Have a 3500watt water heater on a 20 amp double pole, 12 awg.
If my math is correct 3500watt/220v = 15.90 amp. This shouldn't be an issue? "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Nope, pretty common actually.
Thing is, your calc is off a bit. "220" is dead. Unless you know for fact that the nominal voltage is 220v, we use a more accurate 240v. 120/240v is nominal these days. 3500w / 240v = 14.58 |
|
#3
|
||||
|
||||
|
So Speedy, this setup should be ok?
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#4
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Also a fixed storage-type water heater that has a capacity of 120 gallons or less shall be considered a continuous load so that would be 14.58 times 125% or a load of 18 amps
|
|
#5
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
||||
|
||||
|
Speedy
Should I also calculate the rating a 125%, which would be at 18.22 amps? "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#7
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Per the NEC
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yup, Mike gave all the pertinent info.
|
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
BTW these elements are rated at 240v, so if you really have 220v the watts will just be lower, by a factor of the square of the difference.
|
![]() |