Default Wired as Sub Panel?

This panel appears to be wired as a sub panel. I did not locate any other disconnect. The original ground was not connected. Very neat wiring, but why separate the neutrals and grounds? Opinions appreciated.



wired-sub-panel-109.jpg

wired-sub-panel-111.jpg

wired-sub-panel-112.jpg

wired-sub-panel-107.jpg

wired-sub-panel-110.jpg




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801

Last edited by jevans; 2/19/10 at 5:13 AM..
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/19/10, 5:19 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Wired as Sub Panel?

seperation is just workmanship, which is in short supply these days. Pic 3 shows that the neutrals are bonded.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 2/19/10, 7:16 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Wired as Sub Panel?

Looks good to me.
Reply With Quote
  #4  
Old 2/19/10, 7:24 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Wired as Sub Panel?

Quote:
Originally Posted by bgraham View Post
seperation is just workmanship, which is in short supply these days. Pic 3 shows that the neutrals are bonded.
Yes, see the upper greenish screw on the neutral buss? It is bonding that buss to the panelboard.



Quote:
Originally Posted by dvalley View Post
Looks good to me.
Agreed...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 2/19/10, 7:42 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Wired as Sub Panel?

Thanks to all. Only thing missing is a grounding source. The grounding conducter was coiled above the panel.

wired-sub-panel-115.jpg




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #6  
Old 2/19/10, 8:08 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wired as Sub Panel?

Like the others have said, personal choice, pride and workmanship. Looks like one of my panels except for the GEC and the tyraps.
Reply With Quote
  #7  
Old 2/19/10, 10:26 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Wired as Sub Panel?

Pride in workmanship!!! Get that Sparkies name, and keep it on file. You may have need of his services someday.
Reply With Quote
  #8  
Old 2/19/10, 11:35 PM
rbero rbero is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Green Bay Wi 54304
Posts: 160
Send a message via Yahoo to rbero
Default Re: Wired as Sub Panel?

this is the nices job i have seen in a long time this guy takes pride in his work



Ron Bero
Green Bay Wisconsin
All Star Inspections
www.greenbayhomeinspector.com
Serving Northeastern Wisconsin Including
Brown,Door,Kewaunee,Manitowoc,Calumet,Outagame,
Shawano,Oconto,and Marinette Countys.
Reply With Quote
  #9  
Old 2/19/10, 11:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Wired as Sub Panel?

Yep
I do not even see any #14.Looks good.
Reply With Quote
  #10  
Old 2/20/10, 1:12 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wired as Sub Panel?

We can call it a neat and job with Pride.....However, if he(or she) has not finished what they have started and connect the GEC to the Grounding Electode(s) then he is NOT done and in my mind unprofessional. But in all fairness maybe they are not done yet..

So I will assume this is "NOT" a remote distribution panel for my comments.

Is the opening that the electrician is bringing the GEC into designed for that application?..potatoes...Potatos....probably does not matter for the overall scheme since I really can't tell...



Paul W. Abernathy
Reply With Quote
  #11  
Old 2/20/10, 1:49 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wired as Sub Panel?

Quote:
Originally Posted by pabernathy View Post
We can call it a neat and job with Pride.....However, if he(or she) has not finished what they have started and connect the GEC to the Grounding Electode(s) then he is NOT done and in my mind unprofessional. But in all fairness maybe they are not done yet..

So I will assume this is "NOT" a remote distribution panel for my comments.

Is the opening that the electrician is bringing the GEC into designed for that application?..potatoes...Potatos....probably does not matter for the overall scheme since I really can't tell...
Come on Paul, you aren't going to start about whether the 1/4" hole can be used for the GEC now are you? Or are you one of the ones that requires the Kenny clamp on the GEC?
Reply With Quote
  #12  
Old 2/20/10, 2:25 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wired as Sub Panel?

lol.....I said I was not going to comment on that...

Funny thing is...as a consultant to a larger manufacture of these types of products ( to go without naming )...they say only the hole provided by them for such a intent can be used. if that hole ( their reasoning ) was put into the equipment as part of their listing for the application then it is fine.... and I dont disagee.



Paul W. Abernathy
Reply With Quote
  #13  
Old 2/20/10, 2:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wired as Sub Panel?

no....I have not seen any kenny clamps in Richmond, VA



Paul W. Abernathy
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/20/10, 2:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wired as Sub Panel?

I guess the question is Mr.Port...lol...is would you allow the contractor to bring his GEC through a mounting hole or if possible a weep hole?..Just because they can.



Paul W. Abernathy
Reply With Quote
  #15  
Old 2/20/10, 4:41 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wired as Sub Panel?

Seems I am not the only one. Somewhere I thought I saw something that said they could be used for the GEC. I will need to look.

http://forums.mikeholt.com/showthrea...ight=weep+hole

or this one

http://forums.mikeholt.com/showthrea...ight=weep+hole

Last edited by Jim Port; 2/20/10 at 4:43 PM.. Reason: added links
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts