Where does it state, if anywhere, that a service disconnects shall be provided for water heaters within so many ft in the NEC??
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Quote:
(B) Appliances Rated Over 300 Volt-Amperes or 1/8 Horsepower. For permanently connected appliances rated over 300 volt-amperes or 1/8 hp, the branch-circuit switch or circuit breaker shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be installed on or at the switch or circuit breaker used as the disconnecting means and shall remain in place with or without the lock installed. NEC 422.31 (B) States that appliances over 300VA must have a disconnect within sight. Water heaters are directly referenced in Article 422. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
As far as the NEC is concerned "within sight" is defined as within 50 feet.
|
|
#4
|
||||
|
||||
|
Instead have them install a lock out device instead of a disconnect. Much cheaper and easier.
Comprehensive Building Consultants Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection. Donate here: or send checks to the Fl Home and Insurance Inspector Chapter 1103 W Hibiscus Blvd Ste 311 Melbourne, Fl 32901
|
|
#5
|
||||
|
||||
|
Thanks Mr Larson, and Robert.
Russell, you didn't answer my question. Now to get specific, when if any did this apply for water heaters? Meaning what year. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#6
|
||||
|
||||
|
I have a 1996 NEC and it is stated there...422-21b...that is the oldest NEC I have....want me to send you the pictures of the code? Been down that road before.
Comprehensive Building Consultants Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection. Donate here: or send checks to the Fl Home and Insurance Inspector Chapter 1103 W Hibiscus Blvd Ste 311 Melbourne, Fl 32901
|
|
#7
|
||||
|
||||
|
No thats fine. Everywhere is different, and my biggest problem is I am not 60 years old.
Most around here that are over 20 years never have one.. Its like s traps. Some are still putting them in, and then they say, "thats the way its always beeen done round here!" Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#8
|
||||
|
||||
|
I just note stuff like that and do not make a big deal out of it, if it is a common practice. 98% of all homes in my area have no weep holes in the brick. Do I make a big deal out of it? No. Do I note it in the report? You bet!
It is better sometimes to spend your time on battles you know you can win. Sad but true! Braun Inspection Consultants Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
|
|
#9
|
||||
|
||||
|
Quote:
Gets expensive especially when all the walkways are up higher than the foundation. |
|
#10
|
|||
|
|||
|
Quote:
You are 100% correct my friend. I always do have to remind people that within sight also means it has to be visible as well.....and not just the 50'. In Sight From (Within Sight From, Within Sight). Where this Code specifies that one equipment shall be “in sight from,” “within sight from,” or “within sight of,” and so forth, another equipment, the specified equipment is to be visible and not more than 15 m (50 ft) distant from the other. Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Home Inspector Listings | jbowman | Miscellaneous Discussion for Inspectors | 230 | 3/21/12 9:35 PM |
| Mold Inspectors in Coeur d’Alene, ID 83815 | rspriggs | Ancillary Inspection Services & Additional Topics | 15 | 1/3/12 1:14 PM |
| New Washington Legislation Submitted | gdomagala | Legislation, Licensing & Legal Issues for Inspectors | 294 | 2/10/08 1:20 AM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical Inspections | 5 | 12/4/06 2:40 PM |