The home owner upgrade his main panel to 150AMPs. There is a new 1/0 conduit to the meter. I'm suspect the meter is limited to 100 AMPs and I need help to confim meter capcity. If 100 AMP want to make recommendations to upgrade to 200 AMP. Welcome comments.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/1/10, 8:21 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Westinghouse D2S 15TA meter AMP?

If wire is copper, it can service up to 175 amps. Reference Table 310.15(B)(6)of the NEC.

To determine meter capacity, examine the meter and meter base and take them into account. The elements to consider are:
  1. The size/rating of the service entrance conductors.
  2. The rating of the panel.
  3. The rating of the main breaker, if any.
  4. The rating of the meter base.
  5. The rating of the meter.
The weakest or smallest of these five items will determine the service ampacity of the system.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 11/1/10, 10:44 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Westinghouse D2S 15TA meter AMP?

While the meter-base may limit service size, the meter-rating has no bearing on the service capacity of the system. The meter rating identifies the capacity to which the meter has been calibrated.

I regularly see old, "15 amp" meters on modern 200 amp services.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/1/10, 12:01 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Westinghouse D2S 15TA meter AMP?

I doubt that the conduit is 1/0. 1/0 is a size for a conductor. Proper terminology helps greatly. Knowing the conductor material makes a difference too.
Reply With Quote
  #5  
Old 11/1/10, 5:15 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Westinghouse D2S 15TA meter AMP?

Quote:
Originally Posted by jbushart View Post
If wire is copper, it can service up to 175 amps. Reference Table 310.15(B)(6)of the NEC.

To determine meter capacity, examine the meter and meter base and take them into account. The elements to consider are:
  1. The size/rating of the service entrance conductors.
  2. The rating of the panel.
  3. The rating of the main breaker, if any.
  4. The rating of the meter base.
  5. The rating of the meter.
The weakest or smallest of these five items will determine the service ampacity of the system.
If the meter is utility owned then it's their responsibility to install the proper meter.
Like Jeff said item #5 doesn't really matter, and it will not change the size of the service.
Reply With Quote
  #6  
Old 11/1/10, 7:47 PM
John Scaparo John Scaparo is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Canton, MI
Posts: 309
Default Re: Westinghouse D2S 15TA meter AMP?

The conductor is 1/0 Copper.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
  #7  
Old 11/1/10, 8:08 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Westinghouse D2S 15TA meter AMP?

Quote:
Originally Posted by jscaparo View Post
The conductor is 1/0 Copper.

As James mentioned 310.15(B)(6) allows you to used reduced size conductors for 120/240 volt, 3-wire, single phase dwelling services and feeders. #1/0 Cu conductors are good for up to 175 amps in this application.


Curious as to why you think that a 100 amp service might require an upgrade to 200 amps?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
gas meter dyoung General Inspection Discussion 20 3/1/10 3:25 PM
Gas Meter dyoung AskNACHI.org Inspection Questions Forum 7 2/25/10 9:06 PM
CPSC -----> Recall on electric meter panels pbolliger Electrical Inspections 0 10/15/09 11:23 PM
Newer Westinghouse furnaces jweinberg Inspecting HVAC Systems 2 7/7/06 12:49 AM


All times are GMT -4. The time now is 7:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts