Question What's wrong with this picture?

Anyone see the problems?
Attached Thumbnails
whats-wrong-picture-113-jefferson-rd.-high-shoals-ga.-draw-ins.-023.jpg   whats-wrong-picture-113-jefferson-rd.-high-shoals-ga.-draw-ins.-020.jpg  



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America)
  #2  
Old 4/29/09, 4:52 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 931
Default Re: What's wrong with this picture?

Yea, Someone left a piece of re-rod and a water bottle in the middle of the floor... What were they thinking!!!
Reply With Quote
  #3  
Old 4/29/09, 4:54 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,361
Default Re: What's wrong with this picture?

See anything else?



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
  #4  
Old 4/29/09, 5:46 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: What's wrong with this picture?

How far are the studs apart

Last edited by wwilson3; 4/29/09 at 6:18 PM..
Reply With Quote
  #5  
Old 4/29/09, 5:54 PM
Andrew Rook Andrew Rook is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 202
Default Re: What's wrong with this picture?

Lack of green wood?



Andrew Rook
NJ Home Inspector
License # 24GI00063600

Rook Home Inspections LLC
Hamilton NJ
(609) 588 - 0125
www.RookInspections.com
www.MercerCountyHomeInspection.com

Be Smart, Be Sure, Be Inspected TM
Reply With Quote
  #6  
Old 4/29/09, 6:00 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 931
Default Re: What's wrong with this picture?

#1 Re-rod is not approved for a grounding rod. It is not adequately buried anyway. Should be outside.
#2 Correct me if I'm wrong, but I don't think the wood is womanized. and it is on contact with a concrete floor.
#3 Unsecured wiring. 12-2, prob for an outside outlet, put a few staples in it.
#4 If this is an outside wall, why the heck didn't they use cellulose??

Last edited by mroberson; 4/29/09 at 6:03 PM..
Reply With Quote
  #7  
Old 4/29/09, 6:20 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: What's wrong with this picture?

I think i see a 2x4 stuck under the concrete
Reply With Quote
  #8  
Old 4/29/09, 6:25 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's wrong with this picture?

That piece of rebar may be the turned up stub from a Ufer ground.
Reply With Quote
  #9  
Old 4/29/09, 8:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,035
Default Re: What's wrong with this picture?

Rebar is used for grounding in almost all modern construction. It's referred to as a Ufer ground, and is the preferred method for grounding a system.

I see no problem here.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 4/29/09, 8:26 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 1,624
Default Re: What's wrong with this picture?

I see them often in access panels in garages. I've seen a couple in basements as pictured too.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
  #11  
Old 4/29/09, 8:32 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: What's wrong with this picture?

Quote:
Originally Posted by Jim Port View Post
That piece of rebar may be the turned up stub from a Ufer ground.
Exactly...I believe Jim's got it.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #12  
Old 4/29/09, 9:11 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's wrong with this picture?

Well, unless that wall is going to be built out some more, i do see a slight problem.
Reply With Quote
  #13  
Old 4/29/09, 10:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,035
Default Re: What's wrong with this picture?

Quote:
Originally Posted by Jim Port View Post
That piece of rebar may be the turned up stub from a Ufer ground.
You're correct Jim. Apparently your post hadn't been "approved" before I posted mine. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America)
  #14  
Old 4/29/09, 10:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,035
Default Re: What's wrong with this picture?

Quote:
Originally Posted by gevans2 View Post
The rebar stub up is for bonding the steel so there is not a difference of potential from other metal components of the home.
Actually Gary, that is the grounding electrode.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 4/29/09, 10:07 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 931
Default Re: What's wrong with this picture?

Just read up on an Ufer ground, Never needed it here, we have more water here than any other state
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Picture with text software? bforeman Hardware, Software & Publications 5 2/16/09 1:24 PM
www.FireDoorInspector.org gromicko Commercial 108 1/12/09 3:39 PM


All times are GMT -4. The time now is 6:42 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts