Default Where's the defect?

Service entrance conductors in this 200-amp main panel connect to a 125-amp breaker installed on the bus bar instead of the main bus bar lugs. Similar to a split bus, except I'm used to seeing the controlling breaker of a split bus installed separately from branch circuit breakers.
What exactly is the defect here?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 1:38 AM..
Reply With Quote
  #2  
Old 10/1/08, 3:48 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Where's the defect?

Looks like the grounding cable and SE neutral are switched.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 10/1/08, 3:48 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Where's the defect?

Hi Kent,

there isn't one, at least not a big one that I could see. That is just a back-fed breaker acting as the main (it should have and additional fastener preventing it's removal)

BTW what do those feeders go to they're huge?

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 10/1/08, 3:51 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Where's the defect?

They feed a 900 sq. ft. garage workshop, yep, they're whoppers, especially for the 100-amp breaker feeding the shop sub panel.
This is a configuration I'm not used to seeing, thanks

Neutral and grounding bus bars were joined by a jumper and had a bonding strap.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #5  
Old 10/1/08, 3:57 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Where's the defect?

In the 2nd picture the service entry goes to the breaker on the lower right. The neutral is feeding the bus with the bare ground wires (should feed the neutral bus). There is no evidence of a cable to an earth-ground rod.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 10/1/08, 4:03 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Where's the defect?

Quote:
Originally Posted by jwilliams4 View Post
In the 2nd picture the service entry goes to the breaker on the lower right. The neutral is feeding the bus with the bare ground wires (should feed the neutral bus). There is no evidence of a cable to an earth-ground rod.
You're right Jae, a could be seen leaving the panel but there was no electrode visible.

"The main electrical service grounding electrode was not visible at the time of the inspection. A grounding conductor was visible exiting the main panel, but the inspector was unable to confirm it's proper termination or proper grounding of the electrical service.
This is a common condition and no problems relating to this condition was apparent at the time of the inspection. Outlets in the home appeared to be properly grounded at the time of the inspection. Confirmation of proper grounding would require the services of a qualified electrical contractor using special equipment."




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 10/1/08, 4:14 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Where's the defect?

Quote:
Originally Posted by jwilliams4 View Post
In the 2nd picture the service entry goes to the breaker on the lower right. The neutral is feeding the bus with the bare ground wires (should feed the neutral bus). There is no evidence of a cable to an earth-ground rod.
Hi Jae & Kent, I hate to differ, but I think you are wrong.

As this is the panel containing the main disconnect the Neutrals and grounds may be connected, which they are as seen from the silver jumper at the extreme left of picture 2.

As to the panel ground, that is achieved through the ridgid conduit connecting the Panel to the meter base, if you look real close you can also see a conductor attached to it at the bottom of the picture.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106


Last edited by gbeaumont; 10/1/08 at 4:17 PM..
Reply With Quote
  #8  
Old 10/1/08, 4:24 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Where's the defect?

Quote:
Originally Posted by gbeaumont View Post
Hi Jae & Kent, I hate to differ, but I think you are wrong.

As this is the panel containing the main disconnect the Neutrals and grounds may be connected, which they are as seen from the silver jumper at the extreme left of picture 2.

As to the panel ground, that is achieved through the ridgid conduit connecting the Panel to the meter base, if you look real close you can also see a conductor attached to it at the bottom of the picture.

Regards

Gerry
Why is it that people "hate to differ", but do it anyway. Seems to me if it's so hateful, ya' hadn't oughta punish yourself.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #9  
Old 10/1/08, 4:28 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Where's the defect?

Quote:
Originally Posted by jwilliams4 View Post
Why is it that people "hate to differ", but do it anyway. Seems to me if it's so hateful, ya' hadn't oughta punish yourself.

Too funny Jae, actually I was just about to correct myself as you were posting, the GEC should be continuous, but I see a lot done like that with the GEC wire coming out of the meter and down to the rod(s)

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 10/1/08, 4:44 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Where's the defect?

I often see a GEC coming from the panel to a GE and the GC from the meter splices into it with a connector.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 10/3/08, 4:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Where's the defect?

hmm...I dont see a picture to comment on.



Paul W. Abernathy
Reply With Quote
  #12  
Old 10/3/08, 9:47 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Where's the defect?

Quote:
Originally Posted by pabernathy View Post
hmm...I dont see a picture to comment on.
Maybe they got deleted
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Defect slide show dandersen Miscellaneous Discussion for Inspectors 50 7/18/08 7:34 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Electrical Defect Recognition jtedesco1 Electrical Inspections 17 1/13/08 4:04 PM
Defect recognition bkelly1 Electrical Inspections 13 4/25/07 3:52 PM


All times are GMT -4. The time now is 7:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts