Default Were double-taps ever "legal"?

I was just wondering if double-taps were ever within the rules of the NEC. The reason I'm asking is that I, like every good home inspector, call out any double-taps I find and recommend that they be further evaluated by a qualified electrician and/or repaired. Mostly, the double-taps are lighting circuits.

When the electrician checks it out, the feedback I get from the sellers and/or buyers falls into two categories:

1. The electrician says that it definitely is a violation of the current NEC and should be changed immediately and offers to repair it, etc..

2. The electrician says that it definitely is a violation of the current NEC, BUT says that since it is original wiring and was done under previous code regulations, it not required to be changed at this time. He does add that if the breaker, at some point, needs to be changed then the double-tap is required to be repaired. He, of course, recommends that it be repaired at this time but does not push the issue.

I, personally, have heard electricians say the same thing about GFCI receptacles in kitchens: they are not required to be changed unless the receptacle needs to be changed, then it must be replaced with a GFCI receptacle or a GFCI breaker installed. They do, of course recommend GFCI's as a matter of safety.

I live in an area where aluminum wiring was used - Henry Kaiser development in the '70's. I have heard the same argument regarding the wiring: it should be replaced with copper or properly spliced (Copalum) with copper pigtails, etc.. However, it is not required to have every resident in the area do this.

My inspection reports always say I recommend further evaluation of double-taps, etc., by a qualified electrican, and that I recommend installation of GFCI equipment for safety. I do not say it is required to be repaired/replaced by code. Should I be saying that - or more correctly, CAN I be saying that.

Thanks for any replies!
Reply With Quote
  #2  
Old 2/26/07, 4:56 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Were double-taps ever "legal"?

Regardless of code, past - present - future, double taps are unsafe and should be called out, IMO.

Do not refer to code in your reports unless you want to be held accountable for any code violations that you may have missed.

Additionally, it is not unusual to have 3 AHJs looking at the same concern and not making the same ruling. A "violation" to one is okay to the next. You are safer to stay away from referencing it, altogether.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 2/26/07, 5:10 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Were double-taps ever "legal"?

Some panels and breakers are made to take two same sized conductors (Square D for example). And since they are made for two condictors it is not considered as "double tap" or defect.
Reply With Quote
  #4  
Old 2/26/07, 5:14 PM
ghawley ghawley is offline
New User
 
Join Date: Mar 2006
Location: Honolulu, HI
Posts: 12
Please Note: ghawley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Were double-taps ever "legal"?

Good advice. I have not been quoting code of any sort just for that reason. In retrospect, I was probably asking the question more for my own understanding. I'm an electrical engineer by education - which in no way qualifies me as an electrician - and that engineering curiosity just has to be satisfied...
Reply With Quote
  #5  
Old 2/26/07, 5:17 PM
ghawley ghawley is offline
New User
 
Join Date: Mar 2006
Location: Honolulu, HI
Posts: 12
Please Note: ghawley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Were double-taps ever "legal"?

Yup, I know about the Square D breakers. I was wondering about a regular breaker with just the screw and no plate where double-tapping is clearly not within code regulations.
Reply With Quote
  #6  
Old 2/26/07, 6:02 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Were double-taps ever "legal"?

Gary,
I would explain it to my customers just exactly like you did in your original post. Then I would still refer it (in my report) to a licensed electrician to make the final determination and if they decide not to correct it, recommend the buyers get that in writing for their records. You have then done your job and the homeowners have assumed the responsibility to going the extra step and you are out of the loop on the decision.
Reply With Quote
  #7  
Old 2/26/07, 6:30 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Were double-taps ever "legal"?

Double taps like these?

were-double-taps-ever-legal-suc50987-small-.jpg.JPG
Views:	122
Size:	48.8 KB
ID:	9526 were-double-taps-ever-legal-suc50990-small-.jpg.JPG
Views:	135
Size:	40.6 KB
ID:	9527


This was in an old duplex I inspected yesterday, with all this they still only got 120V to the range upstairs, and left dangling HOT knob and tube in the crawl space.
Reply With Quote
  #8  
Old 2/26/07, 8:12 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Were double-taps ever "legal"?

I'd red flag the paint contamination of that panel and its overcurrent devices. That alone, would be good cause for me as an electrician to replace that panel.
Reply With Quote
  #9  
Old 2/26/07, 9:44 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Were double-taps ever "legal"?

Same problem exists with neutral wires

rlb
Reply With Quote
  #10  
Old 2/27/07, 2:34 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Were double-taps ever "legal"?

As Richard stated above ... double lugging is a no no

Last edited by cduphily; 6/10/08 at 11:33 PM..
Reply With Quote
  #11  
Old 2/27/07, 3:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Were double-taps ever "legal"?

Quote:
Originally Posted by lcapaul
Attachment 9526 Attachment 9527
This was in an old duplex I inspected yesterday, with all this they still only got 120V to the range upstairs, and left dangling HOT knob and tube in the crawl space.
I assume you know that you're looking at a Federal Pacific Stab-lok Load Center? As Marc indicated, this is one that should be replaced. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 3/7/07, 11:53 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Were double-taps ever "legal"?

Quote:
Originally Posted by lcapaul
Double taps like these?

Attachment 9526 Attachment 9527


This was in an old duplex I inspected yesterday, with all this they still only got 120V to the range upstairs, and left dangling HOT knob and tube in the crawl space.
FPE panel link;
http://www.inspect-ny.com/fpe/fpepanel.htm
Reply With Quote
  #13  
Old 3/7/07, 5:03 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Were double-taps ever "legal"?

Here is one from today, old sq D split bus that has been modified to a sub panel, there is no single disconnect in house. We won't ever talk about what the attic wiring looked like. POS
Attached Thumbnails
were-double-taps-ever-legal-jsw_p1010099.jpg   were-double-taps-ever-legal-jsw_p1010101.jpg  



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Square D double taps abishop Electrical Inspections 3 10/29/06 9:01 AM
Double Taps... Here we go again rwand1 Canadian Inspectors 12 10/28/06 3:55 PM
Double taps Mike Parks Electrical Inspections 11 5/28/06 1:52 PM
Double Taps rwand1 Canadian Inspectors 39 3/29/06 7:16 PM
Double Taps psmothers Electrical Inspections 3 3/9/06 10:04 PM


All times are GMT -4. The time now is 7:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts