Default Wires crossing bus bar.

Need help with proper report verbiage.

Would you call out the neutral wires crossing the bus bar?

Also a few of the neutrals were doubled up at the ground/neutral bars.

These wires feed the panel GFCI.

I forget why is it an issue to have doubled neutrals?

Any verbiage and explanation would be appreciated.

A few of the wires/insulation were over sprayed with paint/drywall compound.
I did not think this was an issue as it only was on the insulation.
Attached Thumbnails
wires-crossing-bus-bar-150709-031-small-.jpg.jpg
Views:	266
Size:	53.6 KB
ID:	33438  
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 11/21/09, 1:55 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Wires crossing bus bar.

I probably wouldn't report them crossing the buss bar.

I would report the doubled up.
Observed multiple neutral wire connections in a single lug. This is a major fire hazard. If you have 2 or more wires in a lug and you disconnect one of the two hot wires at the breaker you could damage all the circuits and anything plugged into these circuits. Some electricians (who haven't done their homework) will tell you that it is OK to have more than one neutral (white) wire under a screw on the bus bar. They are wrong. It has long (at least as far back as 1967) been required by manufacturer's instructions and Underwriters Laboratories Standard 67 for panel boards.
I would also report the neutrals being taped together with black tape. When I see anything black on a white wire, that communicates to me that it is being used as a "hot" line as opposed to neutral.

The over spray isn't right, but isn't that big of a deal either.

Here is an example that I took off this board showing why it's important to not double neutrals...
Attached Thumbnails
wires-crossing-bus-bar-doublelugneutrals.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 11/21/09, 1:59 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Wires crossing bus bar.

Thanks Mark.

Nice picture. I have seen that one a few times.

Appreciatte the comments.

Would you comment on the main grounded conductor not being identified with whit tape?
Reply With Quote
  #4  
Old 11/21/09, 2:01 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Wires crossing bus bar.

Quote:
Originally Posted by dmacy View Post
Thanks Mark.

Nice picture. I have seen that one a few times.

Appreciatte the comments.

Would you comment on the main grounded conductor not being identified with whit tape?
No (but that's because I probably wouldn't have noticed that.) That's not something I check for. (Maybe I should, I don't know.)



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wires ran from lugs to auxilary panels Kevin Luce Electrical Inspections 7 9/20/07 10:24 AM
grounding wires tvanvranken Electrical Inspections 14 3/16/07 8:24 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Black wires dmacy Electrical Inspections 7 7/6/06 9:53 PM


All times are GMT -4. The time now is 7:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts