Default White electrical groung wire question.

Condo inspection. White tape wire on ground. Is this OK? Is this to indicate aluminum?



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/16/11, 4:11 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: White electrical groung wire question.

It is simply a way to identify the conductor (grounded vs black)when more than one is present. It is fine.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 4/16/11, 4:11 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: White electrical groung wire question.

Quote:
Originally Posted by ryoung7 View Post
Condo inspection. White tape wire on ground. Is this OK? Is this to indicate aluminum?
This is not the ground.
It is a black wire being used as a neutral and they have identified it with white tape .
This is OK every thing looks fine to me ... Roy

Where did this picture come from strange date on it

MAUCK INSPECTION FOR WEBSITE FEB 5 2011 017.jpg (1 of 1)
is this canadian



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 4/16/11 at 4:16 PM..
Reply With Quote
  #4  
Old 4/16/11, 4:29 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: White electrical groung wire question.

Thanks Roy. I was in a hurry band used the wrong wording, Nutral.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #5  
Old 4/16/11, 4:29 PM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: White electrical groung wire question.

I'm usually surprised the see a black being used as a neutral and taped white. I keep the narrative on my template just for the odds.



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #6  
Old 4/16/11, 4:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: White electrical groung wire question.

According to the NEC the tape is fine if that conductor is larger than #6 AWG. It looks like the neutral is much smaller than the other conductors in the raceway.

Quote:
200.6 Means of Identifying Grounded Conductors.
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor of 6 AWG or smaller shall be identified by a continuous white or gray outer finish or by three continuous white stripes on other than green insulation along its entire length. Wires that have their outer covering finished to show a white or gray color but have colored tracer threads in the braid identifying the source of manufacture shall be considered as meeting the provisions of this section. Insulated grounded conductors shall also be permitted to be identified as follows:
Reply With Quote
  #7  
Old 4/16/11, 5:11 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: White electrical groung wire question.

Quote:
Originally Posted by Robert Meier View Post
According to the NEC the tape is fine if that conductor is larger than #6 AWG. It looks like the neutral is much smaller than the other conductors in the raceway.
Good catch I agree ,I should have looked closer.Thanks.. Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #8  
Old 4/16/11, 5:12 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: White electrical groung wire question.

Mr.Leahy points out a position when using his narrative on a report
I'm usually surprised the see a " black being used as a neutral and taped white." I keep the narrative on my template just for the odds
Opinions please.
Thank you....Robert



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 4/16/11, 8:53 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: White electrical groung wire question.

Larger cables are used a lot more in Black and not much in white . So for the small amount needed it is easier to Just carry one reel of wire and when white is need to identify it .
Industry uses I would guess 50 times what is needed in home wiring so 50 black used a lot to one roll of white used little .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question on Wire? dokeefe Electrical Inspections 6 3/2/09 3:11 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
White Wire to Breaker and Splice Inside Panel maitai11 Electrical Inspections 31 9/5/06 11:09 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical Inspections 0 6/16/06 2:10 PM


All times are GMT -4. The time now is 7:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts