Default waste line over panel box

I was doing a home inspection on a new home (not finished yet). The waste line is running directly over the main panel box. Is this ok I've never seen it before and I cant fined any info on it. I know its not ok under ground but not sure in the home.
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/1/10, 4:51 PM
Rick Marton Rick Marton is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Paramus, New Jersey
Posts: 58
Default Re: waste line over panel box

Phillip, Here are the exceptions,then I will read the code. If they are going to install a suspended ceiling between the pipe and panel, then it would be okay. If they are going to install protection to avoid damage to the panel from condensation, leaks or breaks from the pipe, then it would be okay. I would ask the AHJ about the leak protection first. If not here is the code. 110.26 (F) (1)a-Dedicated Electrical Space- The space equal to the width and depth of the equipment and extending from the floor to a height of 6 feet above the equipment or to the structual ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping,ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone. I have chased plumbers out of that area a few times in the past. I tell them that they can move their pipes now, or after a failed inspection, move it later. Hope this helps Rick
Reply With Quote
  #3  
Old 3/1/10, 7:31 PM
Philip J. Cavalcante Philip J. Cavalcante is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Callaway, Md
Posts: 246
Default Re: waste line over panel box

Rick thanks for the help
Reply With Quote
  #4  
Old 3/2/10, 7:59 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: waste line over panel box

Here's the section that Rick touched on:

Quote:
110.26(F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.
Exception: Control equipment that by its very nature or because of other rules of the Code must be adjacent to or within sight of its operating machinery shall be permitted in those locations.
(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.
A suspended ceiling is permitted in the dedicated space but does not remove the prohibition for other foreign system within the 6' zone. In other words you cannot have a foreign piping system in the dedicated space simply because it's hidden by the ceiling. Condensation or leak protection is permitted if the foreign piping is directly above the 6' dedicated space.
Reply With Quote
  #5  
Old 3/3/10, 7:25 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: waste line over panel box

My guys fail electricians on this daily........My space fella...so get those plumin pipes out of it.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Sub Panel jharashinski Electrical Inspections 7 3/26/07 8:26 AM


All times are GMT -4. The time now is 7:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts