Default Why??

Why do we keep finding things like this, light switch next to the SPA tub. House is three years old. Shouldn't the local AHJ find this?
Attached Thumbnails
why-100_0321.jpg  
Reply With Quote
  #2  
Old 1/26/09, 4:34 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why??

Quote:
Originally Posted by bhartley View Post
Shouldn't the local AHJ find this?
The logical answer to this is yes. We all know reality is different.

I want to know how the contractor did that and walked away satisfied with a job well done. I wouldn't sleep at night knowing I did something like that.
Reply With Quote
  #3  
Old 1/26/09, 4:39 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Why??

Can someone provide a citation of the code this violates?



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #4  
Old 1/26/09, 4:47 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Why??

Quote:
Originally Posted by cevans View Post
Can someone provide a citation of the code this violates?
NEC

404.4 Damp or Wet Locations.

A surface-mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2. A flush-mounted switch or circuit breaker in a damp or wet location shall be equipped with a weatherproof cover.Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 1/26/09, 4:50 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Why??

Quote:
Originally Posted by mlarson View Post
NEC

404.4 Damp or Wet Locations.

A surface-mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2. A flush-mounted switch or circuit breaker in a damp or wet location shall be equipped with a weatherproof cover.Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
Thank you



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #6  
Old 1/26/09, 4:51 PM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: Why??

Quote:
Originally Posted by bhartley View Post
Why do we keep finding things like this, light switch next to the SPA tub. House is three years old. Shouldn't the local AHJ find this?

Check this recommendation....
Attached Thumbnails
why-1682.jpg  




Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #7  
Old 1/26/09, 4:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Why??

Quote:
Originally Posted by swaskewicz View Post
Check this recommendation....
Nice illustration but that is not what the code says.

Just can't be within the tub footprint.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 1/26/09, 4:57 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Why??

Quote:
Originally Posted by mlarson View Post
Nice illustration but that is not what the code says.

Just can't be within the tub footprint.
That's precisely why I asked for the code citation



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #9  
Old 1/26/09, 5:47 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why??

Are you sure it wasnt put in after the home was sold by the homewoner?
Reply With Quote
  #10  
Old 1/26/09, 5:51 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why??

What did it control?
Reply With Quote
  #11  
Old 1/26/09, 6:09 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why??

Quote:
Originally Posted by swaskewicz View Post
Check this recommendation....
Be careful using those Carson Dunlop illustrations - some are from Canadian code rules, such as the 3 foot (1 metre) rule.

Someone could argue that the wall switch above the spa is not in a wet location. Not me, but someone .......

John Kogel
www.allsafehome.ca
Reply With Quote
  #12  
Old 1/26/09, 6:12 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is online now
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Why??

The light switch controls the light fixture over the SPA tub. The house has been on the market 3 years, never been lived in.
Reply With Quote
  #13  
Old 1/26/09, 6:14 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why??

I wouldn't put it there myself, but that switch IS NOT within the wet area. It's mounted in a drywall wall... certainly not a wet area. It might get wet one day by some means, but it is not mounted within the wet location.
Reply With Quote
  #14  
Old 1/26/09, 6:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Why??

Quote:
Originally Posted by Marc D. Shunk View Post
I wouldn't put it there myself, but that switch IS NOT within the wet area. It's mounted in a drywall wall... certainly not a wet area. It might get wet one day by some means, but it is not mounted within the wet location.
How about this Marc?

Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.

Is this a "damp location" by definition?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #15  
Old 1/26/09, 6:22 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Why??

Quote:
Originally Posted by Marc D. Shunk View Post
I wouldn't put it there myself, but that switch IS NOT within the wet area. It's mounted in a drywall wall... certainly not a wet area. It might get wet one day by some means, but it is not mounted within the wet location.
Mark, it just needs to be outside the tub line right?
Thats what I thought.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On