Service entrance conductors in this 200-amp main panel connect to a 125-amp breaker installed on the bus bar instead of the main bus bar lugs. Similar to a split bus, except I'm used to seeing the controlling breaker of a split bus installed separately from branch circuit breakers.
What exactly is the defect here? Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 10/2/08 at 1:38 AM.. |
|
#2
|
|||
|
|||
|
Looks like the grounding cable and SE neutral are switched.
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#3
|
||||
|
||||
|
Hi Kent,
there isn't one, at least not a big one that I could see. That is just a back-fed breaker acting as the main (it should have and additional fastener preventing it's removal) BTW what do those feeders go to they're huge? Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
||||
|
||||
|
They feed a 900 sq. ft. garage workshop, yep, they're whoppers, especially for the 100-amp breaker feeding the shop sub panel.
This is a configuration I'm not used to seeing, thanks Neutral and grounding bus bars were joined by a jumper and had a bonding strap. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#5
|
|||
|
|||
|
In the 2nd picture the service entry goes to the breaker on the lower right. The neutral is feeding the bus with the bare ground wires (should feed the neutral bus). There is no evidence of a cable to an earth-ground rod.
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#6
|
||||
|
||||
|
Quote:
"The main electrical service grounding electrode was not visible at the time of the inspection. A grounding conductor was visible exiting the main panel, but the inspector was unable to confirm it's proper termination or proper grounding of the electrical service. This is a common condition and no problems relating to this condition was apparent at the time of the inspection. Outlets in the home appeared to be properly grounded at the time of the inspection. Confirmation of proper grounding would require the services of a qualified electrical contractor using special equipment." Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#7
|
||||
|
||||
|
Quote:
As this is the panel containing the main disconnect the Neutrals and grounds may be connected, which they are as seen from the silver jumper at the extreme left of picture 2. As to the panel ground, that is achieved through the ridgid conduit connecting the Panel to the meter base, if you look real close you can also see a conductor attached to it at the bottom of the picture. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 Last edited by gbeaumont; 10/1/08 at 4:17 PM.. |
|
#8
|
|||
|
|||
|
Quote:
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#9
|
||||
|
||||
|
Quote:
Too funny Jae, actually I was just about to correct myself as you were posting, the GEC should be continuous, but I see a lot done like that with the GEC wire coming out of the meter and down to the rod(s) Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#10
|
||||
|
||||
|
I often see a GEC coming from the panel to a GE and the GC from the meter splices into it with a connector.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#11
|
|||
|
|||
|
hmm...I dont see a picture to comment on.
Paul W. Abernathy |
|
#12
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Maybe they got deleted
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Defect slide show | dandersen | Miscellaneous Discussion for Inspectors | 50 | 7/18/08 7:34 PM |
| Is inadequate roof or attic ventilation a defect? | gliebig | Exterior Inspections | 85 | 1/16/08 6:56 PM |
| Electrical Defect Recognition | jtedesco1 | Electrical Inspections | 17 | 1/13/08 4:04 PM |
| Defect recognition | bkelly1 | Electrical Inspections | 13 | 4/25/07 3:52 PM |