Is a water heater considered to be rated continuous duty and subject to 125% rating?
Thanks, Bill |
|
#2
|
||||
|
||||
|
Quote:
Yes, if it is 120 gallons or less, it is considered continuous duty and the water heater amps must not exceed 80% of the circuit conductor rating. (This is the same thing as 1.25 times the amps just said in a different way) An exception exists if you use a circuit breaker rated for continuous operation at 100% of its rating but these may not be readily available items. This was found via google and not direct from a code book but I doubt if this has changed any lately. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#3
|
||||
|
||||
|
Thanks Bruce,
That is what I thought. |
|
#4
|
|||
|
|||
|
That's why a typical 50 gallon heater has (2) 4500 watt elements that don't operate simultaneously - keeps the current well within the 80% limit for a 30 amp breaker.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#5
|
||||
|
||||
|
Quote:
Seems like it has a potential to be a higher demand than a 50 gallon unit. |
|
#6
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
(3800/240=15.83Ax1.25=19.79A) |
|
#7
|
|||
|
|||
|
I guess higher 'water' demand would not be an issue if we consider the unit to be continuous duty anyway. However, while 4300 watt elements would exceed 80% of a 20 amp circuit, 3800 would not. As a home inspector, I probably would not write up either if it appeared that the system had been operating ok for a lengthy period of time. In all this I am assuming the circuit ws a 20 Amp 240 volt circuit.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#8
|
||||
|
||||
|
Quote:
I put in the report that is was undersized and advised it be wired to a proper amp circuit. I may have verbally advised something realistic when they replaced the undersized and aged water heater that exhibited signs of previous leakage. Last edited by wthacker; 2/27/09 at 11:42 AM.. |
|
#9
|
||||
|
||||
|
You need to account for each element which are both over 4000 watts at 240VAC, exceeding the 20A rating. The rating was actually 4500/3380.
Last edited by wthacker; 2/27/09 at 11:38 AM.. |
|
#10
|
||||
|
||||
|
Why worry if it is not popping?
|
|
#11
|
||||
|
||||
|
What's realistic and what is "right" may be two different things at times.
Last edited by wthacker; 2/27/09 at 11:49 AM.. |
|
#12
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The thermostat relay is designed so that it can only energize one element at a time, when it makes at one, it breaks at the other. |
|
#13
|
||||
|
||||
|
Quote:
Anyway, what I was really trying to say was that when an element is energized, it would be drawing current in excess of the 125% rating if were rated at anything above 4,000 watts. I really don't know what I was thinking after that. (Medicine head) I think I adjusted my previous erroneous BS Brian. Bill |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Longevity of Conventional Water Heater Tanks. | lagudo | Plumbing Inspections | 8 | 9/7/08 6:13 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Water Heater Dip Tube Failure | jacaron | Plumbing Inspections | 2 | 2/24/07 11:28 PM |
| Need Help On Chimney Liners | Nick Scibetta | Exterior Inspections | 13 | 1/11/06 9:53 PM |