Default Weather Heads

How close do you get?
Attached Thumbnails
weather-heads-601-bishop-7-.jpg.jpg
Views:	1380
Size:	77.9 KB
ID:	8069  
Reply With Quote
  #2  
Old 12/30/06, 10:47 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Hard to see on the picture, but there is some copper showing through.
Reply With Quote
  #3  
Old 12/30/06, 10:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

The neutral appears bare or partially bare, but that is okay. Some are installed bare to begin with. The hot legs don't appear to have any bare spots, but will certainly be brittle. Disturbing them can have some spectacular consequences if any of the insulation cracks off.

Given the apparent age of that installation, it's nearing the end of its service life anyway. Additionally, the inproper flashing around the service mast concerns me. That's a 20 year roof with 5 year Blackjack smeared around the mast. Hate to see that sort of work. A proper split boot should have been utilized when the roof was replaced last.
Reply With Quote
  #4  
Old 12/30/06, 11:00 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

The hot leg has a bare spot on it. About three inches long.
Reply With Quote
  #5  
Old 12/30/06, 11:33 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Quote:
Originally Posted by bkelly1
The hot leg has a bare spot on it. About three inches long.
There's no compliant repair method for that. Those service conductors have reached the end of their useful life, in that case. When they are (hopefully) replaced, that would be the ideal time to also pop off that weatherhead and install a proper boot to flash that service mast in properly. It might be worth noting that the service mast size (as in, pipe size; diameter) is too small according to most utility specifications nowadays for support of an aerial cable drop. I also note that the triplex wedge grip terminates directly around the mast without the proper fitting, called a 'mast rack' or 'one point rack' or 'mast insulator'. During a wind condition, this can permit the wedge grip bail to slide up and down on the mast, unnecessarily straining and possibly abrading the service conductors. This sliding action has obviously occurred in the past, as I note that the black paint is worn off the conduit in the area where the wedge grip bail moved up and down.

Last edited by Marc D. Shunk; 12/30/06 at 11:38 PM..
Reply With Quote
  #6  
Old 12/30/06, 11:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weather Heads

Ben,

It also appears that their are little or no drip loops on these conductors and what was the clearance from the service points to the actual roof itself. All these things need to be noted as well in ordered also build a basis for the client having it replaced.

But most certainly in the LEAST....defer for electrical evaluation.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 12/30/06, 11:45 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Ya, I posted the picture to see how close other inspectors get to weather heads, and why they should. My electrical license is still goog here in Tn, but thanks for all the replys.
Reply With Quote
  #8  
Old 12/30/06, 11:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weather Heads

Now see ben....if you had not inspected it...you could have picked up a few bucks fixing it...ahhh but now you can't...Conflict of Interest...

You are correct however....in that in the past seminars I ask guys if they actually check the mast head when available....90% did not until I explained to them it may be helpful in sizing the service...since most of the time the mast is under the installation habits of the Electrician and not the POCO..atleast it is where I come from....just installed one on Friday..

great picture and does serve to show guys......you have to be careful but most certainly they need to pop that ladder up and check the connections at the weatherhead....never know what you will find lurking their....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 12/30/06, 11:53 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Ya, I try not to fix them any more. THe going rate for an upgade to a 200amp service would be between 1000 to 1400. Not Enough for me and my talent. HA
Reply With Quote
  #10  
Old 12/30/06, 11:57 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

I also did 95 percent commercial and industrial. I never really liked doing residential wiring. My favorite job was probably a grocery store I did. There was more crammed into it than most factories I have wired. I also ejoyed remodeling 2 hospitals. The regular, emergency, critical, and life safety, branches of power made it very interesting. Not to mention all the generators.

I also did a data center for a bank. It was also crammed packed.
Reply With Quote
  #11  
Old 12/31/06, 12:06 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Here are some pictures from the last job that I did. THis is the job where I injured my shoulder. I will be having my 3rd surgery in January. Yes, I am dredding it already.

Reply With Quote
  #12  
Old 12/31/06, 12:07 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weather Heads

Wow...fella you have dabbled.

I have been primary in Residential since 1993 but before that I wired the Lexus building in Charlottesville, VA....they print law books and used to be Michie Publishing.

Had my fun with large CT Cabs and endless runs of 4" Rigid.....OH I am SOOO glad those days are gone...I kinda like residential but these days they are all high dollar homes and we are really getting into data control systems and home automation....neat stuff.

Now I did not mind doing the strip mall shops...did quite a few of those...man they are easy.....plans may give you 10-15 receptacles in the whole joint and mostly lighting and whamo....DONE......most of the time the engineering specs layed out our entire electrical plan.....no brainer just do what is on the print.

I like residential because I can be creative....yet use it to teach my guys also ...but winter is here.....not LIKING rough in's as of late....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 12/31/06, 12:08 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

OOPs, left out the picture.
Attached Thumbnails
weather-heads-2-bapt.jpg   weather-heads-2nd-baptist-ch0006.jpg   weather-heads-2nd-baptist-ch0012.jpg   weather-heads-2nd-baptist-ch0020.jpg   weather-heads-2nd-baptist-ch0039.jpg  

Reply With Quote
  #14  
Old 12/31/06, 12:10 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

and some.
Attached Thumbnails
weather-heads-2nd-baptist-ch0005.jpg   weather-heads-im000448.jpg  
Reply With Quote
  #15  
Old 12/31/06, 12:14 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weather Heads

Another weather head.
Attached Thumbnails
weather-heads-electric-curls.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
House Wrap brepanshek Exterior Inspections 26 10/4/08 10:45 PM
Sprinkler heads in Suspended Ceilings mcyr General Inspection Discussion 9 7/22/07 6:39 PM
Vinyl siding installation guide badair Exterior Inspections 18 3/27/07 6:38 PM
Weather head dmacy Electrical Inspections 3 2/8/06 8:19 AM


All times are GMT -4. The time now is 7:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts