Outdoor unit of a Central Forced Air Conditioner system indicates max amperage is 45 amps.

At the distribution panel (not the disconnect) there is a 40 Amp bridged breaker but the gauge of the copper conductor going into it appears to be 10 gauge (appropriate for 30 amps max).

Question: Do A/Cs system manufacturers sell their products with the conductors that run between the outdoor unit to the distribution panel attached to the unit? Or are the conductors supplied and installed separately by the installation company.

I can't see how the Air Conditioner company (Coleman) would state max amperage at 45 and supply a 10 gauge wire.

Any insights as to why this might be okay would be considered. But for now I am putting it in my report as: "Oversized breakers within the main distribution panel should be replaced. All breaker should be sized according to wire gauge."

Thanks in advance.
Attached Thumbnails
wire-gauge-breaker-rating-img_4986.jpg  
Reply With Quote
  #2  
Old 7/14/06, 8:55 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Here is an example that will confuse you more.

Sizing is an engineering issue.

http://www.mikeholt.com/onlinetraini...13923033_2.jpg

Note the smaller egc size.
Reply With Quote
  #3  
Old 7/14/06, 9:03 PM
jweinberg's Avatar
jweinberg jweinberg is offline
Active Poster
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by Mike Parks
Here is an example that will confuse you more.

Sizing is an engineering issue.

http://www.mikeholt.com/onlinetraini...13923033_2.jpg

Note the smaller egc size.
Thanks Mike....What's up with that?????

I think I'll just go shoot myself in the head!
Reply With Quote
  #4  
Old 7/14/06, 9:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: wire gauge / breaker rating

You noted the fact that it's a Zinsco panel, didn't you Jeff?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 7/14/06, 9:12 PM
jweinberg's Avatar
jweinberg jweinberg is offline
Active Poster
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by jpope
You noted the fact that it's a Zinsco panel, didn't you Jeff?
Sure did Jeff.... Thanks for asking. I've recommended further evaluation for that and also for the Zinsco Main Service Disconnect breaker and the double tap and pointed cover screws in the dist. panel.

Question for you. What is the correct type of screw to be used in the side of the distribution panel for the ground wires. This looks suspect to me.
Attached Thumbnails
wire-gauge-breaker-rating-img_4979.jpg  
Reply With Quote
  #6  
Old 7/14/06, 9:42 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Without getting real technical, because the AC unit is considered a motor load it can be fused higher than you would normally see for household loads. If you look closely at the AC nameplate you will see a listing for Maximum Circuit Breaker size as well as a Minimum Allowable Ampacity. You can use this rule of thumb. Wire for the minimum and breaker for the maximum and get an allowable wire and breaker size. This doesn't mean that you can't use a larger conductor, just that it is not required.

The sheet metal screw that the grounding conductors are attached to is a total no-no. There should be a ground bar attached to the panel with machine screws installed into threaded holes.

Last edited by smcarthur; 7/14/06 at 9:49 PM..
Reply With Quote
  #7  
Old 7/14/06, 9:54 PM
jweinberg's Avatar
jweinberg jweinberg is offline
Active Poster
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by smcarthur
Without getting real technical, because the AC unit is considered a motor load it can be fused higher than you would normally see for household loads. If you look closely at the AC nameplate you will see a listing for Maximum Circuit Breaker size as well as a Minimum Allowable Ampacity. You can use this rule of thumb. Wire for the minimum and breaker for the maximum and get an allowable wire and breaker size. This doesn't mean that you can't use a larger conductor, just that it is not required.

The sheet metal screw that the grounding conductors are attached to is a total no-no. There should be a ground bar attached to the panel with machine screws installed into threaded holes.
Thanks Steve,

Is the reason that motor loads can be fused higher than household loads because at start up they may surge to the maximum ampacity but then settle in to run at a lower amperage?
Is installing the larger breaker with the smaller conductor an attempt to create the same kind of time delay or 'slow blow' found in some fuses.... but for a breaker configuration?

