Had a #12 wire being used for a sump pump with a #15 wire spliced into the box going into a room outlet. The circuit breaker was a 20 amp breaker. I wrote it up as improper conductor sizes connected together recommend evaluation by a licensed electrician. The realtor called and told me the electrican said it was okay. Am i wrong?
|
| Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
You're correct. The #14 AWG conductor needs to be protected at 15 amps according to NEC 240.4(D) unless if falls under part (E) or (G) which in this case it does not.
240.4 Protection of Conductors. (D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied. (D)(3) 14 AWG Copper. 15 amperes |
|
#3
|
|||
|
|||
|
Quote:
You may want to consider that it doesn't need to be evaluated again but simply repaired/replaced. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#4
|
|||
|
|||
|
Leave your findings and let the client decide whom to believe. Tell them to have electrician put it on paper that it is ok.
Greensboro Home Inspection Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas. greensboro-home-inspection.html Raleigh Home Inspection Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas. Raleigh-home-inspection.html BassRumors.com Providing a blog, news, and forum dedicated to bass fishing. |
|
#5
|
||||
|
||||
|
I doubt the realtor even talked to an electrician. It is a simple/quick replacement and I don't see why an electrician would even hesitate to replace the wire.
I always run a sump circuit as dedicated, but that's another story/issue. Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#6
|
||||
|
||||
|
What is the amperage rating on the pump? If it only pulls a few amps it will never overload the wire. Thats why the electrician said it was ok probably. I would still called it out as being mismatched, but I doubt it will ever be an issue, if it is the only thing on that branch of wiring. Now if you add a few more things, then you will have problems.
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#7
|
||||
|
||||
|
I don't think the problem is the pump only pulling a few amps under normal condition. It is if there is a problem with the pump and it starts pulling too many amps when it is broken. The small wire could melt and start a fire before the OCD trips.
|
|
#8
|
||||
|
||||
|
Well then replace the breaker with a 15 amp. Problem solved!!
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
According to NEC Table 310.16, 60° C, #14 conductors are rated for 20 amps. For an application like this 240.4(D) limits their protection to 15 amps. It's likely that at 20 amps this circuit could operate forever without damaging the conductor.
|
|
#10
|
||||
|
||||
|
Quote:
Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#11
|
||||
|
||||
|
I saw a 14/2 (AC unit) protected with 100Amps breakers last week...
Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |
| 30 amp breaker wire size | kweiss | Electrical Inspections | 18 | 10/10/06 9:53 PM |