Default Re: Wire size?

Joe
Inspector to Inspector, If the nameplate states, 27.5 amp draw, then the conductor needs be be greater than 12 awg? Thats all I am asking.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #47  
Old 3/2/08, 10:37 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

27.5 a is not that ambiguous, where it gets confusing is when the number is something like 23a that falls between the 240.4(D) and 310.16 rating (for #12). HVAC equipment makes this easier by actually giving you the max breaker size but in the case of a hardwired motor load you might have to do some pencil work to see if the breaker is appropriate. The general rule is the breaker can be 250% of the motor nameplate FLA and the wire size has to be 125% of FLA, using 310.16 rating and that might be at the 75c column if the motor has 75c lugs (and not wired with a cable wiring method like AC, NM or MC which limit you to 60c).
Reply With Quote
  #48  
Old 3/2/08, 10:45 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

It might be noted that as soon as you put a plug on a motor you lose these concessions because a user can come along and plug anything into that receptacle. That is the reason why we have 240.4(D) (the 15a-14ga, 20a-12ga rule) The installer has no control over what a user might plug in so they build the 80% safety factor into the allowable breaker size. 14, 12 and 10 gauge wire is the most likely to end up on a receptacle.
Reply With Quote
  #49  
Old 3/4/08, 12:31 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Wire size?

Quote:
Originally Posted by nbhi
What size would you say it is?
Conductors sizes are continously printed along the wire. When looking at a short peice, you may not be able to see the size markings but the visible portion of the wires in a panel are usually long enough to be able to see the markings.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #50  
Old 3/4/08, 1:08 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

Quote:
Originally Posted by nbhi
Joe
Inspector to Inspector, If the nameplate states, 27.5 amp draw, then the conductor needs be be greater than 12 awg? Thats all I am asking.
Not an inspector but you are correct. For a Air Conditioner a #12 would be maxed out at 25 amps.
Reply With Quote
  #51  
Old 3/4/08, 1:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire size?

The problem is when it is a cable. Individual conductors are usually not marked in cables, you need to see the cable jacket. That will usually be behind the drywall if this is a flush mounted panel.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 4:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 9:53 PM


All times are GMT -4. The time now is 5:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts