Hi -
I'm just double checking here... 1. White wire to breaker is ok IF it is wrapped with black electrical tape indicating that it is "Hot". Please confirm? 2. Splicing inside the main electrical panel - not permitted, right? The argument I got was that they were trying to avoid a double lug/tap condition. Please confirm? Thanks in advance!! Maitai |
|
#2
|
||||
|
||||
|
1. What argument did you get for using a white wire with black tape instead of the standard black wire? I wouldn't consider it okay; sounds like a handyman job that needs the evaluation of a competant electrician.
2. While not recommended, splicing in panels is not condemned by NEC as long as it is done properly (with proper sized wire nuts, etc.). Sounds better than double tapping to me too. |
|
#3
|
|||
|
|||
|
Please Note:
maitai11 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the input...I maintained that a licensed electrician needs to investigate and verify.
|
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
For a straight 240v circuit, such as for a larger wall A/C or shop tool, it is/was very common and legal to run "2-wire" (eg: 12/2). This would put the black and white on a two-pole breaker.
Until the last code cycle there was NO requirement to re-mark the white wire. There is a new requirement to re-mark the white wire to a hot color, only tape is not an option for wires under #4. Typically we use a Sharpie marker, paint is also acceptable. So, if this is a house that more than a few years old there is no issue at all with a white on a breaker if this is the situation. As for splices in a panel, this is a wives tale long perpetuated by myth. Yes, it is very true hat you cannot use a panel as a raceway for certain condutors, and splicing is illegal under certain circumstances, but pigtailing is absolutely legal, safe and accepted. Actually it is required in some cases to avoid double tapped breakers. |
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
||||
|
||||
|
Peter,
Are you saying that the requirements of 200.7(C), first came about in the 2002 edition? I seem to remember it being much earlier, but I can't verify that at the moment. As for your comment with regards to splices in the panel, I concur. The NEC is quite clear that a panel board may not be used as a junction box, however, the simple presence of wire-nuts does not make a panel into a "junction box." When conductors are spliced in order to lengthen them, or to relieve a "double tap," it is acceptable for this to occur within the electrical panel - the conductors are still being served by the breakers or panel components, which is the purpose of the panel. When conductors enter the panel and are spliced to conductors which exit the panel, this is generally not acceptable. In this case, the conductors are not being served by components of the panel, and the panel is being used as a junction box for those conductors. The basic "rule-of-thumb" for the home inspector is that all conductors entering the electrical panel, should terminate at a breaker or terminal bar/lug. There should be no "through and through" conductors within the panel, whether they are spliced or not. As we are not "experts," this condition would warrant a recommendation for further evaluation and/or correction. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The ground wire would be used for ground. A 240V circuit does not require a dedicated neutral to work properly. |
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is nothing in the code about splices in the panelboard enclosure and a splice does not increase wire count in fill calculations.
The code 312.8 really quibbles on using the panelboard enclosure for conductors passing through. It says Quote:
Quote:
Generally, as an inspector, I just look at the workmanship and whether the resulting installation is servicable. I wouldn't get too concerned about a few "foreign" wires passing through if the box wasn't crowded to the point that you couldn't easily work in there or sort out what was going on. |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
It should be noted that you can only reidentify a white wire in a cable. If this is wire in pipe you need to use another color for ungrounded conductors.
This is only to give people using 2 wire (with ground) the ability to run a 240v circuit. I have seen red/black/bare romex but it is very rare. |
|
#10
|
||||
|
||||
|
Quote:
|
|
#11
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
the neutral on a 240v circuit would be designed to carry the difference between the two "hot" wires. since both "hot" wires are 120v, there is no difference to carry, therefore negating the need for a dedicated neutral on a 240v circuit |
|
#13
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Jeff's always smooth with a capital SMOO. thanks again... |
|
#14
|
||||
|
||||
|
Quote:
Quote:
Here is my conclusion based on many conversations and debates on this matter (and remember, I like to stand behind the most restrictive interpretation and let the experts loosen it up). "Adequate space" IS NOT provided - per the manufacturer. NO SPACE is PROVIDED by the manufacturer for through and through conductors, splice or no splice - in other words - they are designed as load centers only, and space is PROVIDED for use as load centers only. If the equipment is listed as a load center/raceway, then space IS provided for that purpose. Then we fall back onto the capacity limits defined by the NEC. It's much easier for me to let you, Greg, decide whether or not the installation is acceptable IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
It all depends on the enclosure. If you look at a catalog you can find identical panelboards in different sized enclosures. Most of the extra space is wire bending space more than simply extra room for "fill".