Question Weatherhead help

Is this an allowed weatherhead? I've never seen one like it before.


Thanks,




Mike
Attached Files
File Type: pdf Weatherhead.pdf (41.2 KB, 297 views)
Reply With Quote
  #2  
Old 4/28/06, 9:16 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Weatherhead help

Hi Mike,

I too have not seen one quite like that, it seems to be serving its primary purpose and keeping water out of the service entrance, but it sure looks all wrong, plus I can't help but think that the conduit into the home is way too small for the conductors.

Maybe Paul or Joe can comment

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 4/28/06, 9:31 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weatherhead help

Mike and Gerry:

I will try to help.

Looks like an old weatherhead that was used for Type SE "Service Entrance Cable" because of the opening for a screw or bolt, and if so are the service entrance conductors in a conduit or still in the old SE cable?

The service entrance conductors are supposed to be visible before entering the meter socket enclosure, can we see the meter socket and the rest of the installation such as the main and panelboard, etc.?

I feel like there are many more issues we need to discuss.
Reply With Quote
  #4  
Old 4/28/06, 9:54 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Weatherhead help

Hi to all,

good call on the SE cable I missed it from the photo, I am guessing that it was relocated when an addition was put on the home.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 4/28/06, 9:58 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weatherhead help

Looks like a Job for the Enhanced Electro Paul Abernathy Squad on all points everywhere!

Go for it and get the Enhanced Super Duper Inspection for the same price today !

Last edited by jtedesco1; 6/15/06 at 12:35 AM..
Reply With Quote
  #6  
Old 4/28/06, 11:00 AM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Weatherhead help

The drip loop looks wrong too - the splices are at the bottom of the loop.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 4/28/06, 11:57 AM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weatherhead help

I agree with Joe more pictures.

Unfused conductors are "inside" the structure.

Where is the panel?
Reply With Quote
  #8  
Old 4/28/06, 1:10 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weatherhead help

Quote:
Originally Posted by jtedesco1
Looks like a Job for the Enhanced Electro Paul Abernathy Squad on all points everywhere!

Go for it and get the Enhanced Super Duper Inspection for the same price today !
Funny Man....lol......Always BUSTIN my balls fella...lol....

Anyway....looks to me like a SE Weather Head but what is NOT correct is the fact they dont mount onto conduit....they bolt to the wall and since it has conduit running from it....we cant see the connection point of this as it goes into the wall....

Now...considering it may be in pipe under siding.....can't really determine this from the images......Ok.....where is the Meter Cab located....???

As joe said....need images of the panel location inside as well.......otherwise I can give you the stock electricians thing......You need me to come and re-wire it.

Also the conduit looks way to small going into the wall and we need to be able to SEE this conduit......defer..defer..defer and have someone local get a close up look at it...



Paul W. Abernathy

Last edited by pabernathy; 4/28/06 at 1:41 PM..
Reply With Quote
  #9  
Old 4/28/06, 3:49 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Weatherhead help

Quote:
Originally Posted by jtedesco1
Mike and Gerry:

I will try to help.

Looks like an old weatherhead that was used for Type SE "Service Entrance Cable" because of the opening for a screw or bolt, and if so are the service entrance conductors in a conduit or still in the old SE cable?

The service entrance conductors are supposed to be visible before entering the meter socket enclosure, can we see the meter socket and the rest of the installation such as the main and panelboard, etc.?

I feel like there are many more issues we need to discuss.
I see this quite often where the Siding (Vinyl, Aluminum, Stucco, etc...) is installed over the Service Cable.

Is there a specific code reference to address this situation?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 4/28/06, 4:27 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weatherhead help

Quote:
Originally Posted by jhagarty
I see this quite often where the Siding (Vinyl, Aluminum, Stucco, etc...) is installed over the Service Cable.

Here you go Joe: From the 2005 NEC www.nfpa.org

Is there a specific code reference to address this situation?

230.6 Conductors Considered Outside the Building.




Conductors shall be considered outside of a building or
other structure under any of the following conditions:

(1) Where installed under not less than 50 mm (2 in.) of
concrete beneath a building or other structure

(2) Where installed within a building or other structure in a
raceway that is encased in concrete or brick not less
than 50 mm (2 in.) thick

(3) Where installed in any vault that meets the construction
requirements of Article 450, Part III




(4) Where installed in conduit and under not less than
450 mm (18 in.) of earth beneath a building or other
structure

Reply With Quote
  #11  
Old 4/28/06, 4:33 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Weatherhead help

As always....

Thank you very much for your prompt response and assistance.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #12  
Old 4/28/06, 4:41 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Weatherhead help

Quote:
Originally Posted by jhagarty
I see this quite often where the Siding (Vinyl, Aluminum, Stucco, etc...) is installed over the Service Cable.

Yes, that's what I see.
Reply With Quote
  #13  
Old 4/29/06, 11:50 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weatherhead help

Joe,

the 230.6 is more for classification of what is considered outside of a building when we are trying to consider if we need a Service Disconnect prior to the SE entering the dwelling.....

With the issue of SE being placed under siding( subject now to damage even more )....I feel it is more of a 230.50 is the better call here......"Protection of Open Conductors and Cables Against Damage- Above Ground "



Paul W. Abernathy

Last edited by pabernathy; 4/29/06 at 11:57 AM..
Reply With Quote
  #14  
Old 4/30/06, 6:35 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weatherhead help

Paul


230.50 covers the protection for Type SE cables and the list gives us various types of wiring methods that can be used. Some of them allow the SE to be sleeved for that protection.


When any SE conductors are concealed behind any surface they present a problem if the system faults at a pole top XFMR.

From the picture I see a service drop connected to the service entrance conductors (service point) that are "concealed" behind the siding, that's why I cited 230.6.
Reply With Quote
  #15  
Old 4/30/06, 8:54 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Weatherhead help

Joe,

No problem...as you stated before among those issues I am sure we can pull ALOT of references to why it is wrong....in the end I think the best course of action is to refer to the local Electrical Contractor......and they can get a UP CLOSE look at the problem...

But most certainly a defer..defer..defer issue for the HI



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this weatherhead placement OK? wdecker Electrical Inspections 20 12/28/07 8:15 PM


All times are GMT -4. The time now is 7:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts