Default Weird GFCI

Any ideas on this. Two year old house. Kitchen GFCI tripped normally with my tester unless I was plugged into the actual GFCI. Then, no trip. The built in test button on the GFCI worked fine. Never seen this before. What would cause it?



Keith Runquist, CMI
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/22/10, 12:52 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weird GFCI

Not grounded.
Reply With Quote
  #3  
Old 4/22/10, 12:56 AM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Weird GFCI

Bingo Bob...I see it all the time.
Reply With Quote
  #4  
Old 4/22/10, 3:08 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Weird GFCI

That's why you always test the actual GFCI outlet. Sometimes they show up grounded, but still don't trip. Who knows why. I write it up stating that it would not trip using a dedicated GFCI test device.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 4/22/10, 5:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weird GFCI

Quote:
Originally Posted by krunquist View Post
Any ideas on this. Two year old house. Kitchen GFCI tripped normally with my tester unless I was plugged into the actual GFCI. Then, no trip. The built in test button on the GFCI worked fine. Never seen this before. What would cause it?
Does this mean that it would trip when you tested downstream devices but not the actual GFCI receptacle itself? If so, I agree with the others, the GFCI receptacle itself is un-grounded.
Reply With Quote
  #6  
Old 4/22/10, 5:35 AM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weird GFCI

There is no reason for a 2 year old house to have an ungrounded receptacle.
Reply With Quote
  #7  
Old 4/22/10, 8:11 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Weird GFCI

I know Joe said he didn't know why, but does anyone else know why that doesn't show up as ungrounded on the tester?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 4/22/10, 8:32 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weird GFCI

It can be set up as a false ground .
The others may actually be grounded.
Reply With Quote
  #9  
Old 4/22/10, 11:02 AM
rturner's Avatar
rturner rturner is offline
New User
 
Join Date: Sep 2004
Location: Talbott, TN
Posts: 12
Please Note: rturner is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weird GFCI

Quote:
Originally Posted by belliott View Post
Not grounded.

A GFCI monitors the amount of current flowing from hot to neutral. If there is any imbalance, it trips the circuit. In some areas, upgrading 2 prong outlets (in older homes with a 2 wire electrical system) with 3 prong GFCI outlets is acceptable. Without a ground, a GFCI should still trip. Something else is causing it not to trip.

Some GFCI testers can simulate too weak an electrical "leak" or imbalance to trip some GFCI's.

Did it trip when you mashed the test button?
Reply With Quote
  #11  
Old 4/22/10, 6:19 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Weird GFCI

Quote:
Originally Posted by belliott View Post
False ground.
I cant believe I am about to say this but, I...I....I..........agreewithBob.
Reply With Quote
  #12  
Old 4/22/10, 6:37 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weird GFCI

Quote:
Originally Posted by jlevy1 View Post
I cant believe I am about to say this but, I...I....I..........agreewithBob.

Yes...Yess...Yessssssss
Join me.ha...haaa.haaaaaaa!
Reply With Quote
  #13  
Old 4/22/10, 6:42 PM
rturner's Avatar
rturner rturner is offline
New User
 
Join Date: Sep 2004
Location: Talbott, TN
Posts: 12
Please Note: rturner is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Weird GFCI

Sorry guys, I happen to disagree. The GFCI does not use the equipment grounding conductor in the sensing circuit. A GFCI will protect non-grounded circuits and according to the NEC Sec. 210-7(d), GFCI can replace two-wire (ungrounded) receptacles.

Being ungrounded should not cause a GFCI NOT to trip. However, I am still not sure why the downstream outlets will trip but not the first, and I don't see how being ungrounded or having a false ground would cause this either. Please explain!
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/22/10, 8:01 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Weird GFCI

Quote:
Originally Posted by Jim Port View Post
There is no reason for a 2 year old house to have an ungrounded receptacle.
Sloppy work would do it.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 4/22/10, 8:05 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Weird GFCI

Bob, do you think it might not be grounded?!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 7:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts