Default Wires ran from lugs to auxilary panels

I came across these wires connected to lugs on the top part of the main service panel. Two wires were running to one auxilary panel and the second two wires are running to the second auxilary panel. Both auxilary panels are about a foot away from the service panel. Each auxilary panel had 4 breakers in them.

I was told by an electrician at one time that this is allowed due to the short distance from the service box and the auxilary panel.

Is this true because I cannot find it in the NEC book.

I know there are double taps.
Attached Thumbnails
wires-ran-lugs-auxilary-panels-dsc02261.jpg  
Reply With Quote
  #2  
Old 9/18/07, 10:54 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Wires ran from lugs to auxilary panels

Those conductors are only protected by the main C/B at the top left which looks to be way over the rating of those top lug wires.

I doubt a licensed electrcian wired this.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 9/18/07, 11:09 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 201
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wires ran from lugs to auxilary panels

I agree about not being installed by an electrician. Number 10 wires installed.

An electrician that works at a local steel mill (I know steel mill electricians have their own way of thinking) made that statement when we were talking about electrical panels. I could not think of any reason why that statement would be true but I wanted to ask just in case.
Reply With Quote
  #4  
Old 9/18/07, 11:29 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wires ran from lugs to auxilary panels

Read the "tap" rules in 240. This is a "feeder tap" since it is on the load side of the main.
Quote:
240.21(B)(1) Taps Not Over 3 m (10 ft) Long. Where the length of the tap conductors does not exceed 3 m (10 ft) and the tap conductors comply with all of the following:
(1) The ampacity of the tap conductors is
a. Not less than the combined computed loads on the circuits supplied by the tap conductors, and
b. Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent-protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply.
(3) Except at the point of connection to the feeder, the tap conductors are enclosed in a raceway, which shall extend from the tap to the enclosure of an enclosed switchboard, panelboard, or control devices, or to the back of an open switchboard.
(4) For field installations where the tap conductors leave the enclosure or vault in which the tap is made, the rating of the overcurrent device on the line side of the tap conductors shall not exceed 10 times the ampacity of the tap conductor.
Basically if the wire is good for 1/10th of the main, it is in conduit and it is sufficiently protected in the load side panel it is OK.

The thinking is a short tap is adequately protected from a short circuit at the 10x number, if it does burn up it is in pipe anyway and overload protection comes at the loadside panel.
Reply With Quote
  #5  
Old 9/18/07, 11:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wires ran from lugs to auxilary panels

Now the "double taps" are another issue
Reply With Quote
  #6  
Old 9/19/07, 12:22 AM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 201
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wires ran from lugs to auxilary panels

Thanks for the info. I've already book marked it.
Reply With Quote
  #7  
Old 9/19/07, 9:48 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Wires ran from lugs to auxilary panels

Lets not also forget that "WHITE" conductors are never allowed as ungrounded conductors in conduit.....so thats an issue as well.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 9/20/07, 10:24 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wires ran from lugs to auxilary panels

Whats going on at the left side of the panel. I see electrical tape. Is that a splice? Doesnt look right.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Distribution panels bking Electrical Inspections 2 3/11/07 11:29 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 7:31 PM
Old electrical panels? ysoltis Electrical Inspections 0 1/13/06 12:38 PM


All times are GMT -4. The time now is 3:35 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts