Default Water Heater minimum circuit is??

Is a water heater considered to be rated continuous duty and subject to 125% rating?

Thanks,
Bill
Reply With Quote
  #2  
Old 2/25/09, 8:27 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by wthacker View Post
Is a water heater considered to be rated continuous duty and subject to 125% rating?

Thanks,
Bill

Yes, if it is 120 gallons or less, it is considered continuous duty and the water heater amps must not exceed 80% of the circuit conductor rating.
(This is the same thing as 1.25 times the amps just said in a different way)

An exception exists if you use a circuit breaker rated for continuous operation at 100% of its rating but these may not be readily available items.

This was found via google and not direct from a code book but I doubt if this has changed any lately.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 2/25/09, 9:48 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Thanks Bruce,

That is what I thought.
Reply With Quote
  #4  
Old 2/25/09, 10:35 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Water Heater minimum circuit is??

That's why a typical 50 gallon heater has (2) 4500 watt elements that don't operate simultaneously - keeps the current well within the 80% limit for a 30 amp breaker.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 2/25/09, 11:10 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by fnewman View Post
That's why a typical 50 gallon heater has (2) 4500 watt elements that don't operate simultaneously - keeps the current well within the 80% limit for a 30 amp breaker.
This was a 30 gallon with if I recall correctly, was something lower, like 4300/3800 + or - some change. It was on a 20 amp breaker and wired with 12 wire.

Seems like it has a potential to be a higher demand than a 50 gallon unit.
Reply With Quote
  #6  
Old 2/26/09, 9:10 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by wthacker View Post
This was a 30 gallon with if I recall correctly, was something lower, like 4300/3800 + or - some change. It was on a 20 amp breaker and wired with 12 wire.

Seems like it has a potential to be a higher demand than a 50 gallon unit.
It's pretty important you know the KW rating before you go and write it up as being under sized. You say it might be 3.8KW, which would make it ok on a 20A ckt.
(3800/240=15.83Ax1.25=19.79A)
Reply With Quote
  #7  
Old 2/26/09, 9:51 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by wthacker View Post
This was a 30 gallon with if I recall correctly, was something lower, like 4300/3800 + or - some change. It was on a 20 amp breaker and wired with 12 wire.

Seems like it has a potential to be a higher demand than a 50 gallon unit.
I guess higher 'water' demand would not be an issue if we consider the unit to be continuous duty anyway. However, while 4300 watt elements would exceed 80% of a 20 amp circuit, 3800 would not. As a home inspector, I probably would not write up either if it appeared that the system had been operating ok for a lengthy period of time. In all this I am assuming the circuit ws a 20 Amp 240 volt circuit.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 2/26/09, 9:47 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by fnewman View Post
I guess higher 'water' demand would not be an issue if we consider the unit to be continuous duty anyway. However, while 4300 watt elements would exceed 80% of a 20 amp circuit, 3800 would not. As a home inspector, I probably would not write up either if it appeared that the system had been operating ok for a lengthy period of time. In all this I am assuming the circuit ws a 20 Amp 240 volt circuit.
The actual rating was 4500/3380. While what you say is correct for some instances, if an element is energized drawing anything over 4000 watts it exceeds the 20 amp continuous duty rating.

I put in the report that is was undersized and advised it be wired to a proper amp circuit. I may have verbally advised something realistic when they replaced the undersized and aged water heater that exhibited signs of previous leakage.

Last edited by wthacker; 2/27/09 at 11:42 AM..
Reply With Quote
  #9  
Old 2/26/09, 9:49 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by brian winkle View Post
It's pretty important you know the KW rating before you go and write it up as being under sized. You say it might be 3.8KW, which would make it ok on a 20A ckt.
(3800/240=15.83Ax1.25=19.79A)
You need to account for each element which are both over 4000 watts at 240VAC, exceeding the 20A rating. The rating was actually 4500/3380.

Last edited by wthacker; 2/27/09 at 11:38 AM..
Reply With Quote
  #10  
Old 2/26/09, 10:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by wthacker View Post
This was a 30 gallon with if I recall correctly, was something lower, like 4300/3800 + or - some change. It was on a 20 amp breaker and wired with 12 wire.

Seems like it has a potential to be a higher demand than a 50 gallon unit.
Why worry if it is not popping?
Reply With Quote
  #11  
Old 2/26/09, 10:41 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by relliott View Post
Why worry if it is not popping?
What's realistic and what is "right" may be two different things at times.

Last edited by wthacker; 2/27/09 at 11:49 AM..
Reply With Quote
  #12  
Old 2/26/09, 11:52 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by wthacker View Post
You need to account for two elements which are over 4000 watts, exceeding the 20A rating. The rating was actually 4500/3380.
William, the two KW ratings are for 240 volts and 208 volts, not for one or two elements. At 240 volts, your water heater uses 4500 watts, one element at a time. If both elements energized (which would be a malfunction), it would use 9000 watts.

The thermostat relay is designed so that it can only energize one element at a time, when it makes at one, it breaks at the other.
Reply With Quote
  #13  
Old 2/27/09, 11:48 AM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Water Heater minimum circuit is??

Quote:
Originally Posted by brian winkle View Post
William, the two KW ratings are for 240 volts and 208 volts, not for one or two elements. At 240 volts, your water heater uses 4500 watts, one element at a time. If both elements energized (which would be a malfunction), it would use 9000 watts.

The thermostat relay is designed so that it can only energize one element at a time, when it makes at one, it breaks at the other.
Thanks Brain.....I had a "duhhhh" moment there. I blame this terrible cold I have and the medication side effects.

Anyway, what I was really trying to say was that when an element is energized, it would be drawing current in excess of the 125% rating if were rated at anything above 4,000 watts.

I really don't know what I was thinking after that. (Medicine head)

I think I adjusted my previous erroneous BS Brian.

Bill
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Longevity of Conventional Water Heater Tanks. lagudo Plumbing Inspections 8 9/7/08 6:13 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/24/07 11:28 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 7:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts