Default Water heater electric ?

Have a 3500watt water heater on a 20 amp double pole, 12 awg.
If my math is correct 3500watt/220v = 15.90 amp.
This shouldn't be an issue?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 7/18/08, 7:35 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

Nope, pretty common actually.

Thing is, your calc is off a bit. "220" is dead. Unless you know for fact that the nominal voltage is 220v, we use a more accurate 240v.

120/240v is nominal these days.

3500w / 240v = 14.58
Reply With Quote
  #3  
Old 7/18/08, 7:43 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Water heater electric ?

So Speedy, this setup should be ok?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 7/18/08, 7:45 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

Also a fixed storage-type water heater that has a capacity of 120 gallons or less shall be considered a continuous load so that would be 14.58 times 125% or a load of 18 amps
Reply With Quote
  #5  
Old 7/18/08, 7:46 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

Quote:
Originally Posted by nbhi
So Speedy, this setup should be ok?
yes
Reply With Quote
  #6  
Old 7/18/08, 7:47 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Water heater electric ?

Speedy
Should I also calculate the rating a 125%, which would be at 18.22 amps?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #7  
Old 7/18/08, 8:01 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

Per the NEC
Quote:
422.13 Storage-Type Water Heaters.
A fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall be considered a continuous load.

210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
Yes as it is required to be done.
Reply With Quote
  #8  
Old 7/18/08, 1:29 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

Yup, Mike gave all the pertinent info.
Reply With Quote
  #9  
Old 7/18/08, 8:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater electric ?

BTW these elements are rated at 240v, so if you really have 220v the watts will just be lower, by a factor of the square of the difference.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM


All times are GMT -4. The time now is 11:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts