Default Wire supports

I would think copper pipe and eyelet type screws are not approved methods of wire supports. The 2nd picture runs perpendiclar to sub floor and it gets worse. I am glad I looked in an access behind a fireplace over a toilet and under a shelf.(Need to make an appointment with Chiropractician as my body is not meant to be in a position like that)

What is the approved method for running wires parellel to joists? I have seen on board but the name escapes me. (Raceway)!!
Attached Thumbnails
wire-supports-140709-083-small-.jpg.jpg
Views:	86
Size:	39.0 KB
ID:	29781   wire-supports-140709-067-small-.jpg.jpg
Views:	80
Size:	48.4 KB
ID:	29782  
Reply With Quote
Find an InterNACHI certified Arkansas Home Inspector (and anywhere else in North America)
  #2  
Old 7/2/09, 9:04 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 739
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire supports

Wires could be secured using properly sized staples. Some staples are good for up to 2 flat cables under one staple. Another method, and the one that I prefer, is something like the 3M stak-it. Less nailing than staples and it maintains spacing better for air circulation.
Reply With Quote
  #3  
Old 7/2/09, 9:25 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Wire supports

Quote:
Originally Posted by Jim Port View Post
Another method, and the one that I prefer, is something like the 3M stak-it. Less nailing than staples and it maintains spacing better for air circulation.
Cool. I hadn't seen those before...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 7/2/09, 10:22 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Wire supports

I always recommend removing tie-wraps from all bundled branch wiring.

I like this....

wire-supports-electricalwiring.jpg
Reply With Quote
  #5  
Old 7/2/09, 11:21 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,115
Default Re: Wire supports

Quote:
Originally Posted by dvalley View Post
I always recommend removing tie-wraps from all bundled branch wiring.

I like this....

Attachment 29790

Including the tie-wraps identifying multi-wire circuits in a panel?


Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #6  
Old 7/4/09, 12:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire supports

Quote:
Originally Posted by jwicklander View Post
Including the tie-wraps identifying multi-wire circuits in a panel?


Jeff
Thats a different application( refering directly to Jeff's reply only )....If the conductors are within a cable that run into the panel no group identification is required. If they still choose to do it so be it but not a code requirement. If you have a conduit or raceway that has multi-wire branch circuits within it in the 2008 NEC you would need to identify them as a grouping to their respected grounded conductor. If the conduit only has one set of multi-wire branch circuits then it is obvious and no grouping is required. Just remember, this new requirement does not apply to cables and it NEW for 2008 so probably wont apply to alot of HI situations unless it is a new home and in chicago...lol


Here...since I am the Cut and Paste King...I will give you some from the NEC.


210.4(D) Grouping.
The ungrounded and grounded conductors
of each multiwire branch circuit shall be grouped by wire
ties or similar means in at least one location within the
panelboard or other point of origination.

Exception: The requirement for grouping shall not apply if
the circuit enters from a cable or raceway unique to the
circuit that makes the grouping obvious.

So basically cables do not apply and if it is a raceway with only one set of multi-wire branch circuits within it then it still does not apply. Hope that was somewhat helpful and not confusing.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 7/4/09, 12:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wire supports

Oh..BTW. The other issue that comes up with that application since we can't see it all is the bundling issue. Basically, if the conductors run more than 24 inches bundled then ampacity adjustments should take place....

From what I see ( and can't really tell very well ) I see 5 12-2's maybe but could be a few 12-3's in their. The number of CCC's would be 10 if we took the assumption of 5 12-2's. If we look at table 310.15(B)(2)(a) an adjustment of 50% would have to take place. ( again assuming this bundle is run for 24" at least ). Solution, seperate them so they are not bundled more than 24".



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Exterior wire & supports dmacy Electrical Inspections 11 1/10/08 10:26 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM


All times are GMT -4. The time now is 3:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts