  #16  
Old 7/16/06, 1:29 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

The toaster wire heat needs full circuit ampacity, based on the labelling of the air handler and the installed heat kit. The confusion is in the condenser wiring, usually smaller than the heat. You set the breaker size to the overcurrent rating and the wire size to circuit ampacity. That will not be what you usually see based on 240.4(D). (20a=12ga 30a=10ga etc)
Motors are under a different rule.
Reply With Quote
  #17  
Old 7/16/06, 9:03 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: wire gauge / breaker rating

With the price of copper we will probably start seeing some creative wiring practices. I did a 3BR house the other day that only had one arc-fault breaker on a single circuit for all bedrooms.
Reply With Quote
  #18  
Old 7/16/06, 11:59 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

The basic rule of thumb is 3va per sq/ft so a 20a breaker could serve 800 sq/ft of bedroom. I doubt anyone is actually measuring this in plan review and the code language is not really there but that is a guideline.
Reply With Quote
  #19  
Old 7/16/06, 12:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: wire gauge / breaker rating

Bruce,

While that seems poor electrical design as I would think (4) bedrooms and only (1) AFCI circuit is rather weak.

What we see is many electricians today ( well the ones I know and teach ) are starting to put (1) AFCI on the bedroom receptacles and (1) on the bedroom Lighting outlets...that way they can get (2) rooms with a different circuit for the recepts than the lights...so the lights dont have that dim effect if a larger load is placed on it for some reason...

But again my personal feeling is on 14 AWG circuit AFCI or not....no more than 12-14 items per circuit....and 14 is my max.....but we all know situations arrise......add one here " quote from the builder/buyer " and well....you know.



Paul W. Abernathy
Reply With Quote
  #20  
Old 7/16/06, 4:36 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wire gauge / breaker rating

210.11(B) Load Evenly Proportioned Among Branch Circuits.


Where the load is calculated on the basis of volt-amperes
per square meter or per square foot, the wiring system up to
and including the branch-circuit panelboard(s) shall be provided
to serve not less than the calculated load. This load
shall be evenly proportioned among multioutlet branch circuits
within the panelboard(s). Branch-circuit overcurrent
devices and circuits shall only be required to be installed to
serve the connected load.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM


All times are GMT -4. The time now is 7:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts