Can anyone tell by this pic what size wire? It appears to be # 8 or #6. If #8 then the breaker should be 40 plus, correct? It is for a range and is on a 30amp breaker.

Attachment 14394

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 9:42 AM..
Reply With Quote
  #2  
Old 9/9/07, 6:15 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by nbhi
If #8 then the breaker should be 40 plus, correct?
No, not "should", "can" be 40a. NOT 40 plus.


Looks like #6 or #8AL to me. Either is fine for 30 amps.
Reply With Quote
  #3  
Old 9/9/07, 6:53 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

A wire that's "too big" for the breaker rating is always fine, as long as the breaker has a lug that can accomodate that gauge. This happens sometimes during new construction when cut sheets aren't available on the appliances, so the electrician makes his best educated guess and runs a conservative gauge. When it comes time for the final connections, he just verifies what the actual delivered appliance needs and picks the right breaker. My only concern is whether the 30 amp breaker has a lug suitable for whatever gauge that conductor is. Among 30 amp breakers, that's a transitional size that could either have a box lug or a pressure plate type terminal. Some brands are even available both ways. If it's a pressure plate terminal, then it's very likely no good for #6 or #8. If it's a box lug, you're good to go. That looks like a Cutler-Hammer CH breaker, and that's my main brand. I can't honestly remember if their 30 amp breakers are rated for #6 and #8 or not. It will say on the breaker.
Reply With Quote
  #4  
Old 9/9/07, 7:23 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

Marc
I to have cutler hammer and I couldn't find on the breaker wire size rating?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #5  
Old 9/9/07, 7:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by nbhi
Marc
I to have cutler hammer and I couldn't find on the breaker wire size rating?
Hang on a bit... I think I have one laying around someplace. I'll just look.
Reply With Quote
  #6  
Old 9/9/07, 7:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Hey, you're right. The 40's and 50's have a chart molded in the side, but the 30's only have the torque spec. I notice that it is a small box lug on the 30's that seems like it should take up to about a #8.
-------------
I just checked CH's website, and that lug on the 30's is rated for one #14 through #8 or two #14 though #10. If that conductor on that breaker in the picture is a #6, then there's a problem. There's not much perspective in the picture, but if I had to guess I'd say that's a #8.

http://www.eatonelectrical.com/unsecure/cms1/F4.PDF
Reply With Quote
  #7  
Old 9/9/07, 8:21 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

The ones I have must be older. They have no chart molded on the side. I up graded to a more current box about a year and a half ago and the breakers Iam looking at are about 15 maybe 25 years old.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 9/9/07, 9:15 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,254
Default Re: Wire size?

Next time take a close look at the wire at the entry point to the breaker, if strands are missing(cut off to facilitate fitting the wire into the lug) you have a legit problem to note. We are getting a little to technical when we have to hit the specs on every breaker in the box.
Reply With Quote
  #9  
Old 9/9/07, 10:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by bhoagland
We are getting a little to technical when we have to hit the specs on every breaker in the box.
I certainly havn't endorsed that. It's just interesting to talk about, is all. Do whatever pleases you most.
Reply With Quote
  #10  
Old 9/9/07, 11:21 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Wire size?

Are you sure the wire is not AL? In any event, just based on the picture, it looks pretty likely that some strands have been cut off. It is a delimma for the home inspetor - sometimes you can't tell for sure without loosening the connection.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #11  
Old 9/10/07, 12:26 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by fnewman
In any event, just based on the picture, it looks pretty likely that some strands have been cut off.
I'm very curious as to why you say that. Looks pretty clean to me. When you cut off strands it is rare that you can get it to look that nice.
No, not that I have done it, but I have seen it as many times as anyone here.
Reply With Quote
  #12  
Old 9/10/07, 12:09 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Wire size?

I've seen situations where one or two strands were removed and the wire rotated (intentionally or otherwise) so that the cut strands were behind the conductor. However, I do agree that most of the time, it is visible.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #13  
Old 9/10/07, 1:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

More likely in the flat washer type breaker, they just flattened out the strands and split them, half on each side.
Legal? ... no
The most serious violation in the world? ... no.
If that was the only thing I found wrong I would probably keep walking.
If Marc is right and C/H doesn't make a set screw breaker in 30a the "fix" might be worse than the violation. (an extra splice to a #10 pigtail)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 5:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 10:53 PM


All times are GMT -4. The time now is 12:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts