Default Window to SEC clearance

If memory serves me correctly, which it probablly isn't, SEC's should be at least 3' away from windows that open. Todays home had a window with 2'9" from the left side of the window and 3'1" from the right side of the window.

The window only opened on the right side with the 3'1" clearance. Is this setup OK or should the clearance be from any part of the window regardless if opens on both sides or not?
Attached Thumbnails
window-sec-clearance-sec1.jpg   window-sec-clearance-sec.jpg   window-sec-clearance-sec2.jpg  
Reply With Quote
  #2  
Old 10/20/07, 10:24 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Window to SEC clearance

Quote:
Originally Posted by vsantos
If memory serves me correctly, which it probablly isn't, SEC's should be at least 3' away from windows that open. Todays home had a window with 2'9" from the left side of the window and 3'1" from the right side of the window.

The window only opened on the right side with the 3'1" clearance. Is this setup OK or should the clearance be from any part of the window regardless if opens on both sides or not?
Three foot clearance is not required from non openable windows.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 10/20/07, 11:04 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Window to SEC clearance

230.9(A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.

as long as the conductors are inside the sheathing of the cable or in a raceway they can be within one inch of the window.
Reply With Quote
  #4  
Old 10/20/07, 3:43 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Window to SEC clearance

Quote:
Originally Posted by Mike Whitt
230.9(A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.

as long as the conductors are inside the sheathing of the cable or in a raceway they can be within one inch of the window.
Thanks Mike, that was helpful.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 10/22/07, 11:35 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Window to SEC clearance

Mike is so right...it is very important that you READ and understand the actual meaning of the code issue and disect the safety issue out of it.

It is also important to not forget the fact it applies to other areas of the code as well for feeders and branch circuits also..

(D) Final Spans.
Final spans of feeders or branch circuits
shall comply with 225.19(D)(1), (D)(2), and (D)(3).

(1) Clearance from Windows.
Final spans to the building
they supply, or from which they are fed, shall be permitted
to be attached to the building, but they shall be kept not less
than 900 mm (3 ft) from windows that are designed to be
opened, and from doors, porches, balconies, ladders, stairs,
fire escapes, or similar locations.

Exception: Conductors run above the top level of a window
shall be permitted to be less than the 900-mm (3-ft)
requirement.



Paul W. Abernathy
Reply With Quote
  #6  
Old 10/22/07, 2:18 PM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 351
Lightbulb Re: Window to SEC clearance

Hi! Paul;
I know that a main panel has a max height of 6'7" isn't there a min to the floor also??????
Len
Reply With Quote
  #7  
Old 10/22/07, 2:37 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Window to SEC clearance

Only for a mobile home and the minimim is 24 inches
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Window well finishing rmuller Interior Inspections 7 5/10/07 8:11 PM
CPA of Health Canada reminding us of corded window coverings. gromicko Canadian Inspectors 7 4/23/07 7:31 AM
Water heater flue and window clearance? jfunderburk Inspecting HVAC Systems 5 4/19/07 10:00 AM
Window installation jmichalski Exterior Inspections 17 1/24/06 9:42 PM


All times are GMT -4. The time now is 5:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts