My question pertains to using a SureTest or similar instrument for testing voltage drop.
According to the pamphlet I have it states the NEC recommends no more then a 5% voltage drop. It also states that a higher voltage drop leads to heat buildup and performance issues. What percentage would you recommend evaluation by a licensed electrician? What are the causes for higher voltage drops. How would you report high voltage drop. Thanks |
|
#2
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
.......... Cookie |
|
#3
|
|||
|
|||
|
Quote:
You might want to consider a consultation for doing voltage drops. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#4
|
||||
|
||||
|
I do
First thing to remember is, the NEC statement is a "Permissive Rule," and not a "Mandatory Rule." Simply put, this is not an "enforceable code." Generally, excessive VD is an indication of high resistance within a circuit. I don't have time this morning to get into this, but I'll check back later. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
You have apply a bit of common sense to such findings.
A 10% drop at the end of AWG 14 outlet circuit in the far corner of a McMansion may not be evidence of a wiring "defect". The same voltage drop 20' from the service equipment and half way down a string of kitchen counter outlets suggest there is a problem. |
|
#6
|
||||
|
||||
|
Please Note:
rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
I agree Ron.
Reporting on voltage drops can get you into trouble. I would suggest that anyone considering this, educate themselves first. The first consideration is the line voltage. If the voltage at a given receptacle is 125V, a 10% drop with a 15 amp load is not necessarily a "big deal," as this will have little effect on appliances because you still have 112.5V at the receptacle. However, if your initial voltage reading is in the 110V range, a 10% drop may cause problems with some appliances. A large variation in VD at receptacles on the same circuit is more of a concern (IMHO). All receptacles on the same circuit should generally have similar drops when a load is applied. A big difference could indicate a poor connection or worse. There's much more to understand before attempting to accurately interpret voltage drop measurements and I'm not the one you should be learning from Maybe some of our resident experts will chime in. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
That might not be a good rule to live by. I have installed lights such as those in the photograph as far as 700 feet away using #14 UF cable. ![]() The door operator that is used on this gate could plug into a receptacle that is on that same circuit and not be hurt due to a voltage drop. The amount of voltage drop is proportionate to the load it is serving. Something else that needs to be considered is the voltage that the power company is supplying. Here at my home, most of the time, I can read as high as 124 volts through out the house. I am the sole user of the transformer supplying my house. My brother shares his transformer with a couple of others and I have saw his at 114 volts especially on a real hot or cold day. Last edited by Mike Whitt; 9/5/07 at 5:43 PM.. |
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Someone who is not well versed on the subject may consider it an opinion that is it not good, but there would be NO factual information to support it. At least in the blanket way it was presented. Quote:
|
|
#10
|
||||
|
||||
|
I would not run any motor on a 14 wire, especially a 700' 14 wire. It may appear to be okay, but it will have a premature death. I would not use and high wattage bulbs either. Some times those gate lights only use 15 watt bulbs. I hate to be one but if you're having to ask these type of questions, you might not want to report on VD, it is not part of a home inspection. JMO
|
|
#11
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
With two 40 watt bulbs and the little charger that is around 75 watts the total draw on the circuit would only be 115 watts and would not be a very large voltage drop at all. A very big misconception about voltage drop can be hushed with the only mandatory calculation for a Voltage Drop found in the NEC 695.7 Voltage Drop. The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage) under motor starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor. |
|
#12
|
|||
|
|||
|
Proper use of a volt meter is not something that requires a person with a lot of training
Voltage drop percentage is not hard to compute if you did not sleep through high school math 101 Measure the no load voltage Measure the voltage under load Do the math ------- To check the drop to the home Turn everything off - read the voltage at the panel Turn everything on - read the voltage at the panel ----- Yes, this is out side of a home inspection but not beyond the skill level of someone who can use a volt meter ----- Remember that voltage drop % does not require one to load a circuit to its max rating -- just the current of what it is used for That is why a long run of #14 to the gate lights is not a problem. ---- If one wants to go the next step - go and compute the % of voltage drop on #14 or #12 wire per 200 feet (or 1000 if you want) at rated current. Having a feel for what readings should be is a good thing - at least if you see something that does not look good you can get on the NACHI BB and ask the experts Remember that when the gage of wire is computed for a job all this math is done by someone that knows ohms law E=IR A good electrician can teach this subject in one day rlb |
|
#13
|
||||
|
||||
|
Please Note:
rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
In a home where the outlets are supposed to be able to deliver 15 amps, when is it OK for #14 to be used for long runs? All the calculators and tables I have seen show 5% drop (at 15 amps) in the wire alone for a 75ft run. Many larger (not mansion) homes may runs much longer than that by the time the wire is routed from the panel on one side to an upper bedroom on the opposite side. I don't consider 75ft to be a long run. Several cities in my area have banned use of #14 for new construction. Is it a problem when pulling 2 amps for a radio? Nope. But the outlets are rated for 15 amps. |
|
#14
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Are we home inspectors or are we trying to do an electricians job.
Where does it end. Balancing Air handling units . Size of the feed and return on AC. Are the air ducts the correct size . Do they have too many bends in the Dryer vent. Is 1/2 pipe large enough for a gas demand water heater. The choice is yours . How long do you wish to spend on a visual Home Inspection. ..... Cookie |
|
#15
|
||||
|
||||
|
Please Note:
rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
I for one, am not trying to do an electricians job but it doesn't take an electrician to go "wow, it's a long way from the panel to this bedroom" and then plug my SureTest into the outlet and see that it shows 22% voltage drop due to the long run of #14 wire and multiple backstabbed outlets in series. I then can suggest that qualified electrician be used to assure that it's really OK or to get it fixed. That gets the monkey off my back and lets me feel better about the situation.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Stray Voltage can kill | rcooke | Electrical | 24 | 10/26/07 12:40 PM |
| Light Bulbs- All Ya Wanna Know | pabernathy | Electrical | 9 | 4/18/07 8:22 PM |
| High voltage | wsiegel | Electrical | 1 | 12/6/06 12:16 AM |