Default Whole house surge protectors

I have sometimes seen the whole house surge protectors that are installed behind the electric meter at the exterior. I was wondering if any of the electric gurus have an opinion on how effective these units are or if they are a waste of $$. The phone and cable are attached to these units also. The local utility will installed the unit and charge $10 a month. What are the facts and what are your opinions.
Reply With Quote
Find an InterNACHI certified Texas Home Inspector (and anywhere else in North America)
  #2  
Old 12/15/09, 8:51 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Whole house surge protectors

We have one on our house and it has protected us a couple of times--we think.

It's difficult to be sure, but we would recommend that everyone have one.

Of course, my wife is a Senior IT Data Base Administrator with Duke Energy...but of course, that wouldn't influence our recommendation.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 12/15/09, 9:02 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Whole house surge protectors

yes they work. Now, I dont know about paying $10.00 a month to the POCO for this but I would always suggest to people a Type 2 SPD (TVSS) at the electrical panel and a Type 3 (TVSSs) at the equipment for a two-step level of protection. The ones we see outside many times at the service drop or on the meter side are Type 1 SPD's (lighting arrestors) and it fine.....but I believe Type 2 and Type 3 are the most important and do not require a monthly fee to have that needed protection.



Paul W. Abernathy
Reply With Quote
  #4  
Old 12/15/09, 9:09 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Whole house surge protectors

Quote:
Originally Posted by pabernathy View Post
yes they work. Now, I dont know about paying $10.00 a month to the POCO for this but I would always suggest to people a Type 2 SPD (TVSS) at the electrical panel and a Type 3 (TVSSs) at the equipment for a two-step level of protection. The ones we see outside many times at the service drop or on the meter side are Type 1 SPD's (lighting arrestors) and it fine.....but I believe Type 2 and Type 3 are the most important and do not require a monthly fee to have that needed protection.
Agreed.

We paid $150 up front 3 years ago with no monthly fee, and yearly check-up included.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moldy House Costs Builder $3 Million dplummer Ancillary Inspection Services & Additional Topics 5 9/25/11 5:51 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 6:11 PM
Home Surge Protectors sblayney Electrical Inspections 5 1/24/08 7:34 PM
Foam Insulation ? wrandolph General Inspection Discussion 13 11/18/07 8:30 PM


All times are GMT -4. The time now is 7:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts