Default Wire connector

Anybody have a link for using an approved connector instead of splitting the 50 amp wire?

This is in the main panel that feeds a sub panel. I have tried google but I am not finding any good info.
Attached Thumbnails
wire-connector-138109-019-small-.jpg.jpg
Views:	92
Size:	44.6 KB
ID:	28820  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 5/21/09, 8:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire connector

david,

Firstly, is that conductor serving as an EGC, GEC or Grounded Conductor that is just improperly color coded.

Are you talking about an image of the lug that shares two terminals to hold a single mounted lug. If that is what you are wanting I will see if I can find an image for you.



Paul W. Abernathy
Reply With Quote
  #3  
Old 5/21/09, 8:12 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Wire connector

Yes, if you had an image or link that would be great.

Yup I missed that. But I did catch the neutral/ground improper isolation, 220 breaker improperly connected, there where 2 15 amp wires to 20 amp breakers. The wire is supposed to be white correct? Can he just use white tape.

Panel is also upside down. Can it be installed this way?
Attached Thumbnails
wire-connector-138109-022-small-.jpg.jpg
Views:	45
Size:	66.3 KB
ID:	28821  

Last edited by dmacy; 5/21/09 at 8:19 PM..
Reply With Quote
  #4  
Old 5/21/09, 8:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire connector

http://tbn0.google.com/images?q=tbn:...duct/tgl20.jpg



Paul W. Abernathy
Reply With Quote
  #5  
Old 5/21/09, 8:45 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Wire connector

Thanks for your time and help!!
Reply With Quote
  #6  
Old 5/21/09, 8:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire connector

Quote:
Originally Posted by dmacy View Post
Yes, if you had an image or link that would be great.

Yup I missed that. But I did catch the neutral/ground improper isolation, 220 breaker improperly connected, there where 2 15 amp wires to 20 amp breakers. The wire is supposed to be white correct? Can he just use white tape.

Panel is also upside down. Can it be installed this way?
Yes, he can use White Tape. Hope you called out the multiple conductors under the terminations onto the buss bar, Those are 408.41 violations and if before 2002 simply cite UL 67 Standards.



Paul W. Abernathy
Reply With Quote
  #7  
Old 5/21/09, 8:51 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire connector

On the panel......Yes, as long as they do not violate 240.81 and the listing of the panelboard. It could be argued that the manufacturer installed the "LINE" labels a certain orientation for a reason and not upside down but I have to say I would not on the surface worry too much about that.

here is a nice article for you...

http://www.ecmag.com/index.cfm?fa=ar...articleID=7650



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 1:08 AM


All times are GMT -4. The time now is 5:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts