets me feel better about the situation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Stray Voltage can kill rcooke Electrical 24 10/26/07 12:40 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 8:22 PM
High voltage wsiegel Electrical 1 12/6/06 12:16 AM


All times are GMT -4. The time now is 3:44 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts