Default Wire size?

Need help to determine wire sizes. The pic on the left, top breaker, 50amp.
it appears to me to be # awg 10 or 8. Same on the breaker right below, 30 amp, #10 or #8.
The pic on the right top breaker, 40amp, #10 aluminum?

Attachment 19003 Attachment 19004

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 8:42 AM..
Reply With Quote
  #2  
Old 2/27/08, 9:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

What sorts of loads do these breakers serve? You need to know that there are instances where a large breaker, with a disparity in conductor size, may safely and compliantly serve certain types of loads.
Reply With Quote
  #3  
Old 2/27/08, 9:14 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

Marc
The pic on the left serves the AC unit. The pic on the right supplies a range oven.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 2/27/08, 9:40 PM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Don't know about the breakers/wires, but I like the Neutrals and Grounds paired together on the bussbar.
Reply With Quote
  #5  
Old 2/27/08, 11:16 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by Tab M. Wilcox
Don't know about the breakers/wires, but I like the Neutrals and Grounds paired together on the bussbar.
He means it is bad, Gary. The branch ground wires should have their own terminal, not doubled with the neutrals, as this means they could become energized. Each neutral wire should be under one screw.

Up here, #10 wire is solid, #8 is stranded.
Reply With Quote
  #6  
Old 2/27/08, 11:22 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Wire size?

Quote:
Originally Posted by Tab M. Wilcox
Don't know about the breakers/wires, but I like the Neutrals and Grounds paired together on the bussbar.
And there's your aluminum neutral



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 2/28/08, 4:50 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

If thats the case John, then the wires feeding the 50amp are undersized for that breaker, #6 copper for 50amps?
Also, the pic on the left 40amps,, its Aluminum, what size? Perhaps #10



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 2/28/08, 6:32 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Wire size?

The wiring looks undersized to me.
Reply With Quote
  #9  
Old 2/28/08, 6:42 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

What size would you say it is?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 2/28/08, 9:52 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Wire size?

Comparing the left breaker with the single breaker below, it looks like #12 from here!

What is the size of the sgl pole breaker?

I have never seen a correct install with this small of wire on an HVAC circuit for a 240 VAC circuit. A gas furnace would be ok but that would be a 120 V.

It also looks like the 2nd sgl breaker (third down) may also be a 240V circuit. Red wire generally is part of a 240V circuit.

It is hard to determine wire size in person. Photos make it even harder.
Reply With Quote
  #11  
Old 2/28/08, 12:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Like Marc was alluding to, you have to know what the load is. It is not unusual to have a smaller wire going to an A/C compressor than you would use for a stove with the same breaker size.
The stove needs to be the full size mandated in 310.16 but motor loads like the A/C will typically need a wire about 60-70% of that. You need to read the label on the condenser. It will specify minimum circuit ampacity (wire size) and breaker size. You won't think they go together if you don't understand motors
Reply With Quote
  #12  
Old 2/28/08, 1:55 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Wire size?

I'm confused.

Are you saying a 50 amp Inductive load has a lower load than a 50 amp resistance load?

I don't think so.

I see no reason to run 20 amp wire from a 50 amp breaker.

HVAC breakers are rated for HVAC for a reason. Not because of lower circuit capacity.
Reply With Quote
  #13  
Old 2/28/08, 3:21 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Wire size?

440.32 Covers the conductor size and breaker rating.

Branch-circuit conductors supplying a single motor-compressor
shall have an ampacity not less than 125 percent of
either the motor-compressor rated-load current or the branch-circuit selection current, whichever is greater.

Thus, your 50 amp breaker for the A/C could conceivably carry 8 gauge wire and be allowed within the code.


I got chastised for calling this out by the AHJ one time when I first started inspecting.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #14  
Old 2/28/08, 4:52 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

*duplicate post

Last edited by Marc D. Shunk; 2/28/08 at 5:25 PM..
Reply With Quote
  #15  
Old 2/28/08, 4:54 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by dandersen
I see no reason to run 20 amp wire from a 50 amp breaker.
If you feel this way, you really need to bone up on your education a bit.

It can be completely proper, safe, and legal to have a "20 amp wire" ( ) coming from a 50 amp breaker for certain types of motor operated loads. You can have a breaker, for instance, 300% larger than what it would seem like the conductor can handle for a motor load. There are instances where you an have overcurrent protection up to 800% larger than what it would seem like the wire could handle.

Without some dataplate information on the equipment connected on the other end of that wire, calling anything out would be unjust, in my opinion.

Are you allowed, as home inspectors, to call out items for further evaluation that you're simply confused by? That is to say, if something just strikes you as weird, odd, or abnormal, but you can't put your finger on exactly why, is it permissible to call it out? Just wondering, because that might explain some of the stuff I get called in to look at.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 4:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 9:53 PM


All times are GMT -4. The time now is 5:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts