Default Re: Wire size?

Look at 310.16, 12ga is good for 25a. You are citing 240.4(D) (the 20a rule) but that says "Unless specifically permitted in 240.4(E) through (G)". (G) Overcurrent Protection for Specific Conductor Applications. Overcurrent protection for the specific conductors shall be permitted to be provided as referenced in Table 240.4(G).
Article 430 and 440 permit you to use 310.16 for ampacity and you can also use 430.52 table to determine the overcurrent device if the motor has integral overload protection in the motor or starter (250% of FLA)

The point is, if you see a motor load, you can't depend on 15a=14ga, 20a= 12g, 10a= 30a. and the wire size may not really match the breaker in the simplest sense.
Reply With Quote
  #32  
Old 2/29/08, 4:42 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by Greg Fretwell
40 amp breaker, 12 ga wire ... any questions?
I have one if I may.
Where do you see 12 ga wire on that tag?
Reply With Quote
  #33  
Old 2/29/08, 5:17 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by sparksnmore
I have one if I may.
Where do you see 12 ga wire on that tag?
Here, I'll quote Greg from the post just before yours:
Quote:
Originally Posted by Greg Fretwell
Look at 310.16, 12ga is good for 25a. You are citing 240.4(D) (the 20a rule) but that says "Unless specifically permitted in 240.4(E) through (G)".
Reply With Quote
  #34  
Old 2/29/08, 6:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

The label is pretty unambiguous about the breaker, Minimum circuit ampacity is the wire size.
Attached Thumbnails
wire-size-ac-condenser.jpg  
Reply With Quote
  #35  
Old 2/29/08, 9:50 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by Greg Fretwell
The label is pretty unambiguous about the breaker, Minimum circuit ampacity is the wire size.
I see but it doesn't have to be the minimum
Reply With Quote
  #36  
Old 2/29/08, 10:46 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by sparksnmore
I see but it doesn't have to be the minimum
Of course it doesn't have to be, but it may be and it would still be completely safe and completely legal. This would represent an economical and very servicable installation.
Reply With Quote
  #37  
Old 3/1/08, 9:47 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by sparksnmore
I see but it doesn't have to be the minimum
How can you say that.
It says right there: "MINIMUM CIRCUIT AMPACITY".
Reply With Quote
  #38  
Old 3/1/08, 12:58 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

You as a home inspector are not limited to code problems. You should be pointing out design problems that are beyond code requirements like light switches behind doors and other things that will be a pain in the butt for the new owner . Where I have a concern is when you start pointing to perfectly safe and legal things like the wire size to the A/C condenser (that just don't seem right to you) as a safety problem. This implies that you ARE citing code.
Reply With Quote
  #39  
Old 3/1/08, 1:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Wire size?

Quote:
Originally Posted by Greg Fretwell
Where I have a concern is when you start pointing to perfectly safe and legal things like the wire size to the A/C condenser (that just don't seem right to you) as a safety problem. This implies that you ARE citing code.
Even worse, it implies that we know better than the codes. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #40  
Old 3/1/08, 11:06 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by Marc D. Shunk
Of course it doesn't have to be, but it may be and it would still be completely safe and completely legal. This would represent an economical and very servicable installation.
Gotcha, thanks Marc, I was thinking he meant it "had to be minimum".... duha.
We always use 10 ga on those but it's good to know we could save a couple of dollars I suppose.
Reply With Quote
  #41  
Old 3/2/08, 3:03 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

This one is a little more straight forward
8ga wire, 50 or 60a breaker
Attached Thumbnails
wire-size-pool-heater.jpg  
Reply With Quote
  #42  
Old 3/2/08, 9:18 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

Joe
So what your post #20 says, Figure 2, in the text below, That a 40amp protective devise with a minimun wire sizes, awg#10, because the total amps are 27.5

The Branch Circuit Requirements
The branch-circuit conductor size requirements for hermetic refrigerant motor-compressors are located in Part D of Article 440. The sizing requirements for the branch-circuit conductors are very similar to those requirements for standard motors. Basically, the branch-circuit conductors are required to be sized at 125 percent of the rated-load current of the single hermetic motor-compressor or 125 percent of the branch-circuit selection current, whichever is less. However, for combination-load equipment having a nameplate as required by Section 440-4(b), the branch-circuit conductors are required to be "not less than the minimum circuit ampacity marked on the" nameplate of the equipment (see Figure 2). See NEC Section 440-35.
The manufacturer has already calculated the conductor size to be based on the total of all of the motor loads in the combination-load equipment times 125 percent. It is not necessary to do these calculations again. For this type of equipment, the installer and the inspector only have to install and verify that the branch-circuit conductors supplying the equipment have an ampacity equal to or greater than the minimum circuit ampacity marked on the nameplate of the equipment.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #43  
Old 3/2/08, 9:43 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by nbhi
Joe
So what your post #20 says, Figure 2, in the text below, That a 40amp protective devise with a minimun wire sizes, awg#10, because the total amps are 27.5

The Branch Circuit Requirements
The branch-circuit conductor size requirements for hermetic refrigerant motor-compressors are located in Part D of Article 440. The sizing requirements for the branch-circuit conductors are very similar to those requirements for standard motors. Basically, the branch-circuit conductors are required to be sized at 125 percent of the rated-load current of the single hermetic motor-compressor or 125 percent of the branch-circuit selection current, whichever is less. However, for combination-load equipment having a nameplate as required by Section 440-4(b), the branch-circuit conductors are required to be "not less than the minimum circuit ampacity marked on the" nameplate of the equipment (see Figure 2). See NEC Section 440-35.
The manufacturer has already calculated the conductor size to be based on the total of all of the motor loads in the combination-load equipment times 125 percent. It is not necessary to do these calculations again. For this type of equipment, the installer and the inspector only have to install and verify that the branch-circuit conductors supplying the equipment have an ampacity equal to or greater than the minimum circuit ampacity marked on the nameplate of the equipment.
and ....

The "maximum overcurrent protective device" rating is the other very important number on the data plate. The overcurrent protection device marked on combination-load equipment is marked "maximum" such as "maximum fuse size." This means that specified size cannot be exceeded. The device could be less than that maximum size.

It may seem that the conductors are improperly protected. However it is the combination of the maximum size short-circuit and ground-fault protective device together with the overload protection system of the equipment that is providing the overcurrent protection for all circuit components. If the overload protection is field-installed for a hermetic refrigerant motor-compressor, the overload sizing must be in accordance with Section 440-52 and must not exceed the manufacturer’s values.

In Figure 2, the nameplate indicates the minimum circuit ampacity and the maximum overcurrent device. Based on the nameplate data the conductors are required to be capable of carrying 27.8 amperes. Remember, with combination-load equipment the 125 percent factor is already used by the manufacturer to determine the 27.8-ampere total. A No. 10 THWN copper conductor is an acceptable size for the circuit conductors. The maximum overcurrent protective device marked on the equipment is 40 amperes. It appears as though the No. 10 THWN conductors are improperly protected. This is not true. The 40-ampere fuse or HACR circuit breaker provides the short-circuit and ground-fault protection. The overload protective device limits the normal running current to the proscribed values.

The overcurrent protective device could be a device rated smaller than 40 amperes as long as it can handle the starting and running current of the equipment. These maximum values are often misunderstood to be the only size allowable by the Code, when in fact it is the value that must not be exceeded.
Reply With Quote
  #44  
Old 3/2/08, 9:55 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Wire size?

Joe
So nothing smaller than 10 awg wire, (12 or 14) correct? Thats because of the amp draw of 27.5, right. And the circuit breaker, nothing larger than a 40?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #45  
Old 3/2/08, 11:03 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Please contact the IAEI for further clarification, I posted the reference for you, and I agree and do not question the author Michael Johnston.

Here's another route you (we) can take directly to the people who write the rules.

An example:

Question 2. I am very confused on what inspectors of Riverside County, California, are asking for on A/C condensers (breakers size). For example, if the condenser plate reading has a minimum breaker size of 24 amps, and a maximum breaker size of 35 amps, and I install a 30-amp breaker size, am I in the wrong? Inspectors are telling me that I should go to the max on the breaker. Are they correct? I cannot find this section in the NEC 1999. — F. A.

Answer 2. This is not a violation of the Code unless the nameplate of the unit specifies a minimum size fuse or circuit breaker greater than 30 amperes. Section 440.4(B) in the NEC 2002 applies to air-conditioning equipment that contains a hermetic refrigerant motor compressor and other equipment such as a fan motor. The Code does not require manufacturers to list minimum size overcurrent protective device sizes on the nameplate. The nameplate must only indicate the maximum rating of the fuse or circuit breaker.
If the manufacturer elects to specify a minimum size device on the nameplate, NEC 110.3(B) would require the installer to abide by the nameplate information. — Tom Garvey, CMP-11.

You can find additional information in the NECH and at www.bussmann.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 5:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 10:53 PM


All times are GMT -4. The time now is 4:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts