Outdoor unit of a Central Forced Air Conditioner system indicates max amperage is 45 amps.
At the distribution panel (not the disconnect) there is a 40 Amp bridged breaker but the gauge of the copper conductor going into it appears to be 10 gauge (appropriate for 30 amps max). Question: Do A/Cs system manufacturers sell their products with the conductors that run between the outdoor unit to the distribution panel attached to the unit? Or are the conductors supplied and installed separately by the installation company. I can't see how the Air Conditioner company (Coleman) would state max amperage at 45 and supply a 10 gauge wire. Any insights as to why this might be okay would be considered. But for now I am putting it in my report as: "Oversized breakers within the main distribution panel should be replaced. All breaker should be sized according to wire gauge." Thanks in advance. |
|
#2
|
||||
|
||||
|
Please Note:
Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here is an example that will confuse you more.
Sizing is an engineering issue. http://www.mikeholt.com/onlinetraini...13923033_2.jpg Note the smaller egc size. |
|
#3
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I think I'll just go shoot myself in the head! |
|
#4
|
||||
|
||||
|
You noted the fact that it's a Zinsco panel, didn't you Jeff?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Question for you. What is the correct type of screw to be used in the side of the distribution panel for the ground wires. This looks suspect to me. |
|
#6
|
|||
|
|||
|
Please Note:
smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Without getting real technical, because the AC unit is considered a motor load it can be fused higher than you would normally see for household loads. If you look closely at the AC nameplate you will see a listing for Maximum Circuit Breaker size as well as a Minimum Allowable Ampacity. You can use this rule of thumb. Wire for the minimum and breaker for the maximum and get an allowable wire and breaker size. This doesn't mean that you can't use a larger conductor, just that it is not required.
The sheet metal screw that the grounding conductors are attached to is a total no-no. There should be a ground bar attached to the panel with machine screws installed into threaded holes. Last edited by smcarthur; 7/14/06 at 9:49 PM.. |
|
#7
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Is the reason that motor loads can be fused higher than household loads because at start up they may surge to the maximum ampacity but then settle in to run at a lower amperage? Is installing the larger breaker with the smaller conductor an attempt to create the same kind of time delay or 'slow blow' found in some fuses.... but for a breaker configuration? Based on your comment I am inclined not to call out the larger breaker then. I knew there was a reason. Just had to hear it from someone else. ---------- In regards to the grounding screw. I agree about the ground bar. This is how I normally see it. But I'm also aware that ground wires are allowed to be attached to the panel box with the correct type of connection screw. Paul Abernathy wrote on 3/9/06: The termination of equipment grounding and bonding conductors must be by exothermic welding, listed pressure connectors of the set screw or compression type, listed clamps, or other listed fittings. Sheet-metal screws cannot be used to connect grounding (earthing) or bonding conductors or connection devices to enclosures. Why it is a problem ( and personally why the wood screws and drywall screws are also wrong in my opinion even though the NEC does not call it out ) is because the threads on these types of screws to not make enough contact with the enclosure to ensure a good bond...pre-threaded holes do with at all points within the thread count...but not with the screws listed above. In a situation where their is a fault and it travels through that "sheet metal " screw the lack of contact could provide a less efficiant bond...and could actually loose the effective bond. Anyone have any pictures of 'pressure connectors of the set screw or compression type' ? Last edited by jweinberg; 7/14/06 at 10:11 PM.. |
|
#8
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
I thought the smaller conductors were allowed only from the disconnect to the hvac unit. The conductors from the panel to the disconnect are always the correct size around here.
|
|
#10
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#11
|
||||
|
||||
|
Please Note:
jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
What do you think Steve? |
|
#12
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The "minimum circuit ampacity" is the whole branch circuit, all the way back. There may be reasons to make it bigger (voltage drop, derating in the attic etc) but that is the minimum.
|
|
#13
|
|||
|
|||
|
Please Note:
smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Hi Bruce, the reason you may be seeing larger conductor in our area is because of the same reason a lot of electricians in our area will not use #14 in residential, they think they are doing a better job by going above code or they don't understand the code that allows them to use smaller wire. Last edited by smcarthur; 7/15/06 at 1:59 PM.. |
|
#14
|
||||
|
||||
|
Does code allow for smaller than normal wire feeding airhandlers with aux heat strips?
|
|
#15
|
|||
|
|||
|
Please Note:
smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
You may wire according to the mfg. nameplate rating. If you check the nameplate and it's lists a minimum circuit ampacity you may wire accordingly. The only ones I've can remember seeing were on the outside unit. The motor load on the air handler would be small compared to auxilliary strip heaters adn probabally not make a lot of difference in the total load, whereas on the outside unit the compressor is the majority of the load.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 9:44 AM |