#1
|
||||
|
||||
|
One year old construction.
Guesses? Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#2
|
||||
|
||||
|
Well, the insulation within the box is certainly a problem.
There's at least one AFCI that won't operate as its neutral has become disconnected. Is there a bonding strap or screw attached to the neutral bus? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hahahahahaha!
That happens to other people too? Cool! I LOVE blown in! Can you tell? Oh yeah, it tastes real good too. Jeff, the bond is the bigger green 1/4-20 screw in the neutral buss at the top right. |
|
#4
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Quote:
Dale Duffy Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Scottsdale Home Inspectors, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You didn't show a picture looking up but I bet there is either a raceway "chimney" into the attic with the RX in it or there are some missing knockouts and a chase. How did the insulation get down there?
BTW I would write up that shreaded newspaper as a defect if I saw it but that may just be a Florida thing. Here it will turn into grey mud in 5 years. In Florida the vapor barrier should be OVER the insulation, particularly if it is going to absorb water. Our warm moist air is outside, not inside like you folks with a winter. Insulation like this becomes a sponge. |
|
#7
|
||||
|
||||
|
I am with Greg....is their a conduit ran to the attic for future? As I have seen many blow ins but never have I seen it fill the panel like this without a knockout missing or a PVC Conduit running to the attic...and the installer leaving it too short as to not make it ABOVE the blown in.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#8
|
||||
|
||||
|
It was in a garage, the third car single garge. The homeowner had had the builder close in and insulate this as an extra room. There was fiberglass blown in the attic, so I am assuming this was what they put in the walls for insulation.
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#9
|
||||
|
||||
|
lol....well they got HAPPY with it......no doubt...
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| What is wrong with this electrical panel? | gromicko | Electrical Inspections | 45 | 12/11/07 1:13 PM |
| Wrong screws on panel front | kgraham | Electrical Inspections | 12 | 4/5/07 6:26 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |