Default Why the double tap?

I bet the breaker above it (unused) was tripping too often...
Attached Thumbnails
why-double-tap-s4026619.jpg  



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 1/7/07, 6:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

Does seem odd. Many of the Cutler Hammer CH series 15 and 20 amp breakers are rated for two conductors of the same gauge. The fact that these breakers lack the amp rating in black ink on the ends of the handles leads me to believe that they have a bit of age on them (I think they started making black amp ratings in the early 90's. before that they were embossed). Perhaps the empty breaker was nuisance tripping, as you suspect. The Cutler Hammer CH series is a famously high quality plug-on style breaker. It's certainly the most expensive residential panel.

[Edited for spelling]

Last edited by Marc D. Shunk; 1/7/07 at 7:26 PM..
Reply With Quote
  #3  
Old 1/7/07, 7:22 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

1979 Condominium...

It's a 20 amp (recessed numbers on the tip)...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #4  
Old 1/7/07, 7:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

So what do you write during such a finding? Technically, I see no particular violation. It does seem pretty obvious the the above breaker must have had some issue, and the conductor was moved down one. Do you just note this in your report, with no particular remedial action recommended?
Reply With Quote
  #5  
Old 1/7/07, 7:34 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

"Doubled lugged breaker within the panelboard; It was almost certainly due to the breaker above it nuisance tripping. Monitor for issues with this breaker tripping as well. If such tripping is noted I recommend a licensed electrician replace both breakers (repeated tripping can cause them to trip prior to a real circuit overload) to ensure adequate load is available to all circuits."

is what I have wrote so far...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 1/7/07, 7:37 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

What about the use of the white conductors on the devices to the right side?
Reply With Quote
  #7  
Old 1/7/07, 7:40 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

Quote:
Originally Posted by jtedesco1
What about the use of the white conductors on the devices to the right side?
Noted as well... just not any mystery there...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #8  
Old 1/7/07, 7:56 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

It looks as though the empty breaker is not of the same vinatge as the others. Close but not quite. It may have been installed later.
Reply With Quote
  #9  
Old 1/7/07, 8:00 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

I was thinking it's a bit "polished" from the repeated resets (prior to moving the conductor, of course) but it looks as old as the rest in person....



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #10  
Old 1/7/07, 8:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Why the double tap?

I agree with Joe..those white conductors need to be re-identified and it appears that double tap regardless of the model...appears to have (2) different sizes running to it...but it could just be the angle.

Also I can't tell behind the conductors on the left....but possibly some double luggin goin on with some grounded conductors....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 1/7/07, 8:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

That is the problem with guessing. It could be a breaker that was being saved for a load they never got around to adding, or are taking with them.
Some real estate folks are smart enough to remove some homeowner added stuff before a sale. Where there any KO seals (or missing ones) in the panel?
Reply With Quote
  #12  
Old 1/7/07, 8:20 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

Quote:
Originally Posted by pabernathy
Also I can't tell behind the conductors on the left....but possibly some double luggin goin on with some grounded conductors....
There were ganged grounds but the neutral conductors were separated



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #13  
Old 1/7/07, 8:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Why the double tap?

Oh yes...never underestimate the WILL of a person who REALLY want's to sell their home...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 1/7/07, 8:23 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Why the double tap?

Quote:
Originally Posted by Greg Fretwell
That is the problem with guessing. It could be a breaker that was being saved for a load they never got around to adding, or are taking with them.
Some real estate folks are smart enough to remove some homeowner added stuff before a sale. Where there any KO seals (or missing ones) in the panel?
Condo is a FSBO (daughter was in it for 4 years at College of Charleston) buyer reports a "family friend" kept it up for her...

No missing knockouts...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #15  
Old 1/7/07, 8:25 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Why the double tap?

Ok Micheal. You were there. I was not so I'll take your word for it. It might just be the way it shows in the picture but here is what makes me think it was installed a little later.

why-double-tap-s4026619.jpg

Not that it really matters for the double tap.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double tapping question mroe Electrical Inspections 17 8/30/07 9:32 AM
Double Tap Questions jkogel Electrical Inspections 6 6/28/07 10:46 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 10:04 AM
Doorbell transformer double tap bsmith Electrical Inspections 11 4/17/06 1:48 PM
Double Taps rwand1 Canadian Inspectors 30 3/29/06 8:16 PM


All times are GMT -4. The time now is 5:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts