Default Is this weatherhead placement OK?

Inspected a 3 unit condo (new construction) and the service drop goes to the weatherhead at the same level as the 2nd floor (my client's level) back porch deck.

I could easily reach out and tough the conductors without even touching the railing. Drip loop bottom was 4'11" above the porch deck floor level.

The back porch (structure) is steel and the decking is treated lumber.

Remember, this is in Chicago, where the porches themselves are dangerous
Attached Thumbnails
weatherhead-placement-ok-low_drop1.jpg   weatherhead-placement-ok-low_drop_2.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 10/18/06, 8:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Is this weatherhead placement OK?

I think you would be hard pressed to find anything prohibiting that installation except for maybe this. . .

Quote:
Drip loop bottom was 4'11" above the porch deck floor level.
I believe it needs 10 feet from the walking surface. However, I don't have my books in front of me right now.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 10/18/06, 8:27 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Is this weatherhead placement OK?

One point is that the POCO hooked up to it. You would think that they would not have if it was bad. Probably like the idea of not haveing to use a ladder or basket. Just connect it from the back porch.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #4  
Old 10/18/06, 8:37 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Is this weatherhead placement OK?

2003 IRC E3504.1 Clearance from building openings. Open conductors and multiconductor cables without an overall outer jacket shall have a clearance of not less than 3 feet (914mm) from the sides of doors, porches, decks, stairs, ladders, fire escapes and balconies, and from the sides and bottom of windows that open. See figure E3504.1
I can scan and post the figure if needed.
Reply With Quote
  #5  
Old 10/18/06, 8:47 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this weatherhead placement OK?

Michael, that code section is basically NEC verbatim. It applies only to conductors along side these areas.
Quote:
...not less than 3 feet (914mm) from the sides of...
The area in question, if applicable, would fall under NEC 230.9(B) & 230.24(B).

This requires 10' vertical clearance, and this 10' clearance must extend 3' out horizontally around the area.
Reply With Quote
  #6  
Old 10/18/06, 8:48 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this weatherhead placement OK?

Quote:
Originally Posted by wdecker
One point is that the POCO hooked up to it.
I agree and was thinking the same thing. Someone inspected it and passed it, or it would not have been hooked up.
Reply With Quote
  #7  
Old 10/18/06, 9:04 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Is this weatherhead placement OK?

Maybe I misunderstand the photo. I was under the impression that this picture was taken while standing on a 2nd floor balcony. The cables would then be somewhere around 15' off the ground below so the >10' requirement above a walkway would be met it would seem. Now, I'm not sure what the technicality is regarding 'sides of these areas'. It would sure seem to me that the cables don't meet that requirement at all. They are "along side of those areas", aren't they? If this photo is taken from ground level then never mind, my assumption is wrong.
Reply With Quote
  #8  
Old 10/18/06, 9:23 PM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Is this weatherhead placement OK?

Here is a similar one.

Stairway leads to access for a 2nd Floor apartment. Service cable is attached at the top of the Stairwell (Fire Escape) just above and to the left of the entry door.

This is After the Repair was Completed.

Work performed by a Licensed Electrician.

Permitted and Inspected by the Local Municipal Inspector.

Underwriter Seal from the Independent Electrical Inspector was affixed to the Main Panel confirming code compliance.

What say you?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:35 PM..
Reply With Quote
  #9  
Old 10/18/06, 9:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Is this weatherhead placement OK?

Great repair Joe

I would hate to see what it looked like before the "repair."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 10/18/06, 9:39 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this weatherhead placement OK?

Here is a the Handbook graphic showing a very similar setting:
Attached Thumbnails
weatherhead-placement-ok-drawing1.jpg  
Reply With Quote
  #11  
Old 10/18/06, 9:51 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is online now
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default Re: Is this weatherhead placement OK?

While not as bad as William's it is just another example of what the poco can do because they can. bottom of drip loop is just under 8' 6"
Attached Thumbnails
weatherhead-placement-ok-jsw_img_0962.jpg  



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #12  
Old 10/18/06, 10:10 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Is this weatherhead placement OK?

Quote:
Originally Posted by Speedy Petey
I agree and was thinking the same thing. Someone inspected it and passed it, or it would not have been hooked up.
Petey;

Just because the 'apparently' inspected it andpassed it and hooked it up, does not, necessarily, mean it is right.

This is Chicago, for goodness sakes!

When was the last time that a POCO or a municipailty (at least around here) was held liable for not doing thinsg according to their own code.

Answer: Never.

Different areas, different codes and no one takes responsibility.

Except good home inspectors.

Hope they are NACHI home inspectors.

(That ought to please Nick, eh .)



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #13  
Old 10/18/06, 11:09 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this weatherhead placement OK?

Some inspectors may not be aware of the code sitations that have been posted.

This is a very good question by the OP and as an inspector myself, I would not pass any of the 3 different situations presented by the different posts here on this thread.
Good catch by you guys!
Reply With Quote
  #14  
Old 10/18/06, 11:16 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Is this weatherhead placement OK?

To clarify. One picture was taken from the ground level and the other one from the 2nd floor porch level.

Sorry for the lack of clarity.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 10/18/06, 11:23 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this weatherhead placement OK?

Quote:
Originally Posted by wdecker
Petey;

Just because the 'apparently' inspected it andpassed it and hooked it up, does not, necessarily, mean it is right.
Sorry, it seemed that came out wrong.
I was pointing out that even though it is an obvious violation it was still hooked up.

It is truly amazing some of the things I see that were "just inspected" by an AHJ.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
saddle valve placement relliott Plumbing 11 9/7/07 11:22 AM
Condenser placement gheller HVAC 10 4/21/07 11:25 AM
Weatherhead help mmorgan Electrical 14 4/30/06 9:54 AM


All times are GMT -4. The time now is 9:47 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts