I would think copper pipe and eyelet type screws are not approved methods of wire supports. The 2nd picture runs perpendiclar to sub floor and it gets worse. I am glad I looked in an access behind a fireplace over a toilet and under a shelf.(Need to make an appointment with Chiropractician as my body is not meant to be in a position like that)
What is the approved method for running wires parellel to joists? I have seen on board but the name escapes me. (Raceway)!! |
| Find an InterNACHI certified Illinois Home Inspector (and anywhere else in North America) |
Wires could be secured using properly sized staples. Some staples are good for up to 2 flat cables under one staple. Another method, and the one that I prefer, is something like the 3M stak-it. Less nailing than staples and it maintains spacing better for air circulation.
Including the tie-wraps identifying multi-wire circuits in a panel? Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
Here...since I am the Cut and Paste King...I will give you some from the NEC. 210.4(D) Grouping. The ungrounded and grounded conductors
of each multiwire branch circuit shall be grouped by wire ties or similar means in at least one location within the panelboard or other point of origination. Exception: The requirement for grouping shall not apply if the circuit enters from a cable or raceway unique to the circuit that makes the grouping obvious. So basically cables do not apply and if it is a raceway with only one set of multi-wire branch circuits within it then it still does not apply. Hope that was somewhat helpful and not confusing. Paul W. Abernathy |
Oh..BTW. The other issue that comes up with that application since we can't see it all is the bundling issue. Basically, if the conductors run more than 24 inches bundled then ampacity adjustments should take place....
From what I see ( and can't really tell very well ) I see 5 12-2's maybe but could be a few 12-3's in their. The number of CCC's would be 10 if we took the assumption of 5 12-2's. If we look at table 310.15(B)(2)(a) an adjustment of 50% would have to take place. ( again assuming this bundle is run for 24" at least ). Solution, seperate them so they are not bundled more than 24". Paul W. Abernathy |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Exterior wire & supports | dmacy | Electrical Inspections | 11 | 1/10/08 9:26 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |