#46
|
||||
|
||||
|
Joe
Inspector to Inspector, If the nameplate states, 27.5 amp draw, then the conductor needs be be greater than 12 awg? Thats all I am asking. "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#47
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
27.5 a is not that ambiguous, where it gets confusing is when the number is something like 23a that falls between the 240.4(D) and 310.16 rating (for #12). HVAC equipment makes this easier by actually giving you the max breaker size but in the case of a hardwired motor load you might have to do some pencil work to see if the breaker is appropriate. The general rule is the breaker can be 250% of the motor nameplate FLA and the wire size has to be 125% of FLA, using 310.16 rating and that might be at the 75c column if the motor has 75c lugs (and not wired with a cable wiring method like AC, NM or MC which limit you to 60c).
|
|
#48
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
It might be noted that as soon as you put a plug on a motor you lose these concessions because a user can come along and plug anything into that receptacle. That is the reason why we have 240.4(D) (the 15a-14ga, 20a-12ga rule) The installer has no control over what a user might plug in so they build the 80% safety factor into the allowable breaker size. 14, 12 and 10 gauge wire is the most likely to end up on a receptacle.
|
|
#49
|
||||
|
||||
|
Quote:
BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
|
#50
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#51
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The problem is when it is a cable. Individual conductors are usually not marked in cables, you need to see the cable jacket. That will usually be behind the drywall if this is a flush mounted panel.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 4:28 PM |
| 30 amp breaker wire size | kweiss | Electrical Inspections | 18 | 10/10/06 9:53 PM |