Here is a weird one. I recently replaced my two-prong receptacles with three prong self-grounding receptacles. I have armored cable with the strip so there is a good ground through the wall box.
Nevertheless, I tested all the receptacles for a ground using a three light thing which I know most of you detest. Most of the receptacles showed a ground. Two did not, on the same circuit. On this cicruit I installed a GFCI receptacle protecting the second receptacle as well. Here is the weird bit. Now the three light tester shows a ground. What could I have got wrong with the original installation? If I installed the load and line the wrong way round on the original receptacles would this have caused the grounding problem (surely not since neither was a GFCI)? Or did I attach the wrong neutral to the live on the wall box where there were two sets of wires (but why would this matter on non-GFCI receptacles)? Or is the GFCI showing a ground? Now that would be silly. Last edited by Ian Gills; 6/27/07 at 4:48 PM.. |
|
#2
|
||||
|
||||
|
Most likely oxidation on a ground connection somewhere.
When you installed the GFCI and tested it with the tester you sent enough current through the ground to cause the resistance to change enough to show a light on the tester. Have you noticed the "ground" light on the tester is dimmer than it should be? B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#3
|
|||
|
|||
|
Please Note:
Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Bruce.
|
|
#4
|
||||
|
||||
|
How did you bond the three-prong receptacles?
tom |
|
#5
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#6
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 4:10 PM |
| Demystify Grounding & Bonding Class | pabernathy | Inspection Education & Training | 5 | 12/24/06 1:10 AM |