Based on your comment I am inclined not to call out the larger breaker then. I knew there was a reason. Just had to hear it from someone else.

----------
In regards to the grounding screw. I agree about the ground bar. This is how I normally see it. But I'm also aware that ground wires are allowed to be attached to the panel box with the correct type of connection screw.

Paul Abernathy wrote on 3/9/06:

The termination of equipment grounding and bonding conductors must be by exothermic welding, listed pressure connectors of the set screw or compression type, listed clamps, or other listed fittings. Sheet-metal screws cannot be used to connect grounding (earthing) or bonding conductors or connection devices to enclosures.

Why it is a problem ( and personally why the wood screws and drywall screws are also wrong in my opinion even though the NEC does not call it out ) is because the threads on these types of screws to not make enough contact with the enclosure to ensure a good bond...pre-threaded holes do with at all points within the thread count...but not with the screws listed above.

In a situation where their is a fault and it travels through that "sheet metal " screw the lack of contact could provide a less efficiant bond...and could actually loose the effective bond.


Anyone have any pictures of 'pressure connectors of the set screw or compression type' ?

Last edited by jweinberg; 7/14/06 at 10:11 PM..
Reply With Quote
  #8  
Old 7/14/06, 11:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by jweinberg
Question for you. What is the correct type of screw to be used in the side of the distribution panel for the ground wires. This looks suspect to me.
Bus bar required. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 7/14/06, 11:45 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: wire gauge / breaker rating

I thought the smaller conductors were allowed only from the disconnect to the hvac unit. The conductors from the panel to the disconnect are always the correct size around here.
Reply With Quote
  #10  
Old 7/14/06, 11:48 PM
jweinberg's Avatar
jweinberg jweinberg is offline
Active Poster
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by jpope
Bus bar required. . .

Quote:
Originally Posted by smcarthur
The sheet metal screw that the grounding conductors are attached to is a total no-no. There should be a ground bar attached to the panel with machine screws installed into threaded holes.
Two against one.... I stand corrected.
Reply With Quote
  #11  
Old 7/14/06, 11:50 PM
jweinberg's Avatar
jweinberg jweinberg is offline
Active Poster
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by bking
I thought the smaller conductors were allowed only from the disconnect to the hvac unit. The conductors from the panel to the disconnect are always the correct size around here.
Good point Bruce....

What do you think Steve?
Reply With Quote
  #12  
Old 7/15/06, 12:44 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

The "minimum circuit ampacity" is the whole branch circuit, all the way back. There may be reasons to make it bigger (voltage drop, derating in the attic etc) but that is the minimum.
Reply With Quote
  #13  
Old 7/15/06, 1:50 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

Quote:
Originally Posted by Greg Fretwell
The "minimum circuit ampacity" is the whole branch circuit, all the way back. There may be reasons to make it bigger (voltage drop, derating in the attic etc) but that is the minimum.
Agreed

Hi Bruce, the reason you may be seeing larger conductor in our area is because of the same reason a lot of electricians in our area will not use #14 in residential, they think they are doing a better job by going above code or they don't understand the code that allows them to use smaller wire.

Last edited by smcarthur; 7/15/06 at 1:59 PM..
Reply With Quote
  #14  
Old 7/15/06, 4:38 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: wire gauge / breaker rating

Does code allow for smaller than normal wire feeding airhandlers with aux heat strips?
Reply With Quote
  #15  
Old 7/15/06, 5:18 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

You may wire according to the mfg. nameplate rating. If you check the nameplate and it's lists a minimum circuit ampacity you may wire accordingly. The only ones I've can remember seeing were on the outside unit. The motor load on the air handler would be small compared to auxilliary strip heaters adn probabally not make a lot of difference in the total load, whereas on the outside unit the compressor is the majority of the load.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM


All times are GMT -4. The time now is 5:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts