Default Whats the normal temperature for breakers

I would like to know if any of you use infared to read the temperature of breakers?

What is temperature I should begin to question the condition of the breaker, or wiring attached to that breaker?
Reply With Quote
  #2  
Old 11/6/07, 4:11 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Whats the normal temperature for breakers

Hi ..I had a simular question regarding AFCI breakers the other day .
If that is what you are concerned about I found out they can run around 15 0r 20 degrees hotter.
Reply With Quote
  #3  
Old 11/6/07, 4:17 PM
James Taylor, 261 James Taylor, 261 is offline
New User
 
Join Date: Dec 2004
Posts: 6
Please Note: jtaylor5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Whats the normal temperature for breakers

Thats good information to have. Thanks.

I have never taken the temperature of a breaker. What should I expect to read from a typical breakers?
Reply With Quote
  #4  
Old 11/6/07, 4:30 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Whats the normal temperature for breakers

To be honest I will not get heavy into the temp thing, as it may be going overboard .I used my gun because I thought the AFCI's were overly hot.
We got enough to look at.
The Flir guys are more into that stuff as part of their routine.
Put it this way.
Say you run the gun and find a two degree variation.
OK now what?
If the dishwasher was just run before you got there will it affect your readings? You get my point.
Reply With Quote
  #5  
Old 11/6/07, 4:39 PM
James Taylor, 261 James Taylor, 261 is offline
New User
 
Join Date: Dec 2004
Posts: 6
Please Note: jtaylor5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Whats the normal temperature for breakers

I agree with not wanting to make more work for myself.
Reply With Quote
  #6  
Old 11/6/07, 4:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Whats the normal temperature for breakers

word
Reply With Quote
  #7  
Old 11/6/07, 4:56 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,281
Default Re: Whats the normal temperature for breakers

Quote:
Originally Posted by jtaylor5
I agree with not wanting to make more work for myself.
and possible liability
Reply With Quote
  #8  
Old 11/6/07, 5:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Whats the normal temperature for breakers

Breaker temperatures can vary from low to relatively hot. There really is no "normal" temperature. There are too many variables that would come into play.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 11/6/07, 5:14 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Whats the normal temperature for breakers

Quote:
Originally Posted by jpope
Breaker temperatures can vary from low to relatively hot. There really is no "normal" temperature. There are too many variables that would come into play.
I will agree with Jpope on this one.


I do take the temperature of the breakers too.,, but there are too many way to tell if this is normal or not.

kinda like a judgment call on breakers just like the example one breaker will be pretty close to 80 % full load it will show up very warm while other breakers is very low loaded so it will show cooler than others so there is not a really a excat guideline to determed if that is the breaker or connections is overheating you may have to check each one indually to determed if it is normal or not.

I am not sure which electrician in this fourm here do have specal camera to tell you the details [ not all of us have it ] so just want to be fair with you.

Merci, Marc
Reply With Quote
  #10  
Old 11/6/07, 5:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Whats the normal temperature for breakers

Exactly what I was saying.
Dead subject .
Reply With Quote
  #11  
Old 11/6/07, 5:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Whats the normal temperature for breakers

Quote:
Originally Posted by relliott
To be honest I will not get heavy into the temp thing, as it may be going overboard .I used my gun because I thought the AFCI's were overly hot.
We got enough to look at.
The Flir guys are more into that stuff as part of their routine.
Put it this way.
Say you run the gun and find a two degree variation.
OK now what?
If the dishwasher was just run before you got there will it affect your readings? You get my point.

Hi. Bob;

You guys with your fancy toys, ha. ha.

I can't afford that luxury, so I still take my electrical panels temperature the old fashion way.

Attachment 15842

Check temperature top and bottom of panels.

Temperature recorded at top= 72 degrees
Temperature recorded at bottom= 68 degrees.

I guess I am alright.

Improvise!!!!!

Marcel

Last edited by mcyr; 6/8/08 at 2:11 PM..
Reply With Quote
  #12  
Old 11/6/07, 5:54 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Whats the normal temperature for breakers

I do it the real old fashioned way, with the back of my fingers. If I can keep my fingers there comfortably, its not too hot.
Reply With Quote
  #13  
Old 11/6/07, 5:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Whats the normal temperature for breakers

Get your hands out of that live panel you goof.
Reply With Quote
  #14  
Old 11/6/07, 8:41 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Whats the normal temperature for breakers

All right, you guys win, I promise that innovations and technology will inherit the earth, so I will try to follow you guys in this new tool technology.







On average, approximately one third of all property losses are electrically related. Fully one fourth of those losses are caused by faulty electrical connections. In such cases, loose, dirty, damaged, corroded or oxidized connections and contacts inevitably lead to increased electrical resistance - generating heat and infrared energy as a result. Such problems, given sufficient time, inevitably result in fire or explosion.

Identifying electrical threats before they reach combustion or component failure temperatures is becoming increasingly more difficult due to the complexity of today’s building operation systems and control equipment. In addition, the sheer number of contactors, breakers, fuses, and other electrical service hardware make it virtually impossible to physically inspect, shut down, and tighten every electrical connection on any regular basis.

With occupant safety, energy conservation, minimal downtime and the protection of capitol equipment all being synonymous with proper maintenance, more and more building operators are turning away from occasional physical electrical checks in favor of the latest preventative maintenance technologies.




Infrared Thermography (IR) operates by measuring the infrared energy of any object’s surface and producing a detailed visual image showing its temperature profile. Since IR operates without physical contact, it offers building operators a safe, on-line, and cost-effective means to evaluate the electrical operation of any property. While many borderline problem areas typically remain undetected during an off-line physical inspection, they can be easily pinpointed using IR.

Infrared Thermography is ideally suited for detecting faults in electrical panels, breakers, switchgear, splices, insulators, starters, contactors, wiring, distribution systems, disconnects, and transformers, etc. With a lesser degree of reliability, IR can locate water leakage in roofs, steam trap malfunctions, ineffective HVAC air distribution patterns, motor and bearing defects, building energy loss, pipe blockages and underground pipe leakage - providing a visual representation of the heat generated or lost in almost any physical application.




The below series of photographs help show the potential of infrared technology, and why it is considered one of the most valuable nondestructive tools available. The control or standard photograph on the left helps to identify the source of the problem; the infrared image the problem.

In many cases, the highest temperature value and most defined point within an infrared photograph will identify the actual source of the problem - such as a single bolt, electrical component, or contact surface.






Knife Switch - Knife switch contacts present a constant maintenance problem to most older properties. Annual IR inspections of such properties typically find multiple contact problems which can only be repaired by shutting down the equipment, disassembly and cleaning of the contacts, reassembly, and re-tensioning. Upgrading with new disconnect equipment is recommended as the obvious long term solution.







Transmission Lines - This 460 volt tower between buildings showed a problem at an old splice. Temperatures were measured at near 300 degrees F., and had charred the nearby wire to bare metal. A combination of weathering, old age, and a less than acceptable wire splice ultimately produced this electrical problem.







Knife Switch - Knife switches and most types of sliding electrical contact always present the potential for hot spot problems. Add to them the moisture present in an outdoor environment and serious faults can result. In this example, the A phase of this disconnect switch was found exceeding 350 degrees F.




For most infrared inspections, a client's primary interest is to identify the hot spot locations presenting the most serious and immediate threat. However, other electrical and mechanical problems may exist which may also present a potential threat to reliable building and plant operations.

A typical IR inspection may identify panel doors damaged, mismatched or over rated fuses in place, indicator lights out, inoperative safety mechanisms, as well as various other forms of potential electrical or mechanical threats and liabilities. Unlabeled panels, while not in themselves an operating problem, would likely slow an emergency response to one.

Emergency automatic transfer switch (ATS) equipment, tested only in normal mode, would not guarantee proper operation during emergency power. Similarly, testing switchgear and starter panels under little or no load, such as often exists for momentary or standby equipment, would not likely show a problem. Identifying such equipment for special attention during future inspections, therefore, will greatly benefit any building or plant operation.

Marcel
Reply With Quote
  #15  
Old 11/6/07, 8:46 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Whats the normal temperature for breakers

Quote:
Originally Posted by jking2
I do it the real old fashioned way, with the back of my fingers. If I can keep my fingers there comfortably, its not too hot.
Exactly done it that way for almost 50 years and To test motors If you can keep your hand on it and count to ten its OK .
Some times you learn to count real fast then blow air on your hand.
.. Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Checking temperature of breakers bking Electrical Inspections 18 7/28/06 8:45 AM
A/C Temperature Differential cthorsen General Inspection Discussion 3 7/26/06 1:47 PM