Default When were panels not allowed in clothes closets?

Panels were not permitted to be installed in clothes closets since 1981
Reply With Quote
  #2  
Old 2/27/06, 10:28 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Re: When were panels not allowed in clothes closets?

Joe,

As is usually the case, many localities (and States)and modular manufacturers lag behind by 1 or even two NEC revisions. I inspected a modular last week that was built in 1986 and had one panel in a second floor clotes closet.

It was a LSAP (sub-Panel)that had the grounds and neutrals bonded together but not to the panel.

UGLY.

TG
Reply With Quote
  #3  
Old 2/27/06, 10:59 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: When were panels not allowed in clothes closets?

I see some panels on bedroom walls in duplex type buildings.
Seems to be allowed in some counties at least.

Anyone know where this is not allowed?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 2/27/06, 11:50 PM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

Joe, just did a house in Tamarac, FL where just LAST WEEK they passed an electrical inspection for a addition to the home where the corport was turned into a efficiency...and the NEW panel was IN THE CLOSET and SIGNED OFF by the City Inspector.

Whats your take on this?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #5  
Old 2/27/06, 11:51 PM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

Oh...just in case it matters...it is a SUB-Panel.





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #6  
Old 2/28/06, 12:58 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: When were panels not allowed in clothes closets?

Harvey:

The final inspection may have been performed before the "closet" was built, or ???

Did you note it as a defect? If so, you have CYA!
Reply With Quote
  #7  
Old 2/28/06, 1:09 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Question Re: When were panels not allowed in clothes closets?

No Joe...It was passed 4 days before my inspection.

Can you paste a code refrence? Or any other data that would CMA?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #8  
Old 2/28/06, 1:14 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: When were panels not allowed in clothes closets?

240.24(D) Not in Vicinity of Easily Ignitible Material

Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.

Examples of locations where combustible materials may be stored are linen closets, paper storage closets, and clothes closets.

240.24(E) Not Located in Bathrooms In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.

www.nfpa.org
Reply With Quote
  #9  
Old 2/28/06, 1:19 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

Man...Joe that now brings into question one I did on Friday...they had the Main Load Center inside the bathroom vanity (I know 36" clearance) right over the sink...NOW WHAT?

I dont know when that was inspected...but I know that only 1 month ago they had an electrical inspection for a new gas generator...they would have had to have an electrical included...right?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #10  
Old 2/28/06, 1:58 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

Heres the foto regarding the bathroom panel...
were-panels-not-allowed-clothes-closets-elecpanelinvanity.jpg





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #11  
Old 2/28/06, 2:06 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

Quote:
Originally Posted by jtedesco1
240.24(E) Not Located in Bathrooms In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.
Joe call me crazy...but this code seems to be related to Rental MDU's, Hotels, and Motels!





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #12  
Old 2/28/06, 3:05 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: When were panels not allowed in clothes closets?

Dwelling Unit. A single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation.

Dwelling, One-Family. A building that consists solely of one dwelling unit.
Dwelling, Two-Family. A building that consists solely of two dwelling units.
Dwelling, Multifamily. A building that contains three or more dwelling units.
Reply With Quote
  #13  
Old 2/28/06, 3:10 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: When were panels not allowed in clothes closets?

What about this Joe?

Quote:
Originally Posted by hgordon
Man...Joe that now brings into question one I did on Friday...they had the Main Load Center inside the bathroom vanity (I know 36" clearance) right over the sink...NOW WHAT?

I dont know when that was inspected...but I know that only 1 month ago they had an electrical inspection for a new gas generator...they would have had to have an electrical included...right?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #14  
Old 2/28/06, 5:23 AM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Re: When were panels not allowed in clothes closets?

Harvey,

That's the medicine storage cabinet for bi-polar electric shock therapy.

TG
Reply With Quote
  #15  
Old 2/28/06, 5:42 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: When were panels not allowed in clothes closets?

Quote:
Originally Posted by hgordon
Heres the foto regarding the bathroom panel...
Attachment 1623
Inadequate working space in front of the equipment, and the panel is not permitted to be installed in a bathroom.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Distribution panels bking Electrical Inspections 2 3/11/07 11:29 AM
Main Panels in Closets rwashington Electrical Inspections 9 2/17/07 12:17 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 7:31 PM
Lampholders are not, and never were allowed in a clothes closet! jtedesco1 Electrical Inspections 0 2/6/06 11:38 AM