Smile What's Wrong Here?



Three strikes and you're out! First, the junction box, located just below the panelboard, is missing its cover. Second, there are open, unused spaces in the panelboard. And third, the circuit directory in the panelboard is not properly filled out.

As per 314.25, each box in a completed installation is required to have a cover, faceplate, lampholder, or luminaire (fixture) canopy, except where the installation complies with 410.14(B). In addition, unused openings for circuit breakers and switches are required to be closed using identified closures, or other approved means that provide protection substantially equivalent to the wall of the enclosure (408.7). And the requirements of 110.12(A) call for you to cover unused cable or raceway openings in boxes, raceways, auxiliary gutters, cabinets, cutout boxes, meter socket enclosures, equipment cases, or housings so they are effectively closed, thus affording protection substantially equivalent to the wall of the equipment.

Although it’s a little difficult to see, the panelboard directory is blank. As per 110.22, each disconnecting means is required to be legibly marked to indicate its purpose, unless it’s located and arranged so the purpose is evident. The marking is required to be of sufficient durability to withstand the environment involved. And the requirements of 408.4 state, “Every circuit and circuit modification must be legibly identified as to its clear, evident, and specific purpose or use. The identification shall include sufficient detail to allow each circuit to be distinguished from all others. The identification shall be included in a circuit directory that is located on the face or inside of the panel door in the case of a panelboard, and located at each switch on a switchboard.”
Reply With Quote
  #2  
Old 1/2/06, 9:51 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?

What's Wrong Here?
--
Reply With Quote
  #3  
Old 1/2/06, 9:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What's Wrong Here?

Hey Joe...good stuff.

Just a note...you may want to just paste some of that info here rather than linking members away from the actual nachi site. On some things it is probably fine but in most cases posting the images here and examples here may help the members even more.

Just a note is all my friend.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #4  
Old 1/3/06, 1:05 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: What's Wrong Here?

Quote:
Originally Posted by pabernathy
Hey Joe...good stuff.

Just a note...you may want to just paste some of that info here rather than linking members away from the actual nachi site. On some things it is probably fine but in most cases posting the images here and examples here may help the members even more.

Just a note is all my friend.
Paul:

Thanks very much for your suggestions. The links above were a quick copy and paste. I will try to avoid links of this type. The following information is the entire UL Directory and is much too large.

Do a right click and Save Target as a PDF file on your desktop

http://www.nachi.org/bbsystem/usrfil..._WhiteBook.pdf
Reply With Quote
  #5  
Old 1/1/07, 7:08 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's Wrong Here?

Overhead Service Drop Near Balcony

What will a visual observation identify for a report?

Reply With Quote
  #6  
Old 12/5/07, 2:14 PM
George P. Wells's Avatar
George P. Wells George P. Wells is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Sylvania, OH
Posts: 287
George P. Wells is generally well trusted George P. Wells is generally well trusted
Default Re: What's Wrong Here?

Quote:
Originally Posted by jtedesco1
Overhead Service Drop Near Balcony

What will a visual observation identify for a report?

Real estate agent's description in ad:

Beautiful balcony with environmentally friendly clothes dryer! Great location for bird watching!



BestInspectors.Net
By Inspectors, For Inspectors
www.BestInspectors.Net

Celebrating 16 Years!
established 1992
InspectorStore.com
Reply With Quote
  #7  
Old 12/5/07, 5:00 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's Wrong Here?

Quote:
Originally Posted by gwells
Real estate agent's description in ad:

Beautiful balcony with environmentally friendly clothes dryer! Great location for bird watching!
George:

I was reminded of the issues here so I developed the dirty dozen, -- right click on the microphone icon upper left and hear the short stories.

Last edited by jtedesco1; 12/8/07 at 10:00 AM.
Reply With Quote
  #8  
Old 12/6/07, 8:37 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's Wrong Here?

UPDATE:

Some of the links were broken, here's a new link for the articles and inspection tips posted during the last 10 years.

http://ecmweb.com/nec/whats_wrong_here/

http://www.youtube.com/v/HKjAmaH6xxk&rel=1

Last edited by jtedesco1; 12/6/07 at 9:09 PM.
Reply With Quote
  #9  
Old 12/8/07, 5:41 AM
Gary L. Porter's Avatar
Gary L. Porter Gary L. Porter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,296
Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute Gary L. Porter has a reputation beyond repute
Default Re: What's Wrong Here?

Thanks



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #10  
Old 12/9/07, 10:00 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,786
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: What's Wrong Here?

Thanks Joe!!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #11  
Old 12/9/07, 10:36 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's Wrong Here?

My pleasure!

Here's another update concerning post #4 above in this thread:

UL White Book, 2007 Edition
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Grandpa, what is wrong with the patio? mcyr Exterior 1 5/12/07 11:29 PM
Anything wrong with this? jweinberg Electrical 11 11/7/06 11:22 PM
What's wrong here? wwarner Structural 14 9/12/06 8:47 PM
Messy work, but is it wrong? mtimpani Electrical 8 9/9/06 10:56 PM
Anything Wrong Here? scosta HVAC 12 6/29/06 10:06 AM


All times are GMT -4. The time now is 7:30 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics