I have grouped the ends of 8 each 12-2 w/ground wires in the center of my attic that feed various 15amp receptacles (the longest wire being less than 20' in length).

My questions are:

1- What gauge main wire will I need to feed feed these wires from the breaker box that is less than 20' away?
2- What amperage breaker will I need?
3- What type of junction box is required to connect the larger gauge wire to the 12-2 wires?

Thank you in advance for any info
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/8/11, 8:52 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: wiring a branch circuit????

20 A breaker max.

You have to protect the 12 gauge wire and it is only rated for 20 A.

You have a larger problem with the size of the junction box and the wire nuts needed to connect it all.

Each junction box is rated for a maxim number of conductors and wire nut connections.

Quote:
314.16 Number of Conductors in Outlet, Device and Junction Boxes, and Conduit Bodies

Boxes and conduit bodies must be of sufficient size to provide free space for all enclosed conductors (See Figure 2). The term “free space” should not be confused with “free conductor” located in 300.14. Contrary to the opinion of some electricians, there are requirements that limit the number of conductors allowed within outlet, device, pull and junction boxes. Many times, when covers are removed from junction boxes, it is discovered that the box is packed full of conductors, and no consideration was given to the sizes and numbers of conductors. Disregarding box fill requirements can create safety as well as fire hazards (See Figure 3).

Article 314 contains detailed requirements for box fill and junction box sizing. Two sections refer to box fill calculations: 314.16(A) Box Volume Calculations, and 314.16(B) Box Fill Calculations. In no case shall the volume of the box, as calculated in 314.16(A), be less than the fill calculation as determined in 314.16(B). Requirements for calculating the minimum volume for conduit bodies are located in 314.16(C). Conduit bodies, also referred to as condulets, are manufactured with a variety of configurations. The Type (i.e., LB, LR, LL, C, T, etc.) indicates the number and location of conduit entries. Unlike junction boxes and conduit bodies, terminal housings supplied with motors are not required to meet box fill requirements.

Use 314.16 to determine the size box required for conductors 18 AWG through 6 AWG. These boxes are calculated by using the number of conductors and their respective sizes. Boxes and conduit bodies enclosing conductors 4 AWG or larger must also comply with the provisions of 314.28.

314.16(A) Box Volume Calculations

Various sizes of metal boxes are listed in Table 314.16(A).



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI


Last edited by mlarson; 11/8/11 at 9:29 AM..
Reply With Quote
  #3  
Old 11/8/11, 9:01 AM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

Isn't there a junction box available with a bus bar that I can use?
I also understand that I don't ground this secondary box?
Reply With Quote
  #4  
Old 11/8/11, 9:05 AM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

any idea what size wire I need to feed the junc box?
Reply With Quote
  #5  
Old 11/8/11, 9:29 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: wiring a branch circuit????

Agreed! You should call in a electrician for this work if you don't have this info.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 11/8/11, 9:31 AM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

can't afford one if there is someone here knowledgeable with the facts I've stated.
Should be fairly straight up info??
Reply With Quote
  #7  
Old 11/8/11, 9:41 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: wiring a branch circuit????

You are not understanding something.

The 12 gauge wire MUST be protected by no more than 20A protection.

Hire or find someone who understands before you hurt someone.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 11/8/11, 9:58 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
I also understand that I don't ground this secondary box?
EVERY metal box must be bonded to the GES.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 11/8/11, 10:03 AM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

OK thanks for the info.
Reply With Quote
  #10  
Old 11/8/11, 10:14 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: wiring a branch circuit????

Why am I envisioning multiple pigtails in that proposed box?

I hate to say this, but I hope that is his home, and not that of an innocent!!
Reply With Quote
  #11  
Old 11/8/11, 1:08 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: wiring a branch circuit????

If you dont have the money to hire a professional, dont run the circuits. You likely will just end up hurting someone.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 11/8/11, 1:34 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,185
Default Re: wiring a branch circuit????

Don't forget the duct tape.
Reply With Quote
  #13  
Old 11/8/11, 7:36 PM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

Thank you again Mr. Larson and Mr. Pope for the useful information.
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/8/11, 8:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
I have grouped the ends of 8 each 12-2 w/ground wires in the center of my attic that feed various 15amp receptacles (the longest wire being less than 20' in length).

My questions are:

1- What gauge main wire will I need to feed feed these wires from the breaker box that is less than 20' away?
2- What amperage breaker will I need?
3- What type of junction box is required to connect the larger gauge wire to the 12-2 wires?

Thank you in advance for any info
Sorry guy but you're in over your head. You're looking to run a larger conductor/cable with larger than 20 amp OCPD to this box and then splice onto your 12/2 circuits. This would involve tap rules and other stuff that is way beyond the scope of this forum.
Reply With Quote
  #15  
Old 11/8/11, 8:11 PM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

To maintain the professionalism of this site I took the liberty of reporting the unnecessary posts such as "I hate to say this, but I hope that is his home, and not that of an innocent!!" and "Don't forget the duct tape". These could be construed as "Taunting" as described in the site rules. The duct tape comment was obviously made to ridicule but the "I hate to say" comment was a direct afront to the safety of myself and my family directed to other than the initiator of the thread.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 7:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts