Default What's wrong with these panels?

Hopefully these pics are big enough to see the details. This main disconnect actually feeds 4 panels. The two included here are the ones I was most suspicious of. The one sub-panel is double tapped at the mains and the mains. What else do you see?

Thanks for any input.
Attached Thumbnails
whats-wrong-these-panels-joy-davis-pics-004.jpg   whats-wrong-these-panels-joy-davis-pics-002.jpg   whats-wrong-these-panels-joy-davis-pics-005.jpg  
Reply With Quote
  #2  
Old 3/21/07, 6:10 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: What's wrong with these panels?

At first, I though this might have been a rubber band, but I guess it's "just"copper wire.
Attached Thumbnails
whats-wrong-these-panels-joydavispic.jpg  

Last edited by mthomas2; 3/21/07 at 6:45 PM..
Reply With Quote
  #3  
Old 3/21/07, 6:40 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: What's wrong with these panels?

Just for starters in this one little area of one load-side panel, in addition to what you have already noted:

1) What's separating (insulating) the bare copper wire from the one above where they cross over above the left-hand breakers?

2) For that matter, what's that bare wire doing connected to the grounded (neutral) conductors over to the left of the left-hand breaker?

3) In any case, is the left-hand breaker listed for that panel?

4) There is (at best) marginal connections at top of both left hand breakers.

And it's just what I can see offhand in this one corner of one panel... I would suggest deferring the entire electrical system to an exorcist.
Attached Thumbnails
whats-wrong-these-panels-joydavispic5.jpg  

Last edited by mthomas2; 3/21/07 at 6:49 PM..
Reply With Quote
  #4  
Old 3/21/07, 11:00 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: What's wrong with these panels?

BTW, what's the correct term for the device being used to split the connections the breakers?
Reply With Quote
  #5  
Old 3/22/07, 12:20 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,035
Default Re: What's wrong with these panels?

The orange breakers are Zinsco's



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 3/22/07, 8:10 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: What's wrong with these panels?

Hard to tell, but I am assuming the box to the right is the service panel. Those breakers look like they are loose. There is also a white wire connected to a breaker (improperly identified). You could also not over bundling of the wires at the top of the box.
The other two panels look like they have incorrect bonding.
The middle box looks like copper and aluminum wires are tapped togehter
Reply With Quote
  #7  
Old 3/22/07, 11:10 AM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 32
Please Note: ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's wrong with these panels?

Quote:
Originally Posted by mthomas2
Just for starters in this one little area of one load-side panel, in addition to what you have already noted:

1) What's separating (insulating) the bare copper wire from the one above where they cross over above the left-hand breakers?

2) For that matter, what's that bare wire doing connected to the grounded (neutral) conductors over to the left of the left-hand breaker?

3) In any case, is the left-hand breaker listed for that panel?

4) There is (at best) marginal connections at top of both left hand breakers.

And it's just what I can see offhand in this one corner of one panel... I would suggest deferring the entire electrical system to an exorcist.
Thanks for your imput mthomas2. I didn't catch the bare wire connected to the neutral. I think it was the grounding rod wire. Do you know the name of any good priests?
Reply With Quote
  #8  
Old 3/22/07, 11:12 AM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 32
Please Note: ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's wrong with these panels?

Quote:
Originally Posted by jpope
The orange breakers are Zinsco's
What's the deal with Zinsco's? Are they just outdated or are they on the hazard list?
Reply With Quote
  #9  
Old 3/22/07, 11:14 AM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 32
Please Note: ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What's wrong with these panels?

Quote:
Originally Posted by wsiegel
Hard to tell, but I am assuming the box to the right is the service panel. Those breakers look like they are loose. There is also a white wire connected to a breaker (improperly identified). You could also not over bundling of the wires at the top of the box.
The other two panels look like they have incorrect bonding.
The middle box looks like copper and aluminum wires are tapped togehter
Thanks for the imput. Every bit helps.
Reply With Quote
  #10  
Old 3/22/07, 12:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: What's wrong with these panels?

Quote:
Originally Posted by ehyde
What's the deal with Zinsco's? Are they just outdated or are they on the hazard list?
A suggestion would be to try the search feature and type in Zinsco and we have discussed MANY things on them....from the change-over to AL contact bars to problems with the dead fronts falling into the panel itself and causing issues and so on.

it's only a suggestion but in the MASSIVE amounts of posts here....you would be surprised at all the GREAT information that lurks and gets left behind as the message boards rolls on.......people sometimes simply overlook the GREATNESS of the search feature for specific learning topics.

http://www.inspect-ny.com/electric/Zinsco.htm



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 3/22/07 at 12:17 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Distribution panels bking Electrical 2 3/11/07 11:29 AM
Electric Radiant Ceiling Panels bbernier Canadian Inspectors 4 2/15/07 2:22 PM
FPE Panel - Do you open them up? menser Electrical 11 2/7/06 7:31 PM
Old electrical panels? ysoltis General Inspection Discussion 2 1/14/06 11:58 AM
Old electrical panels? ysoltis Electrical 0 1/13/06 12:38 PM


All times are GMT -4. The time now is 6:19 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts