Default Re: wiring a branch circuit????

The guy at Home Depot tells me that I can run a 12-2 wire with ground from the main box to a plastic junction box and wire nut no more than 4 each 12-2 wires to it. Sound plausible? 20 amp breaker in the main box.
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 11/8/11, 8:47 PM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

I have learned that I'm in the wrong place for the answers I'm seeking. Thanks again to those that offered information and to the others that discouraged me from doing the work myself in the name of public safety.
Reply With Quote
  #18  
Old 11/9/11, 5:25 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
can't afford one if there is someone here knowledgeable with the facts I've stated.
Should be fairly straight up info??
I am MORE that knowledgeable and qualified to answer your question. The problem is that what you want to do is absolutely the wrong way to achieve what you want. But to give you the short bus answers since this whole set up is a "short bus" way to do it is you need (and can only feed) a 20 amp Breaker and 12 guage wire to feed this mess. The Junction box will need to accommodate and have the proper box fill capability of all those
12 wires ( I don't have the time to calculate that for you right now, go get an 8x8x 6" Plastic J box that will be more than sufficient and you wont need to worry about grounding it since it is plastic. Then when you are all done, Make sure all of your smoke detectors are working and you are all paid up on your home owners insurance.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #19  
Old 11/9/11, 6:00 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,185
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
To maintain the professionalism of this site I took the liberty of reporting the unnecessary posts such as "I hate to say this, but I hope that is his home, and not that of an innocent!!" and "Don't forget the duct tape". These could be construed as "Taunting" as described in the site rules. The duct tape comment was obviously made to ridicule but the "I hate to say" comment was a direct afront to the safety of myself and my family directed to other than the initiator of the thread.
I hope you reported me to the electricity police. No one else will listen.
Reply With Quote
  #20  
Old 11/9/11, 6:22 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
Thank you again Mr. Larson and Mr. Pope for the useful information.
The term GROUP in your orginal post makes me not want to assist you...sorry. oh...FYI...I am an electrician and darnn right I dont come cheap madam homeowner. Any advice given to someone clearly unable to understand the basic concepts will open yourself up to liability.....have at it everyone.

No mention of Box Fill, Bundling and so on.....Sure hope their home owners policy is current.



Paul W. Abernathy
Reply With Quote
  #21  
Old 11/9/11, 7:00 PM
Cajy Ohone Cajy Ohone is offline
New User
 
Join Date: Nov 2011
Posts: 11
Please Note: Cajy Ohone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: wiring a branch circuit????

I ran a 12-2 wire w/ground from a 20amp breaker in main box (GE) to a 4"x4" plastic junction box (about 20' in wire length).
I then ran four 12-2 wires w/grounds from four separate receptacle boxes to this junction box, none longer than 15'.
Then I wired nutted the blacks to blacks, whites to whites and grounds to grounds with huge wire nuts, rubber taped it then black vinyl taped it.
Is this an except-able configuration?
Reply With Quote
  #22  
Old 11/9/11, 7:19 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: wiring a branch circuit????

Quote:
Originally Posted by pabernathy View Post
The term GROUP in your orginal post makes me not want to assist you...sorry. oh...FYI...I am an electrician and darnn right I dont come cheap madam homeowner. Any advice given to someone clearly unable to understand the basic concepts will open yourself up to liability.....have at it everyone.

No mention of Box Fill, Bundling and so on.....Sure hope their home owners policy is current.
Hey Paul, I mentioned box fill and also Home owners Insurance...hahahaha
This guy makes me think of the old song, by earth wind and fire.....FIRE !!!.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #23  
Old 11/9/11, 7:21 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: wiring a branch circuit????

Nice to see you back on the MB. Maybe Nick will fill you in on all the excitement you missed.
I was thinking the same thing when I saw this thread but I am not an electrician so I kept my mouth shut!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 11/9/11 at 8:01 PM..
Reply With Quote
  #24  
Old 11/9/11, 7:28 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: wiring a branch circuit????

Quote:
Originally Posted by Cajy Ohone View Post
The guy at Home Depot tells me that I can run a 12-2 wire with ground from the main box to a plastic junction box and wire nut no more than 4 each 12-2 wires to it. Sound plausible? 20 amp breaker in the main box.
See what the guy across the street at Lowe's has to say.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #25  
Old 11/9/11, 7:33 PM
Bill Smith's Avatar
Bill Smith Bill Smith is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: wiring a branch circuit????

Quote:
Originally Posted by roconnor View Post
If you dont have the money to hire a professional, dont run the circuits. You likely will just end up hurting someone.
An excellent point.
Also, I would be very careful about giving electrical wiring advice to someone on the BB. Just sayin'



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #26  
Old 11/9/11, 7:36 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: wiring a branch circuit????

Quote:
Originally Posted by ccurrins View Post
See what the guy across the street at Lowe's has to say.
Now c'mon Chris. The Home Depot customer service people in the electrical department are highly trained ....... in bringing in carts from the parking lot. Those guys at Lowe's just come from the gardening department. Sheesh.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 7:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts