Multiwire circuit on a wafer (twin) breaker. Neutral showed no sign of overheating. Your thoughts?
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
| Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
With that arrangement, the load on the neutral is additive of the loads from the hots (eg. #14 AWG.......9 amps on each hot = 18 amps at neutral). When each breaker is served from a different buss, the load on the neutral is the difference of the two (9 and 11 amps on hots = 2 amps on neutral). |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The photo is inconclusive. Do you know that both of those conductors on that CB, the red and black, are from the same cable?
|
|
#4
|
||||
|
||||
|
Brian Thanks - that's what I was thinking.
Robert - Yes - I traced them back to the cable where it entered the panel. The neutral showed no signs of overheating, but I guess it is likely to in the future. Thanks for your replies guys! "A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#5
|
||||
|
||||
|
It's wrong but you will not see any overheating since the multiwire circuits are typically low current such as disposal/dishwasher or gas furnace airhandler/attic lights etc.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#6
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
14-3 is used for kitchen countertop split receptacles here; a neutral on one of these circuits could easily be overloaded if hots are fed from the same buss and a couple of heavier drawing small appliances are being used!!
|
|
#7
|
||||
|
||||
|
Good info - Thanks Bruce.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
#14 AWG conductors would not be permitted on a SABC servicing counter receptacles since that circuit would be required to be 20 amps.
|
|
#9
|
||||
|
||||
|
20 amps according to current codes, but this house was built in the 60's.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#10
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
What does this stand for?
|
|
#11
|
||||
|
||||
|
Small Appliance Branch Circuit
Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Ahh, that makes more sense. |
|
#13
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Does the NEC not allow 15A, (3 wire) split countertop receptacles or is it all 20A circuits to the kitchen. Here there can be a mix depending on proximity to the sink (need 20A GFCI protected receptacles within 5')
|
| Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
All receptacles serving kitchen counter tops require GFCI protection regardless of their proximity to a sink. They also are required to be on 20 amp circuits when serving the counter top.
|
|
#15
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Article 240 : Overcurrent Protection Article | pabernathy | Electrical Inspections | 0 | 5/23/07 11:40 AM |
| Can an AFCI offer GFCI protection | gbeaumont | Electrical Inspections | 19 | 7/6/06 11:45 PM |