I came across these wires connected to lugs on the top part of the main service panel. Two wires were running to one auxilary panel and the second two wires are running to the second auxilary panel. Both auxilary panels are about a foot away from the service panel. Each auxilary panel had 4 breakers in them.
I was told by an electrician at one time that this is allowed due to the short distance from the service box and the auxilary panel. Is this true because I cannot find it in the NEC book. I know there are double taps. |
|
#2
|
||||
|
||||
|
Those conductors are only protected by the main C/B at the top left which looks to be way over the rating of those top lug wires.
I doubt a licensed electrcian wired this. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#3
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree about not being installed by an electrician. Number 10 wires installed.
An electrician that works at a local steel mill (I know steel mill electricians have their own way of thinking) made that statement when we were talking about electrical panels. I could not think of any reason why that statement would be true but I wanted to ask just in case. |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Read the "tap" rules in 240. This is a "feeder tap" since it is on the load side of the main.
Quote:
The thinking is a short tap is adequately protected from a short circuit at the 10x number, if it does burn up it is in pipe anyway and overload protection comes at the loadside panel. |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Now the "double taps" are another issue
|
|
#6
|
||||
|
||||
|
Please Note:
Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the info. I've already book marked it.
|
|
#7
|
||||
|
||||
|
Lets not also forget that "WHITE" conductors are never allowed as ungrounded conductors in conduit.....so thats an issue as well.
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Whats going on at the left side of the panel. I see electrical tape. Is that a splice? Doesnt look right.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Distribution panels | bking | Electrical | 2 | 3/11/07 11:29 AM |
| Ground Wires Inside a Panel | mveitenhans | Electrical | 13 | 10/29/06 12:39 PM |
| FPE Panel - Do you open them up? | menser | Electrical | 11 | 2/7/06 7:31 PM |
| Old electrical panels? | ysoltis | Electrical | 0 | 1/13/06 12:38 PM |