Default Voltage drop

It is my understanding that a voltage drop greater than 5% is conducive to higher resistance which can lead to heat. Can you confirm this is an issue for GFCI protected branch circuits as well? Thanks.
Attached Thumbnails
voltage-drop-dscf3366-medium-.jpg.JPG
Views:	46
Size:	68.0 KB
ID:	29735  




Mark Nicholet
Apple Home Inspections LTD
My Blog

InterNACHI member
Infrared-Certified
CAHPI(BC) member
BC Licence # 47592
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #2  
Old 7/1/09, 5:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Voltage drop

Voltage drop is generally related to resistance, but should not be noted in these lower ranges unless there are interrelated issues. There has been much discussion about this, and I do report on excessive VD, but this particular reading wouldn't give me much concern.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 7/1/09, 5:57 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Voltage drop

Quote:
Originally Posted by jpope View Post
Voltage drop is generally related to resistance, but should not be noted in these lower ranges unless there are interrelated issues. There has been much discussion about this, and I do report on excessive VD, but this particular reading wouldn't give me much concern.

What do you generally consider excessive?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #4  
Old 7/1/09, 6:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Voltage drop

I don't get too excited until I start seeing drops in the range of 10% or more, but again, there needs to be additional concerns before I start deferring to Sparky.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 7/1/09, 6:14 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Voltage drop

Cool, thanks.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #6  
Old 7/1/09, 6:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Voltage drop

I think it's important to get some education/information before we arbitrarily start mentioning voltage-drops as an issue.

For instance;

In the original picture, even though the drop was measured at 9%, the voltage is still at 112V, which is well within the acceptable limits of any appliance or equipment that would use this outlet. Even at 15%, the voltage would have been near 105V, which is still acceptable in most cases.

Also, the drop was measured using a 15 amp pulse (actually a 12 amp pulse extrapolated for 15 and 20 amp loads), which is likely more than would actually be loaded on the circuit at any given time.

Now, if the original standing voltage was 105V, and there is a 12% drop with a 12 amp load, then we're looking at less than 93V, which may not be adequate for some equipment.

This is just one example. There are many variables to take into consideration when looking to report on VD during a home inspection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 7/1/09 at 7:31 PM..
Reply With Quote
  #7  
Old 7/1/09, 10:23 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Voltage drop

Excellent!

Thanks.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #8  
Old 7/2/09, 12:12 PM
Mark Nicholet's Avatar
Mark Nicholet Mark Nicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 404
Default Re: Voltage drop

Thank you




Mark Nicholet
Apple Home Inspections LTD
My Blog

InterNACHI member
Infrared-Certified
CAHPI(BC) member
BC Licence # 47592
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is the highest voltage drop you've worked around? gromicko Electrical 6 6/24/09 10:00 AM
Mention voltage drop? dbucknavich Electrical 18 6/18/08 7:58 PM
Supreme Court Upholds Ruling- Stray Voltage pabernathy Electrical 13 12/16/07 1:05 PM
Voltage Drop dmacy Electrical 51 9/7/07 10:57 AM


All times are GMT -4. The time now is 10:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts